Post by DavidB » Thu Oct 23, 2003 6:14 am

Looking at the retail price list descriptions on the web site, it looks like there are errors in the descriptions under the PSAC section. The description for the PSAC-100Q and PSAC-60Q are exactly the same.... and doesn't the 60D also bypass both legs?

<small>[ October 23, 2003, 08:15 AM: Message edited by: DavidB ]</small>

Robin Gudgel

PSAC Price list descriptions

Post by Robin Gudgel » Tue Oct 28, 2003 5:13 am

The PSAC60Q and 100Q are the same except for the bypass breaker size and price. Use the 100Q when your generator is over 12KW. The 60D is indeed made to bypass leg1 and leg2. The Quad PSAC series will be a better choice though. You also get all of the input and output terminal busbars with the Q's. We only supply half of them on the 60D.You would still need to add 2 red and one black TBB. You also get 4 50 amp breakers in addition to the bypass breakers on the quad system. These can be used as 4 inverter output breakers on a quad system or 2 input and 2 output on a dual system. Then you still have the quad bypass slider for future expansion. Cost ends up very similar in either case.