FM80 goes to Charged and stops charging the batteries
Moderators: OutBack Moderator Team, OutBack
-
jose
- Forum Member
- Posts: 8
- Joined: Tue Jun 23, 2015 3:25 am
- My RE system: 18 x 300W SolarWorld (6 strings of 3 panels in series - strings are paralleled 2x2 for around 100v OC)
1 x Outback 24V 3Kw Inverter VFX3024e
3 x Outback FM80
1 x Outback Mate
12 x 2V BAE 8 PVS 1200 cells
1 x Honda EU2000i Generator
FM80 goes to Charged and stops charging the batteries
Hello,
I have an FM80 controller connected to 1500 W PV and 645 AH battery bank. It is set for the voltages recommended by the battery company (Crown) and does 2.5 hours absorption.
Lately the controller, after the absorbing period, changes to Charged and stops charging the batteries even if the voltages go down. Today, for example, the voltage showed 24.9 at 16.00 PM event though the sun is shinning. This is the third time or so it happens and I have to turn it off to restart a new cycle. How can I solve this? Is this a defect? I am worried because it happens at random, it was fine the last few days and the last time it happened was about a week ago.
Thanks,
Jose
UPDATE: Happened again today and I think I understand why. This is a very hot day with 34 C outside and about 26 C in the battery room (this only happens in hot days). We had a late lunch (being Sunday and all that) and used the kettle to boil water just as the FM80 was going from Absorb into Floating (I always check before turning the kettle on). Unfortunately I did not check what happened to it straight away after the fact but an hour or so later it was in Charged mode and the batteries were being drained with the sun out at 15.00 in the afternoon. A restart fixed it as usual. There are a number of similar posts in this forum that have gone unanswered but I hope that at some point this bug is fixed. Until then the solution is to build something to monitor the controller or do as I do, set an alarm and check it everyday.
EDIT: After reading some more I check the Rebulk voltage on my FM80 and it was set to 24 (possibly the default). I changed it to 25.2 in the hope that it makes a difference.
UPDATE 2: Again today, worryingly twice in a row which had not happened before. Today the temperature has gone up a couple of degrees (36 C outside, 27.5 inside) but the kettle was used half an hour before the end of the Absorbing stage. An hour later or so the status is charged, amps in are zero and the voltage is 25.1 (lower than Rebulk which I had set yesterday to 25.2). Again a restart solved the problem. I will not use the kettle or anything alike tomorrow to see if it makes a difference (assuming the temperatures keep high).
I have an FM80 controller connected to 1500 W PV and 645 AH battery bank. It is set for the voltages recommended by the battery company (Crown) and does 2.5 hours absorption.
Lately the controller, after the absorbing period, changes to Charged and stops charging the batteries even if the voltages go down. Today, for example, the voltage showed 24.9 at 16.00 PM event though the sun is shinning. This is the third time or so it happens and I have to turn it off to restart a new cycle. How can I solve this? Is this a defect? I am worried because it happens at random, it was fine the last few days and the last time it happened was about a week ago.
Thanks,
Jose
UPDATE: Happened again today and I think I understand why. This is a very hot day with 34 C outside and about 26 C in the battery room (this only happens in hot days). We had a late lunch (being Sunday and all that) and used the kettle to boil water just as the FM80 was going from Absorb into Floating (I always check before turning the kettle on). Unfortunately I did not check what happened to it straight away after the fact but an hour or so later it was in Charged mode and the batteries were being drained with the sun out at 15.00 in the afternoon. A restart fixed it as usual. There are a number of similar posts in this forum that have gone unanswered but I hope that at some point this bug is fixed. Until then the solution is to build something to monitor the controller or do as I do, set an alarm and check it everyday.
EDIT: After reading some more I check the Rebulk voltage on my FM80 and it was set to 24 (possibly the default). I changed it to 25.2 in the hope that it makes a difference.
UPDATE 2: Again today, worryingly twice in a row which had not happened before. Today the temperature has gone up a couple of degrees (36 C outside, 27.5 inside) but the kettle was used half an hour before the end of the Absorbing stage. An hour later or so the status is charged, amps in are zero and the voltage is 25.1 (lower than Rebulk which I had set yesterday to 25.2). Again a restart solved the problem. I will not use the kettle or anything alike tomorrow to see if it makes a difference (assuming the temperatures keep high).
-
jose
- Forum Member
- Posts: 8
- Joined: Tue Jun 23, 2015 3:25 am
- My RE system: 18 x 300W SolarWorld (6 strings of 3 panels in series - strings are paralleled 2x2 for around 100v OC)
1 x Outback 24V 3Kw Inverter VFX3024e
3 x Outback FM80
1 x Outback Mate
12 x 2V BAE 8 PVS 1200 cells
1 x Honda EU2000i Generator
Re: FM80 goes to Charged and stops charging the batteries
I am sorry but I ended up expanding my setup with more panels and more FM80s and replacing the batteries. Never happened again.
Re: FM80 goes to Charged and stops charging the batteries
Thanks. Neighbor has the same issue. Definitely not temp related. Pulled bank down to 24.5 with loads. Stayed stuck at CHARGED even with rebulk at 25.2.
-
jose
- Forum Member
- Posts: 8
- Joined: Tue Jun 23, 2015 3:25 am
- My RE system: 18 x 300W SolarWorld (6 strings of 3 panels in series - strings are paralleled 2x2 for around 100v OC)
1 x Outback 24V 3Kw Inverter VFX3024e
3 x Outback FM80
1 x Outback Mate
12 x 2V BAE 8 PVS 1200 cells
1 x Honda EU2000i Generator
Re: FM80 goes to Charged and stops charging the batteries
I see. I would have the FM80's firmware updated (needs to be done at a dealer) if it is not the latest. The two new FM80s I bought when I upgraded the system have a newer firmware and behave differently in may ways. They are slower, for example, and hopefully that problem has been solved. My previous battery bank died and I ended up upgrading the system last Winter. It went through the Summer without a hitch but, to be fair, it is a completely different beast.
Re: FM80 goes to Charged and stops charging the batteries
They are both less than a year old. I'll have him contact the dealer.
- Mike Curran
- Forum Emperor
- Posts: 3603
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: FM80 goes to Charged and stops charging the batteries
Is it possible your battery temperature is over 50°C? This from the Flexmax manual:
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
Re: FM80 goes to Charged and stops charging the batteries
No. While this is in AZ, it's in the high desert at 6800 ft elevation. Ambient is rarely above 36°C, and it's in an insulated pump house. If the batteries have ever seen even 40°C, I'd be shocked.Mike Curran wrote: ↑Mon Nov 02, 2020 7:34 amIs it possible your battery temperature is over 50°C? This from the Flexmax manual:
Screenshot_20201102-103115_Adobe Acrobat.jpg
-
pablo
- Forum Member
- Posts: 13
- Joined: Fri Jul 08, 2016 10:03 am
- My RE system: Flexmax 60 CC, Xantrex True Charger 40, Samlex SA2000 inverter, Trojan L16 RE 12 volt bank, Solar World 285 panel x 2. Honda Eu2000 generator. Totally off-grid.
- Location: High Prairie, WA, USA.
Re: FM80 goes to Charged and stops charging the batteries
I am having a similar problem with my FM60.
The manual states that the charger will go to CHARGED mode briefly between ABSORB and FLOAT. I watched this happen and it only stays in CHARGED mode for a second or two. Except when it doesn't. Lately, frequently, and seemingly at random it stays in CHARGED mode until I do a hard RSTRT. No heat problems (it's winter and the batteries are cool). Most of my settings are at the default for a 12 Volt system. The manual also states that CHARGED mode indicates an external power source. Nope, don't have that. Just my panels on an off-the-grid system.
It's a major bummer. Charge my batteries all the way up on a rare sunny day and then draw them way down while the sun is still shining and end up having to run the genny at night.
I have had this system up and running for 5 years. It's possible this problem has happened before as I have a vague memory of it, but not with this frequency.
The manual states that the charger will go to CHARGED mode briefly between ABSORB and FLOAT. I watched this happen and it only stays in CHARGED mode for a second or two. Except when it doesn't. Lately, frequently, and seemingly at random it stays in CHARGED mode until I do a hard RSTRT. No heat problems (it's winter and the batteries are cool). Most of my settings are at the default for a 12 Volt system. The manual also states that CHARGED mode indicates an external power source. Nope, don't have that. Just my panels on an off-the-grid system.
It's a major bummer. Charge my batteries all the way up on a rare sunny day and then draw them way down while the sun is still shining and end up having to run the genny at night.
I have had this system up and running for 5 years. It's possible this problem has happened before as I have a vague memory of it, but not with this frequency.
- EA6LE-ONE
- Forum Czar
- Posts: 952
- Joined: Tue May 05, 2020 7:51 am
- My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W
System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W - Location: Providenciales, Turks & Caicos Isl.
Re: FM80 goes to Charged and stops charging the batteries
If you have the charging parameters set correctly when you reach float the battery is considered charged. it will still charge a bit in float. What you are describing is that the batteries reached their EOL. You might have the charging parameters a bit wrong, and if no battery monitor then the life of the batteries will be shorter. also is very important how was cycled and what temperature the battery reach while charging to have a better service time. 5 years is not bad.pablo wrote: ↑Mon Nov 30, 2020 12:01 pmI am having a similar problem with my FM60.
The manual states that the charger will go to CHARGED mode briefly between ABSORB and FLOAT. I watched this happen and it only stays in CHARGED mode for a second or two. Except when it doesn't. Lately, frequently, and seemingly at random it stays in CHARGED mode until I do a hard RSTRT. No heat problems (it's winter and the batteries are cool). Most of my settings are at the default for a 12 Volt system. The manual also states that CHARGED mode indicates an external power source. Nope, don't have that. Just my panels on an off-the-grid system.
It's a major bummer. Charge my batteries all the way up on a rare sunny day and then draw them way down while the sun is still shining and end up having to run the genny at night.
I have had this system up and running for 5 years. It's possible this problem has happened before as I have a vague memory of it, but not with this frequency.
-
provo
- Forum Emperor
- Posts: 1464
- Joined: Thu Jul 27, 2006 4:34 pm
- My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back - Location: Sierra foothills
Re: FM80 goes to Charged and stops charging the batteries
I don't really know why this happens, but I've seen it also on occasion. Sometimes doing a "force float" (from the Misc menu) has forced it into float (pablo wrote: ↑Mon Nov 30, 2020 12:01 pm
Lately, frequently, and seemingly at random it stays in CHARGED mode until I do a hard RSTRT. No heat problems (it's winter and the batteries are cool). Most of my settings are at the default for a 12 Volt system. The manual also states that CHARGED mode indicates an external power source. Nope, don't have that. Just my panels on an off-the-grid system.
- Mike Curran
- Forum Emperor
- Posts: 3603
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: FM80 goes to Charged and stops charging the batteries
FWIW, here's what the FM80 manual says about float:
It sounds to me like there might be an incorrect setting for float voltage... too low?
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
pablo
- Forum Member
- Posts: 13
- Joined: Fri Jul 08, 2016 10:03 am
- My RE system: Flexmax 60 CC, Xantrex True Charger 40, Samlex SA2000 inverter, Trojan L16 RE 12 volt bank, Solar World 285 panel x 2. Honda Eu2000 generator. Totally off-grid.
- Location: High Prairie, WA, USA.
Re: FM80 goes to Charged and stops charging the batteries
Thanks all for your ideas. I haven't changed the float voltage in 5 years (13.5 volts). The last time this happened the batteries were under load and the system reading was 12.2 volts and it was stuck in CHARGED mode with plenty of sun available to bump back up to 13.5 where it belonged. I fixed it by manually doing a RSTRT under the MISC menu, but obviously I can't stand there and watch it all the time.
End of life of the batteries is a distinct possibility, but I don't see how that would create the problem, except that it may expose a glitch in the programming that only occurs under specific conditions. The charger should still maintain the float voltage regardless of battery health, yes?
Reading through all of the similar complaints, I am guessing it is a programming glitch. Has Outback addressed this anywhere in the forum? I should probably give them a call.
Also thinking about playing around Rebulk Voltage setting and Auto Restart Mode setting to see if that makes a difference, but it is pretty difficult to troubleshoot w/o sitting there and watching the charger for long periods of time. Especially since it doesn't do it every time.
End of life of the batteries is a distinct possibility, but I don't see how that would create the problem, except that it may expose a glitch in the programming that only occurs under specific conditions. The charger should still maintain the float voltage regardless of battery health, yes?
Reading through all of the similar complaints, I am guessing it is a programming glitch. Has Outback addressed this anywhere in the forum? I should probably give them a call.
Also thinking about playing around Rebulk Voltage setting and Auto Restart Mode setting to see if that makes a difference, but it is pretty difficult to troubleshoot w/o sitting there and watching the charger for long periods of time. Especially since it doesn't do it every time.
- Mike Curran
- Forum Emperor
- Posts: 3603
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: FM80 goes to Charged and stops charging the batteries
That's my understanding, yes. I hate when these one of a kind anomalies pop up!The charger should still maintain the float voltage regardless of battery health, yes?
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
raysun
- Forum Overlord
- Posts: 13674
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FM80 goes to Charged and stops charging the batteries
The Flexmax charge controllers enter the Charged state if the battery voltage is above the Flexmax Float voltage.
Check the calibration of the controller by measuring the battery voltage at the battery +/- terminals and at the charge controller bat +/- terminals. They should agree.
Next check the OUT voltage on the FM's display, it should agree with the bat +/- voltage.
Check the calibration of the controller by measuring the battery voltage at the battery +/- terminals and at the charge controller bat +/- terminals. They should agree.
Next check the OUT voltage on the FM's display, it should agree with the bat +/- voltage.
-
pablo
- Forum Member
- Posts: 13
- Joined: Fri Jul 08, 2016 10:03 am
- My RE system: Flexmax 60 CC, Xantrex True Charger 40, Samlex SA2000 inverter, Trojan L16 RE 12 volt bank, Solar World 285 panel x 2. Honda Eu2000 generator. Totally off-grid.
- Location: High Prairie, WA, USA.
Re: FM80 goes to Charged and stops charging the batteries
Thank you Raysun.
As I mentioned in my original post, the battery voltage was reading 12.2 (well below the float voltage of 13.5) when the CC got 'stuck' in charged mode. After I do RSTRT, it works in FLOAT mode as expected.
As I mentioned in my original post, the battery voltage was reading 12.2 (well below the float voltage of 13.5) when the CC got 'stuck' in charged mode. After I do RSTRT, it works in FLOAT mode as expected.
-
raysun
- Forum Overlord
- Posts: 13674
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FM80 goes to Charged and stops charging the batteries
Yes, I saw that, but it doesn't answer my question, so I'll repeat it: is the charge controller calibrated to the battery voltage?
-
Ndravetsky
- Forum Member
- Posts: 5
- Joined: Mon Nov 28, 2022 12:06 pm
- My RE system: Flex power one FXR
Mate3s
Flexmax 80 charge controller
VFXR inverter
16 Centential 400AH batteries (2 strings of 8)
Wrico 10kw generator
Re: FM80 goes to Charged and stops charging the batteries
My system has done this to me 3 times over the past 3-4 months. I’ve only seen it happen when my generator is on. The gen usually will come on in the morning while getting ready for work. If it’s sunny, I will turn it off and let the sun charge the batteries and it does with no problem. If it’s cloudy I just let AGS shut off the generator once the batteries are charged. Generally there will be some power made with sun on and off during the day. When the FM80 says charged, there will have been no charging all day(0 kw) or until I catch it and start bulk charging again. I have found a variance in the manual saying full charge on the battery monitor screen should be set .4 volts below absorb and another version says .4 volts above absorb. I’ve been above absorb and at absorb for full charge. I’ll see if setting .4 volts below absorb makes a difference.
-
pablo
- Forum Member
- Posts: 13
- Joined: Fri Jul 08, 2016 10:03 am
- My RE system: Flexmax 60 CC, Xantrex True Charger 40, Samlex SA2000 inverter, Trojan L16 RE 12 volt bank, Solar World 285 panel x 2. Honda Eu2000 generator. Totally off-grid.
- Location: High Prairie, WA, USA.
Re: FM80 goes to Charged and stops charging the batteries
Sorry to hear about your trouble Ndravetsky. I am not replying to your post but just posting another tidbit of information regarding my similar issue. Someone had mentioned before that it could be the problem was caused by old batteries. Well, I have a new battery bank and I'm still having the same problem. I have not done the voltage calibration yet. I'll give that a try.
-
fcwlp
- Forum Emperor
- Posts: 1416
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
Re: FM80 goes to Charged and stops charging the batteries
I never came across that discrepancy in the manuals. The FNDC's "charged voltage" must be set below the absorb voltage. A setting of 0.3 to 0.4V for a "charged time" of 1 minute is typical.Ndravetsky wrote: ↑Thu Mar 02, 2023 5:25 pmI have found a variance in the manual saying full charge on the battery monitor screen should be set .4 volts below absorb and another version says .4 volts above absorb. I’ve been above absorb and at absorb for full charge. I’ll see if setting .4 volts below absorb makes a difference.
-
josh
- Forum Whiz
- Posts: 25
- Joined: Thu Nov 10, 2016 9:10 am
- My RE system: Off-grid, Mate 3, VFX 3648, FM 60 Charge Control, Tristar
diversion control, 1KW hydro, 1.5 KW solar panel output
Re: FM80 goes to Charged and stops charging the batteries
I’m having a similar problem with a new FM80. It’s programmed to control a lithium 51.2 volt, 300ah battery. Absorb is set at 57.6 volts for 12 minutes and float at 54.4 volts. I set the wake-up at 1.5 volts and snooze at .2 amps (wake-up interval is 5 minutes). I’m getting two different, random scenarios. After absorb, it will either read “charged”, drop well below 54 and never enter the float stage or “wake-up” then “low light” then “snooze” and 5 minutes later go to float. This at mid-day with full sun. The force float command also randomly won’t work but have found that forcing absorb and then quickly pressing force float puts the device into float. I didn’t see a resolution in this thread. Is it possibly a firmware issue?
-
raysun
- Forum Overlord
- Posts: 13674
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FM80 goes to Charged and stops charging the batteries
New battery? What brand/model?josh wrote: ↑Mon Aug 12, 2024 4:10 pmI’m having a similar problem with a new FM80. It’s programmed to control a lithium 51.2 volt, 300ah battery. Absorb is set at 57.6 volts for 12 minutes and float at 54.4 volts. I set the wake-up at 1.5 volts and snooze at .2 amps (wake-up interval is 5 minutes). I’m getting two different, random scenarios. After absorb, it will either read “charged”, drop well below 54 and never enter the float stage or “wake-up” then “low light” then “snooze” and 5 minutes later go to float. This at mid-day with full sun. The force float command also randomly won’t work but have found that forcing absorb and then quickly pressing force float puts the device into float. I didn’t see a resolution in this thread. Is it possibly a firmware issue?
-
josh
- Forum Whiz
- Posts: 25
- Joined: Thu Nov 10, 2016 9:10 am
- My RE system: Off-grid, Mate 3, VFX 3648, FM 60 Charge Control, Tristar
diversion control, 1KW hydro, 1.5 KW solar panel output
Re: FM80 goes to Charged and stops charging the batteries
New charger. It’s a Relion battery, RB48V300, about 4 years old. I had the same issue with the old FM60 and previous lead acid battery bank. Outback eventually agreed to a warranty replacement, and it was a little quirky, too. For unknown reasons it resolved itself and went to float as intended. That charger operated fine with the new lithium battery.
-
raysun
- Forum Overlord
- Posts: 13674
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FM80 goes to Charged and stops charging the batteries
Is the FM80 the only active charging source?
-
josh
- Forum Whiz
- Posts: 25
- Joined: Thu Nov 10, 2016 9:10 am
- My RE system: Off-grid, Mate 3, VFX 3648, FM 60 Charge Control, Tristar
diversion control, 1KW hydro, 1.5 KW solar panel output
Re: FM80 goes to Charged and stops charging the batteries
Yes. In the wet season we use a TriStar for hydro diversion, but it’s off until then.