Ampere ratings on bus bars?
Moderators: OutBack Moderator Team, OutBack
-
auroraenergy
- Forum Member
- Posts: 10
- Joined: Wed Jul 07, 2004 2:25 pm
- Location: Annapolis, MD
Ampere ratings on bus bars?
What are the ampere ratings on the TBB and BB bus bars that are used in the PSAC & DC enclosures?
Jason Fisher
-
Scott Payne
-
auroraenergy
- Forum Member
- Posts: 10
- Joined: Wed Jul 07, 2004 2:25 pm
- Location: Annapolis, MD
-
Christopher
Re: BB Ampere rating?
The BB is designed to handle up to 1000 amps (four 250 amp breakers or four 4/0 AWG cables). This is also the maximum current rating of the PSDC enclosure. The PS2DC enclosure is rated at a maximum of 500 amps and doesn't usually need a BB in it.auroraenergy wrote: Just checking on what the ampere rating is for the BB.
Thanks,
The TBB's rating is a little more confusing - the 185 amp rating is actually from one end to the other for carrying current - when you make the AC source connection in the middle it can carry twice that as the current can flow in two directions - so using it with 200 amp circuits is acceptable as long as some thought is used in layout the connections. I argued this with a number of UL inspectors over the years and always got them to approve it. 200 amps is the maximum rating on the PSAC and 100 amps for the PS2AC encloures.