We just installed a dual FX2024 system with the X-240 in the PS2AC along with the MATE, Hub-4 and PS2DC. The inverters are configured to run in Master and OB Slave2 mode. During commissioning, the X-240 breakers were turned on and a loud buzz/hum came from Inv 2. The system shutdown and the MATE showed a <PO2 AC output backfeed> error message. We suspect a factory transformer wiring error but can't confirm this because the four transformer leads are not labeled. Here's the question: is there a reliable method to determine which leads are which from the X-240?
Thanks!
X-240 lead identification
Moderators: OutBack Moderator Team, OutBack
X-240 lead identification
David Blecker, PE
Seventh Generation Energy
Seventh Generation Energy
-
Kent Osterberg
- Forum Emperor
- Posts: 1523
- Joined: Mon Jun 09, 2003 11:01 pm
- My RE system: SMA Sunny Boy 2500 with eight Mobil Solar Ra 180 modules
- Location: Cove, Oregon
- Contact:
First confirm that one inverter is programmed to be a 1-2 phase master and that the other is programmed to be OB slave L2. Look in the ADV/FX/PG3/STACK menu. Press the port button to switch between inverters.
If the stacking is okay, you can check the X240 wiring with a voltmeter. The voltage between either output bus and neutral should be 120 vac. The voltage between the two output busses should be 240 vac. If the 120-volt measurement is okay and the 240-volt measurement is not, then the X240 is probably wired incorrectly.
If the stacking is okay, you can check the X240 wiring with a voltmeter. The voltage between either output bus and neutral should be 120 vac. The voltage between the two output busses should be 240 vac. If the 120-volt measurement is okay and the 240-volt measurement is not, then the X240 is probably wired incorrectly.