FlexPower 2 system battery minimum battery usage
I have a FLEXPower 2 system with dual FXR3048A-01 inverters, dual FM80 charge controllers, Mate3s, FNDC, and Hub 10.3
It is no longer my active system, but I keep it powered up in an idle state. The inverters are in Search mode, with no AC loads.
In the attached image DC Loads is actually the battery power needed to keep the FP2 turned on. That's pretty darned economical.
:
It is no longer my active system, but I keep it powered up in an idle state. The inverters are in Search mode, with no AC loads.
In the attached image DC Loads is actually the battery power needed to keep the FP2 turned on. That's pretty darned economical.
:
-
Echo5
- Forum Guru
- Posts: 107
- Joined: Tue Aug 08, 2023 2:00 am
- My RE system: FLEXmax 80, VFXR 3024, MATE3s, HUB10, FLEXnet DC, 2x150Ah Sterling LiFePO4 24V batteries, 8x220w panels in 4 strings of 2.
- Contact:
Re: FlexPower 2 system battery minimum battery usage
I live on the north side of a hill. For most of Dec and January I have to turn off the inverter and just let the FM80's tick along. The little power generated at that time of year is not enough to keep the inverter going as well. The power the FM80's do use is given off as heat which helps keep the room the batterys are in a little warmer than ambient.
I really hate seeing the people across the valley bathed in sunlight in late December and they don't even put up solar panels. Insolation Envy is a thing!
I really hate seeing the people across the valley bathed in sunlight in late December and they don't even put up solar panels. Insolation Envy is a thing!
Kimono: Free and Open Source Outback Monitoring software
http://www.OfItselfSo.com/Kimono
http://www.OfItselfSo.com/Kimono
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FlexPower 2 system battery minimum battery usage
Surely your cross-valley neighbors would have no objection to your constructing a heliostat over there. 
-
JRHill
- Forum Emperor
- Posts: 3124
- Joined: Thu Feb 17, 2011 11:12 am
- My RE system: 48v OB inverter and charge controller, hub and mate3s.
- Location: PNW
- Contact:
Re: FlexPower 2 system battery minimum battery usage
I could've written your post to describe us. To add insult to injury the only living things across the canyon are some deer and field mice enjoying their blanket of sunlight. But, that south facing side of the canyon barely has a shrub growing on it while we are in thick forest. On the other hand we will burn in a wild wire but I doubt anybody would care about the grass on the other side burning - except for the smoke.Echo5 wrote: ↑Tue Feb 17, 2026 12:55 amI live on the north side of a hill. For most of Dec and January I have to turn off the inverter and just let the FM80's tick along. The little power generated at that time of year is not enough to keep the inverter going as well. The power the FM80's do use is given off as heat which helps keep the room the batterys are in a little warmer than ambient.
I really hate seeing the people across the valley bathed in sunlight in late December and they don't even put up solar panels. Insolation Envy is a thing!![]()
Heliostat? Wouldn't that be wonderful? But some city hunter/poacher would probably shoot at it.
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: FlexPower 2 system battery minimum battery usage
Puzzled here. If "The inverters are in Search mode, with no AC loads", why does your screenshot show 974W AC loads coming from inverter?raysun wrote: ↑Mon Feb 16, 2026 11:08 amI have a FLEXPower 2 system with dual FXR3048A-01 inverters, dual FM80 charge controllers, Mate3s, FNDC, and Hub 10.3
It is no longer my active system, but I keep it powered up in an idle state. The inverters are in Search mode, with no AC loads.
In the attached image DC Loads is actually the battery power needed to keep the FP2 turned on. That's pretty darned economical.
Screenshot_20260216-085841.png :
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FlexPower 2 system battery minimum battery usage
[/quote]
Puzzled here. If "The inverters are in Search mode, with no AC loads", why does your screenshot show 974W AC loads coming from inverter?
[/quote]
That is my active system which has a non-Outback inverter.
The only "read" of the Outback system on this display is the DC power drawn from the battery.
Puzzled here. If "The inverters are in Search mode, with no AC loads", why does your screenshot show 974W AC loads coming from inverter?
[/quote]
That is my active system which has a non-Outback inverter.
The only "read" of the Outback system on this display is the DC power drawn from the battery.
-
Echo5
- Forum Guru
- Posts: 107
- Joined: Tue Aug 08, 2023 2:00 am
- My RE system: FLEXmax 80, VFXR 3024, MATE3s, HUB10, FLEXnet DC, 2x150Ah Sterling LiFePO4 24V batteries, 8x220w panels in 4 strings of 2.
- Contact:
Re: FlexPower 2 system battery minimum battery usage
The neighbours across the valley surely would object. Except for the odd farmhouse, it's all sheep, sheep and more sheep. The farmers (whom I like and get on with) would never mess up their fields with solar panels or anything like that - just not done. They are way too traditional. Neither will they sell you a small chunk of their land - they would rather sell you their right arm. A farmer without land ain't no farmer and they like being farmers. Normally they are quite an amiable bunch but you sure do get an agressive "hell no" if you suggest they shave off a bit of land and sell it to you. Believe me I've tried.
My solution is going to have to be to overpanel the hell out of things - if I can figure out a way to snap the the arrays off if I exceed the current imput on the FM80. Either that or purchase some more charge controllers and just let them charge the batteries in parallel. Either way I will have a longish run to get the power back to the batteries from anywhere that gets reasonable sunlight.
I had toyed with the idea of using micro inverters and sending it back as 240V AC but then I found out that you have to have an existing AC signal (mains electric) to get those to work. I have heard that there are "off grid" micro inverters in development so maybe in the future some solution will present itself.
Kimono: Free and Open Source Outback Monitoring software
http://www.OfItselfSo.com/Kimono
http://www.OfItselfSo.com/Kimono
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FlexPower 2 system battery minimum battery usage
While its off the reservation there's another solution:My solution is going to have to be to overpanel the hell out of things - if I can figure out a way to snap the the arrays off if I exceed the current imput on the FM80.
Overpanel to your heart's delight, and swap out the FM80 for a charge controller able to carry the freight.
When Simpliphi suggested my FM80s were a source of a failure that cropped up in my battery, I wasted no time in replacing them. Since I was interested in making minimal changes, I used Victron 150V/85A SmartSolar controllers. They bolted straight onto the leads removed from the FM80s and the whole process including configuration took less than an hour. Array configuration, cabling, and circuit breakers were untouched. The "alien" controllers showed up on the FNDC as generic charging sources, and their PV harvest was properly accounted for.
As long as the array V(oc) stays below 150V, and I(sc) below 85A, the system is all good. That leaves some fairly insane headroom for overpaneling. While Victron recommends 30% over (where OB engineers recommended 20% under) as a design target, folks routinely overpanel as much as 100% with these controllers.
I like the FM80s they are fine old workhorses, but they are just that, a 30 year old design. There are modern controllers with more capability.
For not a few folks, the fact that the SmartSolars use dead-silent passive cooling is reason enough to look into updating.
-
chrisski
- Forum Czar
- Posts: 536
- Joined: Fri May 17, 2024 7:23 pm
- My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity - Location: Central AZ, lowland desert
Re: FlexPower 2 system battery minimum battery usage
With that 30% for Victron, isn’t it the 30% of IOC?
I have a smaller Victron charge controller 100/15 for a 24 volt system. I put 3s3p 100 watt panels on this and the SCC maxes out at around 420 watts give or take.
Even though 900 watts seems like it’s excessive, with each string at 6 amps, I am slightly under 30% overage measured at IOC.
I have a smaller Victron charge controller 100/15 for a 24 volt system. I put 3s3p 100 watt panels on this and the SCC maxes out at around 420 watts give or take.
Even though 900 watts seems like it’s excessive, with each string at 6 amps, I am slightly under 30% overage measured at IOC.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FlexPower 2 system battery minimum battery usage
I(oc) can't exist under normal circumstances because an open circuit cannot conduct current.chrisski wrote: ↑Wed Mar 18, 2026 8:38 pmWith that 30% for Victron, isn’t it the 30% of IOC?
I have a smaller Victron charge controller 100/15 for a 24 volt system. I put 3s3p 100 watt panels on this and the SCC maxes out at around 420 watts give or take.
Even though 900 watts seems like it’s excessive, with each string at 6 amps, I am slightly under 30% overage measured at IOC.
The two typical limits: open circuit voltage V(oc) is the measure of array voltage in the state when no current flows and is the highest (temperature adjusted) voltage the array can reach; and I(sc) is the short-circuit current and occurs at 0V as there is no voltage measured across a short circuit.
V(oc) needs to be less than the maximum input voltage allowed by the charge controller. (The 100 in the Victron 100/15).
I(sc) as a limit is a bit slippery. The 15 in the 100/15 is the maximum current output from the controller feeding the battery. With modern equipment that is capable of clipping input current from the PV array, the input current from the PV array can equal the output current. On older controllers like the FM80 which have no input limiting provision, conservative specifications and overcurrent protrction must be employed. The FM80 is rated 80A output, but the maximum current output is actually 113A (don't try this at home) the 80A spec is reflective of the input current provided the input voltage is not such that it exceeds the heat shedding capabilities of the buck circuit (hence the array wattage calculations.)
The whole exercise is to keep the high speed FET switches from turning into high speed silicon fuses.
Without input clipping, FlexMAX controllers are dependent on outside constraints making overpaneling somewhat limited. The white paper discussing nuicance tripping of the 80A battery disconnect shows a solution moving the 80A GFCI to the FM80 input and placing a 100A disconnect on the output.
The modern controllers manage overpaneling in a different manner. Input clipping permits a substantial overspecification of the PV array PROVIDED the input voltage V(oc) does not exceed the controller maximum, and the input current does not exceed the controller output current rating.
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: FlexPower 2 system battery minimum battery usage
May be a good idea if you're off grid but being grid-tied and wanting to keep the integrated sell function where the FM80's collaborate with my FXRs (i.e. holding off selling until an absorb cycle is completed each day), I'm not sure the Victron CC's would work without wholesale upgrading my system with Victron components. Any thoughts?raysun wrote: ↑Wed Mar 18, 2026 1:05 pmWhile its off the reservation there's another solution:My solution is going to have to be to overpanel the hell out of things - if I can figure out a way to snap the the arrays off if I exceed the current imput on the FM80.
Overpanel to your heart's delight, and swap out the FM80 for a charge controller able to carry the freight.
When Simpliphi suggested my FM80s were a source of a failure that cropped up in my battery, I wasted no time in replacing them. Since I was interested in making minimal changes, I used Victron 150V/85A SmartSolar controllers. They bolted straight onto the leads removed from the FM80s and the whole process including configuration took less than an hour. Array configuration, cabling, and circuit breakers were untouched. The "alien" controllers showed up on the FNDC as generic charging sources, and their PV harvest was properly accounted for.
As long as the array V(oc) stays below 150V, and I(sc) below 85A, the system is all good. That leaves some fairly insane headroom for overpaneling. While Victron recommends 30% over (where OB engineers recommended 20% under) as a design target, folks routinely overpanel as much as 100% with these controllers.
I like the FM80s they are fine old workhorses, but they are just that, a 30 year old design. There are modern controllers with more capability.
For not a few folks, the fact that the SmartSolars use dead-silent passive cooling is reason enough to look into updating.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FlexPower 2 system battery minimum battery usage
Charge controllers are fairly autonomous and their basic function (battery charging) is universal enough to be interchangeable among brands.I'm not sure the Victron CC's would work without wholesale upgrading my system with Victron components. Any thoughts?
The unknown for me is how grid tie works. I know the FlexMAX have Grid Tie control which I assume permits the Mate to dynamically control output current, but don't know if there's other functions under the hood. (Though there's not much else a charge controller does.)
So the first question is what would be needed to "grid tie" the Victron gear in the same manner. I have not explored it, but would assume the system controller (Cerbo GX mk2) would be involved.
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: FlexPower 2 system battery minimum battery usage
I misspoke with the example I gave about daily absorb cycle before selling. That's a function between the FNDC and the inverter, so probably not limited for the Victron CC.
The real issue is how the Mate raises the FM80's float target voltage to equal absorb to insure selling. Maybe Victron's controller would be able to do that. I don't know.
The real issue is how the Mate raises the FM80's float target voltage to equal absorb to insure selling. Maybe Victron's controller would be able to do that. I don't know.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: FlexPower 2 system battery minimum battery usage
Looks like its the same closed Charge Controller/Inverter/System Confroller architecture for Victron, but with better developed "brains".