My FLEXnet DC “charged voltage” is set at 54V. The manual says to set this .4V below absorb voltage, 56.8V on my system. My sales/installer guy says this doesn’t matter but the manual says that the Mate3 can use the FLEXnet DC’s information to stop all charging. My system never gets above 53.5V even though the charge controllers are in ‘bulk’ mode. Is my installer correct or should I reset the “charged voltage” on the FLEXnet DC?
Any help is much appreciated,
Gerry Smith
Does Low “charged voltage” stop charging early?
Moderators: OutBack Moderator Team, OutBack
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Does Low “charged voltage” stop charging early?
Potentially, but not likely unless Global Charge Termination Control is enabled.
OutBack Power's Global Charge Termination Control is a system setting used via an OutBack MATE to automatically stop the absorption charging phase when connected battery parameters are fully met. It does not affect Bulk charging.
Check under Mate/Global Charge and if enabled, either disable, or if it would benefit your battery, properly set the FNDC Charged Voltage, Charged Time, and Charged Return Amps.
The latter you may wish to do in any event so the battery state of charge reading is more accurate.
Regarding not fully charging the battery:
Are the FlexMax 100 set up with Remote Voltage Sense wiring providing accurate battery voltage data?
Does the inverter/charger fully charge the battery when on generator power?
OutBack Power's Global Charge Termination Control is a system setting used via an OutBack MATE to automatically stop the absorption charging phase when connected battery parameters are fully met. It does not affect Bulk charging.
Check under Mate/Global Charge and if enabled, either disable, or if it would benefit your battery, properly set the FNDC Charged Voltage, Charged Time, and Charged Return Amps.
The latter you may wish to do in any event so the battery state of charge reading is more accurate.
Regarding not fully charging the battery:
Are the FlexMax 100 set up with Remote Voltage Sense wiring providing accurate battery voltage data?
Does the inverter/charger fully charge the battery when on generator power?