Panel Array Addition Flexmax 80
Moderators: OutBack Moderator Team, OutBack
-
clark99w
- Forum Junior Member
- Posts: 4
- Joined: Tue Aug 19, 2025 2:47 pm
- My RE system: 4 panel array at 2000 watts, Outback Flexmax 80, Magna Sine 4024 Inverter, 4 6V S6-L16-HC Deep Cycle Rolls Batteries
Panel Array Addition Flexmax 80
Wondering if someone can help me out on the consequences of tying in another panel array to my charge controller. I have 4 panels in my current array sending 2000W to a Flexmax 80. The problem I have is that the sun gets too low in the winter and my batteries have been losing charge and freezing (northern canada, gets cold, they are 4 6v Rolls deep cycle L16s). I am looking to add in another set of older panels, near vertical, that will work as trickle charge panels in the winter months (won't ever be contributing much to the load I use in summer). The older panels (2 of them) are 123W each, tied in series for 250W. My question is whether tying these panels in to the Flexmax 80 will restrict/cap the wattage being produced by the system if I tie them in. My current panels run on two 15 Amp DC breakers. The new panels will have their own 15 amp DC breaker, so no conflict there. Any other consequences to tying them in would be great to note before I do so.
-
raysun
- Forum Overlord
- Posts: 13673
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Panel Array Addition Flexmax 80
The specifications of the two panel types would be very helpful. The critical info is V(oc), I(sc) and V(mp)
Also, how the existing panels are wired into an array. Is it 2 panels in series, 2 strings in parallel?
Also, how the existing panels are wired into an array. Is it 2 panels in series, 2 strings in parallel?
-
clark99w
- Forum Junior Member
- Posts: 4
- Joined: Tue Aug 19, 2025 2:47 pm
- My RE system: 4 panel array at 2000 watts, Outback Flexmax 80, Magna Sine 4024 Inverter, 4 6V S6-L16-HC Deep Cycle Rolls Batteries
Re: Panel Array Addition Flexmax 80
The existing panels run at a Voc 50.7V, Isc 13.81A, and Vmp 550W and are wired in as two strings in parallel
New panels I'm adding are also wired as two in parallel. They are Voc 21.76V, Isc 7.99 A, Vmp 123W
New panels I'm adding are also wired as two in parallel. They are Voc 21.76V, Isc 7.99 A, Vmp 123W
-
raysun
- Forum Overlord
- Posts: 13673
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Panel Array Addition Flexmax 80
Are the existing panels wired 2S2P? That would result in a V(oc) slightly over 100V
The new panels, wired 2S would have a V(oc) around 43.5V
The mismatch would be difficult for a single controller to manage effectively. Rewiring the existing array 4P would lower its voltage to 50V, closer to the 43.5 of the new 2S string, but still a mismatch that will compromise performance.
The ideal would be to get a 2nd small controller for the "winter" panels. A Victron SmartSolar 100/15 would more than fill the bill.
The next option would be to switch off the "summer" panels and switch on the "winter" panels in winter, then reversing the arrangement in summer.
The last option is to try them all in winter and turn off the "winter" panels in summer.
Nothing will break trying the options, but may lead to poor performance due to the mismatch of array strings.
-
clark99w
- Forum Junior Member
- Posts: 4
- Joined: Tue Aug 19, 2025 2:47 pm
- My RE system: 4 panel array at 2000 watts, Outback Flexmax 80, Magna Sine 4024 Inverter, 4 6V S6-L16-HC Deep Cycle Rolls Batteries
Re: Panel Array Addition Flexmax 80
Perfect. Thanks. I'll switch off the summer panels for the winter charging at the breaker box. Don't need the wattage produced by the winter panels in the summer as they are too small to do much.
-
raysun
- Forum Overlord
- Posts: 13673
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Panel Array Addition Flexmax 80
So the drill will be to turn off the summer panels in winter, and the winter panels in summer, so a mismatch won't be present during either season?
That works.
-
clark99w
- Forum Junior Member
- Posts: 4
- Joined: Tue Aug 19, 2025 2:47 pm
- My RE system: 4 panel array at 2000 watts, Outback Flexmax 80, Magna Sine 4024 Inverter, 4 6V S6-L16-HC Deep Cycle Rolls Batteries
Re: Panel Array Addition Flexmax 80
Looking at another option on this that I'm assuming would be best which is just adding in another 2 500W panels in series rather than trying to work with the old panels. Assuming that the Flexmax 80 will be fine handling that total 3000 Watt load.
-
raysun
- Forum Overlord
- Posts: 13673
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Panel Array Addition Flexmax 80
Load depends on battery voltage.
48V - 4000W PV
24V - 2000W PV
12V - 1000W PV
48V - 4000W PV
24V - 2000W PV
12V - 1000W PV