When batteries are low, the inverter doesn't switch back to the grid

Dual Input, 120/240, stainless steel form factor design for unsurpassed surge capability
Post Reply
jmgdebruijn
Forum Junior Member
Posts: 3
Joined: Wed Jan 07, 2026 5:16 pm
My RE system: Outback Radian 4048
OutBack Mate3s
Outback FLEXmax FM60-80

When batteries are low, the inverter doesn't switch back to the grid

Post by jmgdebruijn » Fri Jan 09, 2026 2:30 pm

I am new to the Outback forum, and my question concerns a Radian 4048A with a MidNite Outback Charge Controller, six panels and Surette Batteries

Until recently, the system worked fine. Now, when batteries are low, the inverter doesn't switch back to the grid and makes a clicking sound. We decided to shut it off. Usually, it switches automatically without a problem.

Based on our settings, we discharge the batteries till 50% SOC.
The system is connected to the grid but doesn’t export power to it.

Can anyone tell me what is happening and how I can fix the problem?

Thanks in advance.


Joost

raysun
Forum Overlord
Posts: 13673
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: When batteries are low, the inverter doesn't switch back to the grid

Post by raysun » Fri Jan 09, 2026 5:23 pm

Any messages in the event log?
If the Grid AC is not within tolerance, the inverter will reject it.
The clicking is likely the AC transfer relay. It could be the AC input circuit is failing.
There are two AC inputs, labeled Grid and Gen. They are electrically identical, and either can be used to accept any type of AC input. Try switching the Grid AC feed wires to the other AC input.

chrisski
Forum Czar
Posts: 537
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: When batteries are low, the inverter doesn't switch back to the grid

Post by chrisski » Sun Jan 11, 2026 4:31 am

jmgdebruijn wrote: ↑
Fri Jan 09, 2026 2:30 pm
I am new to the Outback forum, and my question concerns a Radian 4048A with a MidNite Outback Charge Controller, six panels and Surette Batteries

Until recently, the system worked fine. Now, when batteries are low, the inverter doesn't switch back to the grid and makes a clicking sound. We decided to shut it off. Usually, it switches automatically without a problem.

Based on our settings, we discharge the batteries till 50% SOC.
The system is connected to the grid but doesn’t export power to it.

Can anyone tell me what is happening and how I can fix the problem?

Thanks in advance.


Joost
I recommend messaging Outback support.

Sounds like-it could be a relay in the PCBA assembly. This is three circuit cards that cost $2k. If this is correct, support may help to narrow it down to one much cheaper circuit card.
Last edited by chrisski on Sun Jan 11, 2026 5:46 am, edited 1 time in total.

jmgdebruijn
Forum Junior Member
Posts: 3
Joined: Wed Jan 07, 2026 5:16 pm
My RE system: Outback Radian 4048
OutBack Mate3s
Outback FLEXmax FM60-80

Re: When batteries are low, the inverter doesn't switch back to the grid

Post by jmgdebruijn » Sun Jan 11, 2026 5:41 am

Thanks for your feedback. It is very much appreciated. I will check things out.

chrisski
Forum Czar
Posts: 537
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: When batteries are low, the inverter doesn't switch back to the grid

Post by chrisski » Sun Jan 11, 2026 5:48 am

I have not gotten my radian to automatically switch to the grid or battery based off SOC or Voltage ever.

I am constantly doing this manually by tweaking timed strategies every few days.

jmgdebruijn
Forum Junior Member
Posts: 3
Joined: Wed Jan 07, 2026 5:16 pm
My RE system: Outback Radian 4048
OutBack Mate3s
Outback FLEXmax FM60-80

Re: When batteries are low, the inverter doesn't switch back to the grid

Post by jmgdebruijn » Sun Jan 11, 2026 6:59 am

chrisski wrote: ↑
Sun Jan 11, 2026 5:48 am
I have not gotten my radian to automatically switch to the grid or battery based off SOC or Voltage ever.

I am constantly doing this manually by tweaking timed strategies every few days.
Hmmm, I am new to Outback, but that doesn't seem alright at all. When I have solved the issue, I will let you know.

JRKsolar
Forum Guru
Posts: 163
Joined: Thu Aug 20, 2020 11:35 am
My RE system: Outback GS8048A
4) Kilovault HAB 7.5
2) Outback Flexmax 100 AFCI
12) Mission Solar 375W
8) Canadian Solar 395W
Tigo TS4-A2F

Re: When batteries are low, the inverter doesn't switch back to the grid

Post by JRKsolar » Sun Jan 11, 2026 7:41 am

Fwiw, I run mini grid with a connection to the grid and it connects automatically without any problems. Voltage based, not soc in my case.