X-240 lead identification

Discussion about the Power System AC Disconnect (PSAC)

Moderators: OutBack Moderator Team, OutBack

Post Reply
SGES
Forum Junior Member
Posts: 1
Joined: Sun Nov 27, 2005 1:43 pm
Location: Wisconsin
Contact:

X-240 lead identification

Post by SGES » Sun Nov 27, 2005 1:52 pm

We just installed a dual FX2024 system with the X-240 in the PS2AC along with the MATE, Hub-4 and PS2DC. The inverters are configured to run in Master and OB Slave2 mode. During commissioning, the X-240 breakers were turned on and a loud buzz/hum came from Inv 2. The system shutdown and the MATE showed a <PO2 AC output backfeed> error message. We suspect a factory transformer wiring error but can't confirm this because the four transformer leads are not labeled. Here's the question: is there a reliable method to determine which leads are which from the X-240?

Thanks!
David Blecker, PE
Seventh Generation Energy

Kent Osterberg
Forum Emperor
Posts: 1523
Joined: Mon Jun 09, 2003 11:01 pm
My RE system: SMA Sunny Boy 2500 with eight Mobil Solar Ra 180 modules
Location: Cove, Oregon
Contact:

Post by Kent Osterberg » Sun Nov 27, 2005 2:43 pm

First confirm that one inverter is programmed to be a 1-2 phase master and that the other is programmed to be OB slave L2. Look in the ADV/FX/PG3/STACK menu. Press the port button to switch between inverters.

If the stacking is okay, you can check the X240 wiring with a voltmeter. The voltage between either output bus and neutral should be 120 vac. The voltage between the two output busses should be 240 vac. If the 120-volt measurement is okay and the 240-volt measurement is not, then the X240 is probably wired incorrectly.