Can I use the AC-10B-60 bypass switch with a Trace T-240 transformer using it in a Generator Balancing configuration? If so, how would the wiring differ from the Outback X-240 wiring as pictured on page 2 of the Balancing configuration drawing?
Trace has the QOU breaker basically turned 180 degrees from what is shown. Any information would be appreciated. Thanks. [img]images/smiles/icon_confused.gif[/img]
AC-a0B-60 bypass switch use with Trace T-240 transformer
Moderators: OutBack Moderator Team, OutBack
-
Christopher
AC-a0B-60 bypass switch use with Trace T-240 transformer
Yes - the Trace T-240 and the OutBack X-240 are very similar. The breaker can be used either direction - the transformer can be connected on the bottom or top terminals - it makes no difference for this type of breaker.
So - either diagram would work. Basically there are four wires from the autotransformer - two connect to the neutral and the other two go one to one AC hot leg and the other to the other. The trick is figuring out which go where. Fortunately they should be labeled.
Hope this helps - if not let me know!
So - either diagram would work. Basically there are four wires from the autotransformer - two connect to the neutral and the other two go one to one AC hot leg and the other to the other. The trick is figuring out which go where. Fortunately they should be labeled.
Hope this helps - if not let me know!