I am in the process of installing an outback system, inverter, MX60, PSDC. I am wondering why you donÔÇÖt include ground bus in the PSDC and why the negative bus is bonded to the box. Can I remove the negative bond , add a ground bus and an lightning arrestor ( my array is pole mounted), or do I need you ground fault kit ? If so why not just include it with PSDC. I believe a system can only be bonded to ground once and that would be at the Service entrance.
Thanks for your time
Chris
PSDC
Moderators: OutBack Moderator Team, OutBack
Chris,
Both the positive and negative sides are isolated from the PSDC to allow the use of GFPs where they are required. Where GFPs are not used, either the positive of negative side needs to be grounded and I assume the negative bond was the least expensive way to accomplish this. You can install a ground buss if you want. OB supples them with holes and screws to match the holes in the PSDC. No problem adding lightning protection. If I recall correctly, GFPs are required where the array is roof mounted, so they may not be required for your pole mounted array. I believe that you are correct that a system can only be bonded to ground at one point but the DC system is a separate and independent system so it should be possible to bond it to ground in the PSDC. The questions is what size ground conductor to run from the service entrance to the PSDC.
Robert
Both the positive and negative sides are isolated from the PSDC to allow the use of GFPs where they are required. Where GFPs are not used, either the positive of negative side needs to be grounded and I assume the negative bond was the least expensive way to accomplish this. You can install a ground buss if you want. OB supples them with holes and screws to match the holes in the PSDC. No problem adding lightning protection. If I recall correctly, GFPs are required where the array is roof mounted, so they may not be required for your pole mounted array. I believe that you are correct that a system can only be bonded to ground at one point but the DC system is a separate and independent system so it should be possible to bond it to ground in the PSDC. The questions is what size ground conductor to run from the service entrance to the PSDC.
Robert
-
chris olthuis
- Forum Whiz
- Posts: 30
- Joined: Wed Jun 09, 2004 1:56 pm
- Location: Barrie
Chris,
Your question about what size ground conductor to use is one that can generate some debate. Although I used 4/0 cable to connect my SW5548s to the batteries, I did not use 4/0 cable to ground the negative side of my system. I know that some might say this is a code violation but let me explain my reasoning. Because I am using GFPs the maximum ground fault current on the array side is limited to 1A, at which point the system becomes ungrounded or possibly a positive grounded system depending on the location of the fault. At 1A a 14ga wire would be more than adequate. Given that the grounding wires from the GFPs are 10ga and I have two GFPs, the negative side of my system is actually ground with two 10ga conductors.
Since a 1A ground fault will only disconnect the arrays, the real question is what size conductor was needed to ground my PSDC, the cases of my MX60s and my inverters. Since the breakers supplying the inverters are the largest, they will control. With 250A breakers, the maximum fault current should be limited to something near 250A. Therefore, I needed a ground conductor that could carry 250A for the short time it would take to trip a 250A breaker. Table 250-122 indicates that a 4ga wire should be adequate. However, I used a 1ga wire to be extra safe. This wire runs from the GBBs in my PSDC to the ground rod for my house. To put things in perspective, the 1ga wire is twice the size of the wire grounding my 200A service entrance panel. If you want to go larger than what I used, keep in mind that the largest wire an OB GBB can accommodate is 1/0 and it could be a tight fit.
Robert
Your question about what size ground conductor to use is one that can generate some debate. Although I used 4/0 cable to connect my SW5548s to the batteries, I did not use 4/0 cable to ground the negative side of my system. I know that some might say this is a code violation but let me explain my reasoning. Because I am using GFPs the maximum ground fault current on the array side is limited to 1A, at which point the system becomes ungrounded or possibly a positive grounded system depending on the location of the fault. At 1A a 14ga wire would be more than adequate. Given that the grounding wires from the GFPs are 10ga and I have two GFPs, the negative side of my system is actually ground with two 10ga conductors.
Since a 1A ground fault will only disconnect the arrays, the real question is what size conductor was needed to ground my PSDC, the cases of my MX60s and my inverters. Since the breakers supplying the inverters are the largest, they will control. With 250A breakers, the maximum fault current should be limited to something near 250A. Therefore, I needed a ground conductor that could carry 250A for the short time it would take to trip a 250A breaker. Table 250-122 indicates that a 4ga wire should be adequate. However, I used a 1ga wire to be extra safe. This wire runs from the GBBs in my PSDC to the ground rod for my house. To put things in perspective, the 1ga wire is twice the size of the wire grounding my 200A service entrance panel. If you want to go larger than what I used, keep in mind that the largest wire an OB GBB can accommodate is 1/0 and it could be a tight fit.
Robert
690.45 discusses equipment grounding conductors when using ground-fault equipment (you can use table 250.122) and 250.166(c) allows use of #6 copper grounding electrode conductor if that is the only connection to the grounding electrode. You must verify these yourself to make sure they apply to your specific situation.