Decision Time,would like advice

General Talk

Moderators: OutBack Moderator Team, OutBack

Post Reply
josephL
Forum Junior Member
Posts: 1
Joined: Thu Sep 18, 2025 1:39 pm
My RE system: 24 volt lead acid SBS batteries 625 AH (I think)
GVFX 3524 inverter
Flex Max 100 100Adc 300dc charge controller with Flexware 500
Mate 3
8 300 watt panels

Decision Time,would like advice

Post by josephL » Wed Oct 01, 2025 9:21 am

My situation, that I’m posting here because I’m not sure where it fits best. The equipment in my profile has now been up and running for 7 years. The problem; I keep the house heated and running year round with a demand boiler. We don’t live in the house which is 60 miles away and has a 3/4 mile difficult access road. Batteries still have about 3/4 of there original oomph, maybe more. Getting in and out in the winter for me has become more of a challenge at nearly 75 years. I’d like to hook up to the grid but that’s going to cost 40K +. Wondering if LFP batteries with more amp hours tied to a Kohler generator would be reasonable consideration. Have no idea if that would work with my equipment? Currently I have a Westinghouse propane generator tied to an Atkinson generator starter. It does work, but fails periodically when it’s cold and has to be manually rebooted. Also wondering if the Kohler 6kw dc generator might work for me. Ideally, getting read of the lead acid batteries wouldn’t break my heart. Any solution would have to involve some level of professional help. Thanks for ANY advice!

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Decision Time,would like advice

Post by raysun » Thu Oct 09, 2025 9:23 am

I'm amazed at the old FX class inverters that keep chugging along. The GVFX was Outback's first design intended for interactive grid connection (a feature not being used here obviously) and it came with some restrictions on the quality of AC power on its AC Input. The general Outback guidance was to use an inverter type generator. The Kohler is not an inverter generator, but has fairly clean output. It *may* be accepted by the GVFX.

Lithium Ferro Phosphate batteries are a boon for off grid systems. Their fast, efficient charging and sealed design are desirable attributes. Their "Achilles heel" is intolerance to freezing temperatures. If that is expected at the location a quality battery with self-heating should be used.

While the GVFX is designed around lead acid batteries, it will work with LFP. The caveat is the inverter's low battery voltage cutoff cannot be relied upon to protect the battery from over discharge. That's not a show stopper as every LFP battery worth its salt has low voltage (and high voltage) cutoff built into the battery management system (BMS). While the cutoff works it shouldn't be used as a normal operating feature. Rather it's purpose is emergency protection. That's where proper capacity planning and backup charging come into the picture.

LFP batteries have inherently greater usable capacity. 80% of the total Ah capacity is a typical operating guideline. A significantly larger usable capacity battery bank can easily be deployed. All it takes is $$.

LFP come in several form factors. There are "12V drop in replacement" batteries with case sizes similar to lead acid. I don't suggest them for your setup. The "server rack" batteries at native syatem voltage (24V in this case) are a good choice. 24V @ 200Ah is a typical module, and the better quality designs allow modules to be stacked for massive total capacity. The third type are loosly referred to as "Energy Storage Systems" (ESS). These are either wall mounted or in a chassis on wheels to make for easy placement. They too have a "stackable" design that allows for easy capacity expansion.