Hi everyone,
I’m having an issue with my FM100 charge controller where it doesn’t retain any of my configuration after a power cycle. I’m in the middle of a battery replacement and have had to power the system off/on several times. Every time the FM100 boots, all parameters revert to factory defaults, including charging voltages/times and battery type. As a result, the controller briefly targets the factory voltage, which is too high for my bank, and the battery BMS enters over-voltage protection.
Support help was not helpful. They suggest a factory defaults the fm100 and replace the utp cables.
Thanks

-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Post
by raysun » Sun Sep 28, 2025 8:49 pm
IDK much about the FM100 and the factory reset issue but is it possible to work around it by disconnecting the solar panels? It won't help the parameter values getting reset, but will keep the charger from (mis)charging the battery. Once the battery is set up, the FM100 can be reprogrammed and the panels reconnected.
-
chrisski
- Forum Czar
- Posts: 536
- Joined: Fri May 17, 2024 7:23 pm
- My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
- Location: Central AZ, lowland desert
Post
by chrisski » Mon Sep 29, 2025 4:18 am
This is an unresolved issue for some of us.
I have a case open with support with no good conclusion.
Whenever one of my FM100s is powered down, for both solar in and 48 volt connection it reverts to factory selections which causes a an overvoltage to my lithium battery when charging.
Occasionally, the FM100 gets a red fault light requiring reset again to make the fault go away.
AFIK, all a user can do is route the network cable to a different port to see if the error follows and then replace the network cable.
There is no “perform factory reset upon power down setting.”
I think the internal memory on some of these FM100s is shot and not replaceable at our level.
-
dtich
- Forum Guru
- Posts: 109
- Joined: Mon Jul 17, 2023 2:47 pm
- My RE system: 12x Sunpower e20 435; approx 5.2kW; Flexmax100 AFCI; FlexnetDC; Radian 8048; 2x Discover AES 48-6650 (260Ah); Kohler 12RES Gen; completely off-grid, island in NE U.S.
Post
by dtich » Tue Dec 02, 2025 10:59 am
really love this issue to be addressed if not solved.
it makes remote management very difficult.
my only solution is startup with pv input off, confirm/adjust settings, close breaker for panels and start normal charging.
BUT, this can only be done onsite.
makes the system a bit finicky coming out of winter. it would be really great if i could count on the system starting up in a proper mode with correct settings and getting itself back on track. but i can't.