External LFP04 Battery Charger

Post by JRHill » Thu Apr 16, 2026 12:32 pm

@raysun You mentioned you purchased an external charger for your LFP04 batteries. I can't find the post where you told about the external charger.

I may be heading in this direction. Requirements will be 240VAC input. So the mfgr and model you went with and at this point down the line your impressions and anything learned?

I'll add more details but I bought a new to me generator. It's a low RPM single cylinder diesel 6 or 8kW Changfa with Stamford genhead (by Hardy Diesel). It's definately not an inverter generator. When I get it here and start setting things up I won't have to tell you it's running at full load at 1800rpm. If you watch Pacific Coast seismic readings they will register this animal putting away. It is twenty+ years old but barely has two hours of run time. Needless to say this is no cheap Alibaba or Temu junk. My ol Kubota B7100 won't come close to lifting it. If this thing doesn't work out I can scrap it and sell the metals for scrap by the pound and probably end up ahead. :lol: The flywheel is 20" in diameter and probably weighs 50# itself.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: External LFP04 Battery Charger

Post by raysun » Thu Apr 16, 2026 12:44 pm

I usually don't like Chinese designed gear, but the EG4 ChargeVerter GC is a decent 48V LFP charger.
Built around a pair of bog-standard Telco 2 stage battery chargers used in thousands and thousands of switching stations world wide, it's rock solid at up to 100A charge current. (I set it to 75A to run it cooler.)
Constant current to Charge Voltage (absorb) then Constant Voltage until you shut it down.
It has a funky 90's Chinese front panel interface, but is pretty much set once and forget.

I like the fact that battery charging is disconnected from load service. It allows the generator/charger to operate steady-state.

Should work great with a 2000lb Gorilla Diesel.

EG4 Chargeverter - GC | 48V 100A Battery Charger https://share.google/FAP2tZuLg6dt3vLE2

I notice they now have a Plus model for more money that is "smarter" about generator control if you want to go the automated route.

I used the EG4 for over a year instead of my janky dual FXR charging. Never a single complaint. It could run every day if necessary. It's now sitting in backup position because my new inverter and the Honda are so "clean".

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: External LFP04 Battery Charger

Post by JRHill » Thu Apr 16, 2026 1:22 pm

Bingo on the EG4's specs:
AC Input Voltage Range 90-264VAC
AC Frequency 50-60Hz

I may not even mess around with using one leg of the generator through the VFXR. I'm certainly not interested in a big honkin step down transformer and the safety of the VFXR's input from the old school generator's voltage regulator. One thing is for sure, Mary will have no interest in starting the Changfa so if I'm away and she needs to charge batteries all she has to do is run the setup we have in place.

Thanks!

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: External LFP04 Battery Charger

Post by JRHill » Mon Apr 20, 2026 9:44 am

I haven't taken possession of the new genset yet. The original manuals for the engine and the generator head will arrive all together. I have a link to a PDF that covers the 'series' but there are many models within so there are plenty of variations. But I have identified that there are configuration jumpers to select output voltage and hertz for the voltage regulator. What I can not yet determine are wiring changes needed - kind of like changing a 120vac motor to 240 or vv. So I may not need the external battery charger.

Thankfully generator season is over so I have time to acid test the generator. If all is as I expect the unit will have an easy life configured at it's lower end for 6kW but I can only use ~3.6kW through the VFXR. Reaction time to load and release variations in terms of voltage and frequency will be key. But having a 24" flywheel weighing around 50# spinning at 1800RPM will smooth things out nicely (fingers crossed). Having an engine running at high idle with a compression stroke 15x per second is a hoot. You think you can count each hit and puff.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: External LFP04 Battery Charger

Post by raysun » Mon Apr 20, 2026 12:44 pm

Let us know what you find!

I have a MacGyver solution for you to cook your noodle on.

Hook up the 2nd inverter and use it Charger only. Connect it to the battery, do not connect anything to AC Out, set Inverter Mode to Search, set Gen Input Current Limit to some reasonable value (20A perhaps) and make Gen the default profile, program it for the Phi charge profile, then disconnect it from the Hub.
Set the Honda to 240V and create a cable that uses the L14-30 receptacle. On the inverter end, connect L1 and N to the "production" inverter, and L2 and N to the Charger inverter.
The generator will be producing 240V split phase and the inverters will be charging in tandem. The "inverter" inverter will supply house loads as usual, and the "charger" inverter will charge when AC Input is present. Both gensets could be used (singly of course) via a selector switch by some creative cabling.

Or just get a ChargeVerter and hook both generators at 240V to it through a selector.