Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
Hi all,
I’m fully off-grid in rural central Portugal (near Coja, Arganil, Coimbra district,) unusual setup, I’ve been trying for a while to find a technician to complete the AC wiring on my 24V system. I’ve had a few local electricians visit and decline, I think the OPzS bank is spooking them, or the fact the gear is secondhand.
My system:
•OutBack VFX3024E (3000W, 24V)
•Two OutBack FLEXmax MPPT charge controllers
•OPzS 800Ah battery bank
I have tested the system & it’s functioning fine, I just need someone to complete the AC side, I don’t have the tools, or the confidence. I’m not looking for a general domestic electrician; I need someone who actually knows this equipment and isn’t intimidated by flooded cell batteries.
Long shot, but does anyone know of an installer or technician operating in Central Portugal or willing to travel. Any ideas gratefully received.
Thanks
I’m fully off-grid in rural central Portugal (near Coja, Arganil, Coimbra district,) unusual setup, I’ve been trying for a while to find a technician to complete the AC wiring on my 24V system. I’ve had a few local electricians visit and decline, I think the OPzS bank is spooking them, or the fact the gear is secondhand.
My system:
•OutBack VFX3024E (3000W, 24V)
•Two OutBack FLEXmax MPPT charge controllers
•OPzS 800Ah battery bank
I have tested the system & it’s functioning fine, I just need someone to complete the AC side, I don’t have the tools, or the confidence. I’m not looking for a general domestic electrician; I need someone who actually knows this equipment and isn’t intimidated by flooded cell batteries.
Long shot, but does anyone know of an installer or technician operating in Central Portugal or willing to travel. Any ideas gratefully received.
Thanks
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
Hello,
I would highly suggest contacting our folks at Alpha Outback Energy in Germany.
P: +49 9122 79 889 36
www.alpha-outback-energy.com
-Kim
I would highly suggest contacting our folks at Alpha Outback Energy in Germany.
P: +49 9122 79 889 36
www.alpha-outback-energy.com
-Kim
Technical Support


-
provo
- Forum Emperor
- Posts: 1464
- Joined: Thu Jul 27, 2006 4:34 pm
- My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back - Location: Sierra foothills
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
That's
Alpha and OutBack Energy GmbH
Alpha and OutBack Energy GmbH
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
Why would the AC electrician know, or care about the battery?
Its DC, and has nothing to do with his work.
His part starts at the connections to the main AC load panel which has AC distribution circuits for house loads and a connection to an AC power source.
Does the house need to be wired with AC distribution circuits?
That part will be a standard installation done by the electrician.
The connection to an AC power source will be a 3 wire cable that carries Load, Neutral, and PE. Instead of being supplied by the grid, it is supplied by the inverter at its AC OUT terminals.
The main circuit breaker will be 15A.The cable between the inverter and load panel must be rated for 15A.
If there are items to address on the DC side of the system, the AC electrician will not be the one to ask. It definitely would take a qualified technician with Outback expertise.
Its DC, and has nothing to do with his work.
His part starts at the connections to the main AC load panel which has AC distribution circuits for house loads and a connection to an AC power source.
Does the house need to be wired with AC distribution circuits?
That part will be a standard installation done by the electrician.
The connection to an AC power source will be a 3 wire cable that carries Load, Neutral, and PE. Instead of being supplied by the grid, it is supplied by the inverter at its AC OUT terminals.
The main circuit breaker will be 15A.The cable between the inverter and load panel must be rated for 15A.
If there are items to address on the DC side of the system, the AC electrician will not be the one to ask. It definitely would take a qualified technician with Outback expertise.
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
Thank you, I’ll give that a try. If anyone is closer (Germany is a few countries away,
) I’d still love to hear.
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
I don’t have the answer to all those questions, but I’m don’t have a house & I’m not looking to wire one. I need the hook up between the batteries & the inverter, and two sockets, the cables are as thick as my wrist & they don’t want to do it. They’re local installers used to Hybrid plug & plays systems, or small 12v installs, mine is older Outback gear. There is not a lot of choice of installers here, hence the post.raysun wrote: ↑Tue Apr 28, 2026 1:46 pmWhy would the AC electrician know, or care about the battery?
Its DC, and has nothing to do with his work.
His part starts at the connections to the main AC load panel which has AC distribution circuits for house loads and a connection to an AC power source.
Does the house need to be wired with AC distribution circuits?
That part will be a standard installation done by the electrician.
The connection to an AC power source will be a 3 wire cable that carries Load, Neutral, and PE. Instead of being supplied by the grid, it is supplied by the inverter at its AC OUT terminals.
The main circuit breaker will be 15A.The cable between the inverter and load panel must be rated for 15A.
If there are items to address on the DC side of the system, the AC electrician will not be the one to ask. It definitely would take a qualified technician with Outback expertise.
-
chrisski
- Forum Czar
- Posts: 536
- Joined: Fri May 17, 2024 7:23 pm
- My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity - Location: Central AZ, lowland desert
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
Here is a link to wiring diagrams.
Perhaps these make the install easier for an electrician:
https://outbackpower.com/wiring-diagrams/
There are four diagrams for international flex powers.
I can see why an electrician would not want to take the work with all the hours involved in learning a new system, and possibly coming back to troubleshoot an already broke component.
Might be you need to wire yourself.
I did a different off grid system with a mish mash of gear from a similar system and got a lot of help from the folks at diysolarforum.com. Mine was a 3 kW inverter with 13 kWh battery pack and 3 kW of solar. This was hundreds of hours for me to install.
Perhaps these make the install easier for an electrician:
https://outbackpower.com/wiring-diagrams/
There are four diagrams for international flex powers.
I can see why an electrician would not want to take the work with all the hours involved in learning a new system, and possibly coming back to troubleshoot an already broke component.
Might be you need to wire yourself.
I did a different off grid system with a mish mash of gear from a similar system and got a lot of help from the folks at diysolarforum.com. Mine was a 3 kW inverter with 13 kWh battery pack and 3 kW of solar. This was hundreds of hours for me to install.
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
Yes, it’s stationary & it has been uninstalled.
-
chrisski
- Forum Czar
- Posts: 536
- Joined: Fri May 17, 2024 7:23 pm
- My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity - Location: Central AZ, lowland desert
Re: Seeking installer recommendation – Portugal, VFX3024E + OPzS bank
If I understand this right, this appears to be the AC load center you want installed:
The rest of the install can be done by either yourself or someone.
If it does get installed and you do have a Mate of some variety and an internet connection, anyone in the world can remote in and help you tweak most of your settings. If you can do that, the company in Germany may be your only hope.
For the most part, finding an installer for a piece of equipment that came out a couple decades ago is going to be difficult.
For room and board and an airline ticket, a few of us on the forum would love to go to Europe to help out.
The rest of the install can be done by either yourself or someone.
If it does get installed and you do have a Mate of some variety and an internet connection, anyone in the world can remote in and help you tweak most of your settings. If you can do that, the company in Germany may be your only hope.
For the most part, finding an installer for a piece of equipment that came out a couple decades ago is going to be difficult.