charging lithium zte zxdc48fb100b3 batteries
I have just switched from lead acid batteries to lithium zte zxdc48fb100 b3. I have 3 of them wired in parrallel . How can I get them fully charged with my flex master 80 ?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: charging lithium zte zxdc48fb100b3 batteries
The battery accepts a broad range of charge voltages from 53.5 to 56.4V
The FlexMAX 80 can be set to any voltage in that range with the Absorb Voltage parameter setting.
The batteries were likely delivered "unconditioned" so may have unbalanced cells. In order to balance the cells initially, run at least 10 charge cycles (a charge cycle completes to Float) with the following parameters:
Absorb Voltage: 55.4V
Absorb Time: 3H
End Amps: 0
Float Voltage: 54.0V
Those parameters can be used permanently. However, if faster charging is desired, adjust to:
Absorb Voltage: 56.0V
Absorb Time: 1H
End Amps: 0
Float Voltage: 54.0V
NOTE: Remove any Remote Temperature Sensor if installed as LFP must not be charged using Temperature Compensated Charging.
In order to charge properly, its important the FM80 be calibrated. Details here:
viewtopic.php?t=15400
Is the inverter used for charging as well?
The FlexMAX 80 can be set to any voltage in that range with the Absorb Voltage parameter setting.
The batteries were likely delivered "unconditioned" so may have unbalanced cells. In order to balance the cells initially, run at least 10 charge cycles (a charge cycle completes to Float) with the following parameters:
Absorb Voltage: 55.4V
Absorb Time: 3H
End Amps: 0
Float Voltage: 54.0V
Those parameters can be used permanently. However, if faster charging is desired, adjust to:
Absorb Voltage: 56.0V
Absorb Time: 1H
End Amps: 0
Float Voltage: 54.0V
NOTE: Remove any Remote Temperature Sensor if installed as LFP must not be charged using Temperature Compensated Charging.
In order to charge properly, its important the FM80 be calibrated. Details here:
viewtopic.php?t=15400
Is the inverter used for charging as well?
-
olenna67
- Forum Junior Member
- Posts: 1
- Joined: Mon Apr 20, 2026 1:57 am
- My RE system: OutBack Radian GS8048A
DuroMax 12 kW
OutBack Mate3s
Re: charging lithium zte zxdc48fb100b3 batteries
You should set your OutBack FLEXmax 80 to lithium-style charging: bulk/absorb around 54.2–54.6V, very short absorb time (≈10–20 min), float low or disabled (~52–53V) Trees Hate You, and turn off equalize so your ZTE ZXDC48FB100B3 batteries can reach full safely. They’ll only hit 100% when held briefly at the correct absorb voltage and the internal BMS finishes balancing, so avoid lead-acid settings or high voltages.
-
Evan
- Forum Junior Member
- Posts: 2
- Joined: Wed Nov 29, 2023 11:56 am
- My RE system: gfx1548 , flex max 80 , mate ,
Re: charging lithium zte zxdc48fb100b3 batteries
I have set my absorb voltage 55.6
my absorbing time to 3 hours
my end amps to 0
my volt to 54
and I have removed my temp sensor
still not completely charging . only filling to the bottom light on each of the 3 batteries . sometimes my arm lights have started blinking.
in the afternoon my appt bulk turns on and it stop s collecting .what am I doing wrong?
my absorbing time to 3 hours
my end amps to 0
my volt to 54
and I have removed my temp sensor
still not completely charging . only filling to the bottom light on each of the 3 batteries . sometimes my arm lights have started blinking.
in the afternoon my appt bulk turns on and it stop s collecting .what am I doing wrong?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: charging lithium zte zxdc48fb100b3 batteries
Are the battery BMS registering any alerts, logs?
Do the FMs show "Ext Chg" when they stop charging?
What is the Out Volts reading when they stop charging?
Do the FMs show "Ext Chg" when they stop charging?
What is the Out Volts reading when they stop charging?