Inconsistent Ground-Fault Detector Interuptor Wiring Diagram
The Outback wiring diagram for a dual inverter configuration, which is available on the Outback website, shows the GFDI wired between the PV array and the Charge Controller. The GFDI installation instructions shows the unit wired between the Charge Controller and the Battery Bank. Anyone know which is the correct configuration?
-
SHerrera
Re: Inconsistent Ground-Fault Detector Interuptor Wiring Diagram
Sorry about the confusion.
The wiring diagram posted on our website is for are older product GFP.
The new product is the GFDI, and it should be installed between controller and batteries.
The instructions on the GFDI manual is correct.