Power from Solar Panels Low
Moderators: OutBack Moderator Team, OutBack
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Power from Solar Panels Low
I have 18 Evergreen 200watt panels for my system however the wattage coming through fluctuates between 0 and 300 watts (on both the Watt Plot software & Outback Mate). They are wired in parrallel 4 strings of 4ea and one string of two and are split into two feeds going to two Flexmax 80's from the combiner box. The run is about 25ft from the panels to the combiner box using #4 stranded wire and about 4ft from the combiner box to the MX80's. I recently upgraded my system from one MX60 Controller (Did not have this problem) to two Flexmax MX80 Controllers. Help please! The sun is shining.
-
Kwood
Re: Power from Solar Panels Low
I would like to know what firmware revision the FM80's have.
If you press the first button on the controller to enter the main menu, press and hold the first button once again and the firmware revision will appear.
Please indicate what the controller displays.
Whats coming IN, Whats going OUT (voltage & current), and what mode the controller is in display at the bottom right corner.
If you press the first button on the controller to enter the main menu, press and hold the first button once again and the firmware revision will appear.
Please indicate what the controller displays.
Whats coming IN, Whats going OUT (voltage & current), and what mode the controller is in display at the bottom right corner.
-
blackswan555
- Forum Emperor
- Posts: 2625
- Joined: Sat Aug 30, 2008 5:50 am
- My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.
- Location: Ibiza Spain,
Re: Power from Solar Panels Low
have you altered any settings it the FM`s from default ? Have you set the VBATT calibration ? What is your bat voltage and your indicated panel voltage when this is happening ? Has this only started since the new FM`s (are they wired correctly)
Have a good one
Tim
Have a good one
Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
The controller displays 28.2V IN and 25.9V OUT. Current is 0.0A on both. The modes displayed are MPPT BULK on the 1st and SNOOZING on the 2nd.Sweetspark wrote:I would like to know what firmware revision the FM80's have.
If you press the first button on the controller to enter the main menu, press and hold the first button once again and the firmware revision will appear.
First, thanks for the quick response. The firmware revision for the FM80's are both 001.009.000.
Please indicate what the controller displays.
Whats coming IN, Whats going OUT (voltage & current), and what mode the controller is in display at the bottom right corner.
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
The only setting I altered was to turn the AUX setting to off. I did not set the VBATT Calibration. My battery voltage is at 25.9 and the indicated panel voltage is at 27. This only started with the new FM's.blackswan555 wrote:have you altered any settings it the FM`s from default ? Have you set the VBATT calibration ? What is your bat voltage and your indicated panel voltage when this is happening ? Has this only started since the new FM`s (are they wired correctly)
Have a good one
Tim
-
blackswan555
- Forum Emperor
- Posts: 2625
- Joined: Sat Aug 30, 2008 5:50 am
- My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.
- Location: Ibiza Spain,
Re: Power from Solar Panels Low
I presume there was a degree of rewiring for the new FM `s ? do you know if this is done correctly, if you have pics that may be helpful,
Tim
Do you mean they are wired 4 in series then 4 parallel then the other 2 on the other FM in series ?They are wired in parallel 4 strings of 4ea and one string of two
Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
Not sure if the photos will upload, but here goes.blackswan555 wrote:I presume there was a degree of rewiring for the new FM `s ? do you know if this is done correctly, if you have pics that may be helpful,
Tim
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
blackswan555 wrote:I presume there was a degree of rewiring for the new FM `s ? do you know if this is done correctly, if you have pics that may be helpful,
Tim
-
Kwood
Re: Power from Solar Panels Low
This is the reason you are not charging. Your incoming voltage has to be AT LEAST 2 voltage higher then your absorbtion setpoint in order to charge. By default, the absorbtion set point is 28.8, thus, your incoming voltage has to be at least 30.8 to harvest current. The controller is display MPPT-Bulk because it wants to charge, but does not have nesscary power to complete a bulk charge.downrightp wrote:The controller displays 28.2V IN and 25.9V OUT. Current is 0.0A on both. The modes displayed are MPPT BULK on the 1st and SNOOZING on the 2nd.
Just out of curiousity, if you enter the advanced menu on the controller, press next until you reach 'auto restart'. The bottom right hand corner says Mode 0, I want you to change it to Mode 1 for troubleshooting purposes. Press mode and it will change the value, it will ask for a password which will always be 141.
Let me know the outcome O:)
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
Just out of curiousity, if you enter the advanced menu on the controller, press next until you reach 'auto restart'. The bottom right hand corner says Mode 0, I want you to change it to Mode 1 for troubleshooting purposes. Press mode and it will change the value, it will ask for a password which will always be 141.
Let me know the outcome O:)[/quote]
Both controllers went into "sleeping" "Snoozing" mode respectively.
Let me know the outcome O:)[/quote]
Both controllers went into "sleeping" "Snoozing" mode respectively.
-
blackswan555
- Forum Emperor
- Posts: 2625
- Joined: Sat Aug 30, 2008 5:50 am
- My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.
- Location: Ibiza Spain,
Re: Power from Solar Panels Low
Your incoming panel voltage is very low, They are either wired in-correctly or you have a breaker faulty I would think, Please clarify/confirm how they are wired ?
Have a good one
Tim
Have a good one
Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
Just finished re-wiring the panels from 24V to 48V. Will have to wait for tomorrow to see if that takes care of the problem. Will post update tomorrow after the Sun starts doing it's thing.blackswan555 wrote:Your incoming panel voltage is very low, They are either wired in-correctly or you have a breaker faulty I would think, Please clarify/confirm how they are wired ?
Have a good one
Tim
-
blackswan555
- Forum Emperor
- Posts: 2625
- Joined: Sat Aug 30, 2008 5:50 am
- My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.
- Location: Ibiza Spain,
Re: Power from Solar Panels Low
if they were all wired in parallel, they will work to-morrow :-)
Have a good one
Tim
Have a good one
Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
-
downrightp
- Forum Member
- Posts: 9
- Joined: Mon Jun 16, 2008 10:25 am
- My RE system: New to solar systems. Eighteen evergreen 200's, 2-mx80 charge controllers; PSPV solar combiner; disconnects; 840ah battery bank; 2-Outback GVFX inverters mounted on the Flexware 500.
- Location: South Florida
Re: Power from Solar Panels Low
You are right on! Things already looking a lot better even though it's cloudy. Thanks a million to all!blackswan555 wrote:if they were all wired in parallel, they will work to-morrow :-)
Have a good one
Tim
Re: Power from Solar Panels Low
Solar power is fully depends on the power of sunlight. If sunlight power is low then the power of solar is low.