SOLVED: Loose DC Neg Terminals UDATED 6-29-25
-
johnstel
- Forum Member
- Posts: 19
- Joined: Fri Jun 13, 2025 3:02 pm
- My RE system: GS8048a, 16 12v 125ah AGM in 4S4P configuration into busbar, all cables on batt side of 2/0, Midnight Solar Classic 150, 16 220w panels in 4S4P config, Each string has a combiner (using one port) with 20a fuse and disconnect, 2nd 20a breaker for each inside before busbar to charge controller. This system runs 3 bedrooms, refrigerator and 3/4hp(?) 220vac well pump (200' down and 10awg wire). The bedrooms & refrigerator have their own load center with back-feed breakers to the commercial load center. All rooms have one GREY outlet fed by the solar load center. Well pump has it's own load center by the meter & setup same as inside. Siemens FSPD140 whole house surge protection at commercial and inverter load centers. Can switch house and well independently.
SOLVED: Loose DC Neg Terminals UDATED 6-29-25
Solved: Diggin deep I found one module had temps significantly higher than the other. Digging more, discovered the config parameter for inverter load sharing. It was AUTO by default. I changed to BOTH so that one module is not "sleeping or Resting" while in small loads condition. It typically has about 3-4 amps load. When the pump kicks on, both modules are ready and share the load. No more Loose DC NEG Terminals error. Pump ran several times today with no faults.
Without OpticssRE, I would never have discovered this.
----------------------------------------------------------------------------------------------------------------------------
New install of the GS8048a and Midnight Classic 150.
UPDATE: June 29, 2025
The error of "Loose DC Neg Terminals" has been replaced with "Batt Volt Sense Fault GS-1". I did like some members said, isolate one string of batteries at a time and see if the well pump 23aac inrush causes the error. The error remained on each pass of removal of a string. After that, the WhizBang Jr and 500a shunt for the Midnite Solar Classic 150 arrived from Stellavolta and I installed it. The Midnite CC recognizes the WhxBang Jr and all is well on that front. HOWEVER: That is when the error "Batt Volt Sense Fault GS-1" began when the well pump turned on. Troubleshooting this, I disconnected the CC and the only AC load was the well pump. With a DC Clamp meter on DC volts, MAX and Min memory set, It recorded a .8vdc drop momentarily when the well pump turns on. Several repetitions of this and the same - .8v momentary drop. The GS8048a battery charger feature is disabled and it does not have the battery sense or sensor/shunt.
I don't think a .8v drop should cause the inverter to shut down with an error condition. Searches online seem to align with this understanding.
Is there a config parameter that I can set to decrease the sensitivity or turn off the battery sense feature?
NOTE: I know the GS8048a is behind on firmware at 1.6.63. I've downloaded 1.6.70 from OB website but am nervous to install it with OB tech support having gone dark. Don't want to be blamed if something goes wrong. I read the firmware notes and didn't see anything related to this error.
Below is the streaming data from inverter to MAte3s, if it helps. I haev the xml config file as well.
LEE+P@=PS 03P 508
{"devstatus": {
"Gateway_Type": "Mate3s","Sys_Time": 1509726289,
"Sys_Batt_V": 53.6,
"ports": [
{ "Port": 1, "Dev": "GS","Type": "60Hz","Inv_I_L1": 1,"Chg_I_L1": 0,"Buy_I_L1": 0,"Sell_I_L1": 0,"VAC1_in_L1": 0,"VAC2_in_L1": 0,"VAC_out_L1": 120,"Inv_I_L2": 2,"Chg_I_L2": 0,"Buy_I_L2": 0,"Sell_I_L2": 0,"VAC1_in_L2": 0,"VAC2_in_L2": 0,"VAC_out_L2": 121,"AC_Input": "Gen","Batt_V": 53.6,"AC_mode": "NO AC","INV_mode": "Inverting","Warn": ["none"],"Error": ["none"],"AUX": "disabled","RELAY": "disabled"}
]}}
LEE#P@=PPf5P244
{"sys_battery": {
"today_min_batt": 49.6,"today_min_batt_time": 1509697319,"today_max_batt": 55.2,"today_max_batt_time": 1509725751,"sys_min_batt": 49.6,"sys_min_batt_time": 1509697319,"sys_max_batt": 55.2,"sys_max_batt_time": 1509725751
}
}
ALL guidance is most welcomed.
Many Thanks!
END OF UPDATE 6-29-25
UPDATED Diagnostic data: The Midnight charge controller captured the inverter shut down event when well pump switched on. In the screenshot, the pink line is charge controller AMPS out and the yellow line is battery voltage. There was a spike in amps and battery voltage did not change. Spike in Amps from charge controller was from 3.5a to 31.4. Battery bank voltage remained unchanged.
I had two Xantrex SW3012 in series (220v) with four 12v 40a chargers. A nearby lightning strike killed the Xantrex inverters, Again, second time in 10 years. Battery bank was reconfigured from 12v to 48v using existing cables. (The Xantrex inverters ran the well previously.)
All is fine until the well comes on and the GS8048a stops inverting with the "Loose DC Neg Terminals" error. Acknowledge error and turn on inverter and all is fine. I read the thread on this topic from 2023 (very helpful).
System Details:
GS8048a (one)
-16 125a AGM batteries in 4S4P config. Battery voltage 53v
-One Midnight Solar Classic 150 charge controller
-(Whizbang Jr and 500a shunt on the way)
-16 220w 12v panels in 4S4P config charges bank as expected.
-I can individually switch the refrigerator, three bedrooms and well pump between commercial power and solar.
I installed two Siemens FSPD140 whole house surge protectors in hopes they will help with untrustworthy Alabama Power, lightning, brownouts etc. Installed just prior to installing the GS8048a. One is at the main disconnect load center next to the meter, and one is on the inverter load center in the garage.
Well Pump Details:
-220vac L1, L2,N believed to be a 3/4hp(?) at 200ft +-
-Online research shows the inrush and running consistent with 3/4hp.
-No pump controller or soft start device is found above ground.
-Pump has good pressure and flow.
Troubleshooting Details:
I read the thread on this error from 2023 and see no other things to check.
Mate3s shows .2kw running refrigerator and three bedrooms worth of lights and two TVs and electronics.
Without OpticsRE (cannot establish an account) I don't know how to get more performance history from the inverter.
-No current leak on all three wires to pump.
-23amps inrush
-8 amps running
-All cables on the battery side of inverter are 2/0 - terminals tight and cable crimps good.
-Laser temp gun shows no hot spots on battery cables or lugs.
-Checked grounding wires, terminal blocks clamps etc back to the ground rod at the Alabama Power meter, all is good.
-Discovered the max power under settings was set to 1400w. (must be from factory because I did not change that setting). MS Copilot drove me to check that.
-I changed max power to 7300w to leave a safety window on the inverter. This helped and must be on the right track. The pump ran a few times without the inverter shutting down, then it happened again. So, progress was made.
-I changed the max power to 8kw but have not switched the well from commercial power to the inverter to test at 8kw. I wanted guidance from the community first.
The pump ran on the Xantrex inverters but we noticed the lighting in the bedrooms flickered when the pump started. House is all LED lighting. I have an amateur radio in the garage that was connected to the 12v battery bank through a 12v 20a regulator. When the pump kicked in the radio showed no signs of power fluctuations. Now it is hooked to the 48v bank through an old charge controller that has a 12v regulated accessory port. This charge controller is not connected to the panels. No errors on the radio when the GS8048a gets the error and stops inverting.
I've researched soft start devices but they seem a bit pricy for now.
I have a spare soft start capacitor for the geothermal heat pump and considering making my own homebrew soft start device for the pump. Weighing the damage risk to that... UPDATE I did turn on the well pump to see what would happen. Also capturing Mate3s streaming and page refresh data in Wireshark. Not sure it captured the event.
Hopefully there is enough detail above to inspire some guidance from more experienced people (which is likely most of the readers here).
Without OpticssRE, I would never have discovered this.
----------------------------------------------------------------------------------------------------------------------------
New install of the GS8048a and Midnight Classic 150.
UPDATE: June 29, 2025
The error of "Loose DC Neg Terminals" has been replaced with "Batt Volt Sense Fault GS-1". I did like some members said, isolate one string of batteries at a time and see if the well pump 23aac inrush causes the error. The error remained on each pass of removal of a string. After that, the WhizBang Jr and 500a shunt for the Midnite Solar Classic 150 arrived from Stellavolta and I installed it. The Midnite CC recognizes the WhxBang Jr and all is well on that front. HOWEVER: That is when the error "Batt Volt Sense Fault GS-1" began when the well pump turned on. Troubleshooting this, I disconnected the CC and the only AC load was the well pump. With a DC Clamp meter on DC volts, MAX and Min memory set, It recorded a .8vdc drop momentarily when the well pump turns on. Several repetitions of this and the same - .8v momentary drop. The GS8048a battery charger feature is disabled and it does not have the battery sense or sensor/shunt.
I don't think a .8v drop should cause the inverter to shut down with an error condition. Searches online seem to align with this understanding.
Is there a config parameter that I can set to decrease the sensitivity or turn off the battery sense feature?
NOTE: I know the GS8048a is behind on firmware at 1.6.63. I've downloaded 1.6.70 from OB website but am nervous to install it with OB tech support having gone dark. Don't want to be blamed if something goes wrong. I read the firmware notes and didn't see anything related to this error.
Below is the streaming data from inverter to MAte3s, if it helps. I haev the xml config file as well.
LEE+P@=PS 03P 508
{"devstatus": {
"Gateway_Type": "Mate3s","Sys_Time": 1509726289,
"Sys_Batt_V": 53.6,
"ports": [
{ "Port": 1, "Dev": "GS","Type": "60Hz","Inv_I_L1": 1,"Chg_I_L1": 0,"Buy_I_L1": 0,"Sell_I_L1": 0,"VAC1_in_L1": 0,"VAC2_in_L1": 0,"VAC_out_L1": 120,"Inv_I_L2": 2,"Chg_I_L2": 0,"Buy_I_L2": 0,"Sell_I_L2": 0,"VAC1_in_L2": 0,"VAC2_in_L2": 0,"VAC_out_L2": 121,"AC_Input": "Gen","Batt_V": 53.6,"AC_mode": "NO AC","INV_mode": "Inverting","Warn": ["none"],"Error": ["none"],"AUX": "disabled","RELAY": "disabled"}
]}}
LEE#P@=PPf5P244
{"sys_battery": {
"today_min_batt": 49.6,"today_min_batt_time": 1509697319,"today_max_batt": 55.2,"today_max_batt_time": 1509725751,"sys_min_batt": 49.6,"sys_min_batt_time": 1509697319,"sys_max_batt": 55.2,"sys_max_batt_time": 1509725751
}
}
ALL guidance is most welcomed.
Many Thanks!
END OF UPDATE 6-29-25
UPDATED Diagnostic data: The Midnight charge controller captured the inverter shut down event when well pump switched on. In the screenshot, the pink line is charge controller AMPS out and the yellow line is battery voltage. There was a spike in amps and battery voltage did not change. Spike in Amps from charge controller was from 3.5a to 31.4. Battery bank voltage remained unchanged.
I had two Xantrex SW3012 in series (220v) with four 12v 40a chargers. A nearby lightning strike killed the Xantrex inverters, Again, second time in 10 years. Battery bank was reconfigured from 12v to 48v using existing cables. (The Xantrex inverters ran the well previously.)
All is fine until the well comes on and the GS8048a stops inverting with the "Loose DC Neg Terminals" error. Acknowledge error and turn on inverter and all is fine. I read the thread on this topic from 2023 (very helpful).
System Details:
GS8048a (one)
-16 125a AGM batteries in 4S4P config. Battery voltage 53v
-One Midnight Solar Classic 150 charge controller
-(Whizbang Jr and 500a shunt on the way)
-16 220w 12v panels in 4S4P config charges bank as expected.
-I can individually switch the refrigerator, three bedrooms and well pump between commercial power and solar.
I installed two Siemens FSPD140 whole house surge protectors in hopes they will help with untrustworthy Alabama Power, lightning, brownouts etc. Installed just prior to installing the GS8048a. One is at the main disconnect load center next to the meter, and one is on the inverter load center in the garage.
Well Pump Details:
-220vac L1, L2,N believed to be a 3/4hp(?) at 200ft +-
-Online research shows the inrush and running consistent with 3/4hp.
-No pump controller or soft start device is found above ground.
-Pump has good pressure and flow.
Troubleshooting Details:
I read the thread on this error from 2023 and see no other things to check.
Mate3s shows .2kw running refrigerator and three bedrooms worth of lights and two TVs and electronics.
Without OpticsRE (cannot establish an account) I don't know how to get more performance history from the inverter.
-No current leak on all three wires to pump.
-23amps inrush
-8 amps running
-All cables on the battery side of inverter are 2/0 - terminals tight and cable crimps good.
-Laser temp gun shows no hot spots on battery cables or lugs.
-Checked grounding wires, terminal blocks clamps etc back to the ground rod at the Alabama Power meter, all is good.
-Discovered the max power under settings was set to 1400w. (must be from factory because I did not change that setting). MS Copilot drove me to check that.
-I changed max power to 7300w to leave a safety window on the inverter. This helped and must be on the right track. The pump ran a few times without the inverter shutting down, then it happened again. So, progress was made.
-I changed the max power to 8kw but have not switched the well from commercial power to the inverter to test at 8kw. I wanted guidance from the community first.
The pump ran on the Xantrex inverters but we noticed the lighting in the bedrooms flickered when the pump started. House is all LED lighting. I have an amateur radio in the garage that was connected to the 12v battery bank through a 12v 20a regulator. When the pump kicked in the radio showed no signs of power fluctuations. Now it is hooked to the 48v bank through an old charge controller that has a 12v regulated accessory port. This charge controller is not connected to the panels. No errors on the radio when the GS8048a gets the error and stops inverting.
I've researched soft start devices but they seem a bit pricy for now.
I have a spare soft start capacitor for the geothermal heat pump and considering making my own homebrew soft start device for the pump. Weighing the damage risk to that... UPDATE I did turn on the well pump to see what would happen. Also capturing Mate3s streaming and page refresh data in Wireshark. Not sure it captured the event.
Hopefully there is enough detail above to inspire some guidance from more experienced people (which is likely most of the readers here).
Last edited by johnstel on Sat Jul 05, 2025 6:50 pm, edited 7 times in total.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Loose DC Neg Terminals (not 2023 thread)
I think Loose DC Neg Terminals is a catch-all error for many DC voltage drops sensed by the inverter. IIRC, it may also be triggered by ripple voltages in the DC.
If all connections to the battery are proper and sufficient conductor is connected to the Radian (two pair of cables), then I'd take a hard look at the battery.
16 used AGM in 4S4P is fertile ground for buried bad cells.
As a quick and dirty test, connect one series string at a time to the inverter (no charger connection) and with a moderate load, measure the voltage at each 12V monobloc. Note the voltages and repeat for each string. There's a good chance one or (likely) more monoblocs will show a lower than average voltage. These are likely degraded.
Reassemble the battery with the 12 best monoblocs and test the well pump startup.
If all connections to the battery are proper and sufficient conductor is connected to the Radian (two pair of cables), then I'd take a hard look at the battery.
16 used AGM in 4S4P is fertile ground for buried bad cells.
As a quick and dirty test, connect one series string at a time to the inverter (no charger connection) and with a moderate load, measure the voltage at each 12V monobloc. Note the voltages and repeat for each string. There's a good chance one or (likely) more monoblocs will show a lower than average voltage. These are likely degraded.
Reassemble the battery with the 12 best monoblocs and test the well pump startup.
-
johnstel
- Forum Member
- Posts: 19
- Joined: Fri Jun 13, 2025 3:02 pm
- My RE system: GS8048a, 16 12v 125ah AGM in 4S4P configuration into busbar, all cables on batt side of 2/0, Midnight Solar Classic 150, 16 220w panels in 4S4P config, Each string has a combiner (using one port) with 20a fuse and disconnect, 2nd 20a breaker for each inside before busbar to charge controller. This system runs 3 bedrooms, refrigerator and 3/4hp(?) 220vac well pump (200' down and 10awg wire). The bedrooms & refrigerator have their own load center with back-feed breakers to the commercial load center. All rooms have one GREY outlet fed by the solar load center. Well pump has it's own load center by the meter & setup same as inside. Siemens FSPD140 whole house surge protection at commercial and inverter load centers. Can switch house and well independently.
Re: Loose DC Neg Terminals (not 2023 thread)
Thanks Raysun! I hadn't considered bad cells or batteries because they are only about 1 year old. They replaced the old lead acid ones that EOLd themselves. Great idea on isolating the strings one by one. I will do that and report findings.
Thank you,
Thank you,
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Loose DC Neg Terminals (not 2023 thread)
@1 yo, likely they are OK. Doesn't hurt to check.
-
johnstel
- Forum Member
- Posts: 19
- Joined: Fri Jun 13, 2025 3:02 pm
- My RE system: GS8048a, 16 12v 125ah AGM in 4S4P configuration into busbar, all cables on batt side of 2/0, Midnight Solar Classic 150, 16 220w panels in 4S4P config, Each string has a combiner (using one port) with 20a fuse and disconnect, 2nd 20a breaker for each inside before busbar to charge controller. This system runs 3 bedrooms, refrigerator and 3/4hp(?) 220vac well pump (200' down and 10awg wire). The bedrooms & refrigerator have their own load center with back-feed breakers to the commercial load center. All rooms have one GREY outlet fed by the solar load center. Well pump has it's own load center by the meter & setup same as inside. Siemens FSPD140 whole house surge protection at commercial and inverter load centers. Can switch house and well independently.
Re: Loose DC Neg Terminals (not 2023 thread)
UPDATED Diagnostic data: The Midnight charge controller captured the inverter shut down event when well pump switched on. In the screenshot, the pink line is charge controller AMPS out and the yellow line is battery voltage. There was a spike in amps and battery voltage did not change. Spike in Amps from charge controller was from 3.5a to 31.4. Battery bank voltage remained unchanged. I think this is important.
Midnight well pump event captured.jpg
Midnight well pump event captured.jpg
-
chrisski
- Forum Czar
- Posts: 536
- Joined: Fri May 17, 2024 7:23 pm
- My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity - Location: Central AZ, lowland desert
Re: Loose DC Neg Terminals (not 2023 thread)
I had a single Radian 8048 that had no issues keeping up with an Air Conditioner that surged to 70 amps on start up, and when the hard start went bad was in excess of 100 amps. This AC Runs at 4 kW. The AC gives no issues either in grid tied or off grid.
I’m not sure if the Mate has a refresh rate quick enough to pick up a voltage surge and also not a quick enough refresh rate to how max surge amps. My surge amps I mentioned were measured by the AC tech.
I’m just posting this to say that a single 8048 handles an AC with no issues that seems to have more surge than your pump or and I think draws more energy when running.
There’s a world of difference between a laser temp gun and a thermal camera. After using a thermal camera, I think a laser temp reader will only find extremely hot areas if you happen to hit it. A thermal will let you check the whole battery bank at once.
I’m not sure if the Mate has a refresh rate quick enough to pick up a voltage surge and also not a quick enough refresh rate to how max surge amps. My surge amps I mentioned were measured by the AC tech.
I’m just posting this to say that a single 8048 handles an AC with no issues that seems to have more surge than your pump or and I think draws more energy when running.
There’s a world of difference between a laser temp gun and a thermal camera. After using a thermal camera, I think a laser temp reader will only find extremely hot areas if you happen to hit it. A thermal will let you check the whole battery bank at once.
-
johnstel
- Forum Member
- Posts: 19
- Joined: Fri Jun 13, 2025 3:02 pm
- My RE system: GS8048a, 16 12v 125ah AGM in 4S4P configuration into busbar, all cables on batt side of 2/0, Midnight Solar Classic 150, 16 220w panels in 4S4P config, Each string has a combiner (using one port) with 20a fuse and disconnect, 2nd 20a breaker for each inside before busbar to charge controller. This system runs 3 bedrooms, refrigerator and 3/4hp(?) 220vac well pump (200' down and 10awg wire). The bedrooms & refrigerator have their own load center with back-feed breakers to the commercial load center. All rooms have one GREY outlet fed by the solar load center. Well pump has it's own load center by the meter & setup same as inside. Siemens FSPD140 whole house surge protection at commercial and inverter load centers. Can switch house and well independently.
Re: Loose DC Neg Terminals (not 2023 thread)
Thanks for sharing your experience. I agree, the 8048 should handle this pump surge at 23a. Wish I had access to a thermal camera, but it's out of reach and no one I know has one. MY gut tells me I have something configured incorrectly. The batteries handled the rush demand when the Xantrex inverters were in place. I don't think it's a battery issue, but will do the string isolation test to "know" one way or the other.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Loose DC Neg Terminals (not 2023 thread)
31.4A × 240V = 7536W.
That's a heck of a lot of startup power for a 3/4HP pump. What kind is it?
Is the Radian wired to the battery with dual leads? What gauge?
That's a heck of a lot of startup power for a 3/4HP pump. What kind is it?
Is the Radian wired to the battery with dual leads? What gauge?
-
johnstel
- Forum Member
- Posts: 19
- Joined: Fri Jun 13, 2025 3:02 pm
- My RE system: GS8048a, 16 12v 125ah AGM in 4S4P configuration into busbar, all cables on batt side of 2/0, Midnight Solar Classic 150, 16 220w panels in 4S4P config, Each string has a combiner (using one port) with 20a fuse and disconnect, 2nd 20a breaker for each inside before busbar to charge controller. This system runs 3 bedrooms, refrigerator and 3/4hp(?) 220vac well pump (200' down and 10awg wire). The bedrooms & refrigerator have their own load center with back-feed breakers to the commercial load center. All rooms have one GREY outlet fed by the solar load center. Well pump has it's own load center by the meter & setup same as inside. Siemens FSPD140 whole house surge protection at commercial and inverter load centers. Can switch house and well independently.
Re: Loose DC Neg Terminals (not 2023 thread)
Type or pump unknown except 220v L1, L2, N going down to it. Yes both inverter modules are cabled, all cables on the battery side of inverter are 2/0. The spike you see is the inrush current and then inverter shuts down. I measured the inrush and running current with a clamp meter. Inrush is 23 amps and running is 8 amps. Consistent with a 3/4hp pump
-
fcwlp
- Forum Emperor
- Posts: 1416
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
Re: Loose DC Neg Terminals (not 2023 thread)
You have a two-wire pump without a soft-start function, so it is not a Grundfos SQE series. Inrush and running is typical of a 3/4 HP pump.johnstel wrote: ↑Fri Jun 20, 2025 6:44 amType or pump unknown except 220v L1, L2, N going down to it. Yes both inverter modules are cabled, all cables on the battery side of inverter are 2/0. The spike you see is the inrush current and then inverter shuts down. I measured the inrush and running current with a clamp meter. Inrush is 23 amps and running is 8 amps. Consistent with a 3/4hp pump
.
I had a Radian system this past week that was throwing the dreaded "Loose DC Negative Terminals" error. Two things I found:
1) Radian was a retrofit into an old Xantrex install, so I reused the Xantrex dual 250A breaker setup. Noticed on startup of a large load that there was considerable arc flash in one of the breakers. The breakers were not using lugs and did not have ferrules on the 4/0 flexible cables. I replaced both of the breakers with ones with bolted connections and new lugs on the 4/0 cables.
2) I found that the FNDC negative lead at the shunts was loose and tightened.
Not sure which one fixed the issue, but two things to check.
-
johnstel
- Forum Member
- Posts: 19
- Joined: Fri Jun 13, 2025 3:02 pm
- My RE system: GS8048a, 16 12v 125ah AGM in 4S4P configuration into busbar, all cables on batt side of 2/0, Midnight Solar Classic 150, 16 220w panels in 4S4P config, Each string has a combiner (using one port) with 20a fuse and disconnect, 2nd 20a breaker for each inside before busbar to charge controller. This system runs 3 bedrooms, refrigerator and 3/4hp(?) 220vac well pump (200' down and 10awg wire). The bedrooms & refrigerator have their own load center with back-feed breakers to the commercial load center. All rooms have one GREY outlet fed by the solar load center. Well pump has it's own load center by the meter & setup same as inside. Siemens FSPD140 whole house surge protection at commercial and inverter load centers. Can switch house and well independently.
Re: Loose DC Neg Terminals (not 2023 thread)
Thanks for the info. Mine is also a Xantrex replacement. It was a 12v system with one 300a T-fuse. I replaced that with two 175a T-Fuses. All cables are 2/0 and have lugs that I crimped myself (which could be the problem). These cables were used on the old system. No access to a thermal camera. A 500a shunt and Whiz Bang Jr are somewhere in USPS system. Info collected so far from group and onsite point to a bad connection (can't find it) or a failing battery. Next step is to remove one string of four at a time to see if that changes the fault.fcwip wrote
You have a two-wire pump without a soft-start function, so it is not a Grundfos SQE series. Inrush and running is typical of a 3/4 HP pump.
.
I had a Radian system this past week that was throwing the dreaded "Loose DC Negative Terminals" error. Two things I found:
1) Radian was a retrofit into an old Xantrex install, so I reused the Xantrex dual 250A breaker setup. Noticed on startup of a large load that there was considerable arc flash in one of the breakers. The breakers were not using lugs and did not have ferrules on the 4/0 flexible cables. I replaced both of the breakers with ones with bolted connections and new lugs on the 4/0 cables.
2) I found that the FNDC negative lead at the shunts was loose and tightened.
Not sure which one fixed the issue, but two things to check.