unexpected reset to fact defaults

Discussion about the FM100 AFCI Charge Controller
Post Reply
dtich
Forum Guru
Posts: 109
Joined: Mon Jul 17, 2023 2:47 pm
My RE system: 12x Sunpower e20 435; approx 5.2kW; Flexmax100 AFCI; FlexnetDC; Radian 8048; 2x Discover AES 48-6650 (260Ah); Kohler 12RES Gen; completely off-grid, island in NE U.S.

unexpected reset to fact defaults

Post by dtich » Sat May 17, 2025 6:16 am

hello all.

have modest system on island in maine. working very well for 3 years. (prev system worked well for 21 years.)

two winters gone by with the system coming up no issue in the spring. this spring, system up for an hour, then the batteries (discover aes) shutdown. i am not on location so had to remotely diagnose through caretaker, but seems the batteries got into an overvoltage situation. not sure how that is possible. but after trying to restart for over a week, system is finally up and the log clearly shows a reset of the charge controller settings to fact defaults (lead acid, which is too high for li for sure) on the 7th of this month. i have since restored the proper settings and we'll see how she goes, but question is:

how can the cc settings spontaneously reset to default? and, is it possible my caretaker reset it accidentally on the front panel or on the mate3? he does not have admin passcodes so it would have to be on user level access which i assume doesn't include fact default reset.

is it possible the repeated battery cutouts and power downs did this? or any other cause?

grateful for any info on this, as going forward a spontaneous reset is not something i want to entertain.


thanks!

JRKsolar
Forum Guru
Posts: 162
Joined: Thu Aug 20, 2020 11:35 am
My RE system: Outback GS8048A
4) Kilovault HAB 7.5
2) Outback Flexmax 100 AFCI
12) Mission Solar 375W
8) Canadian Solar 395W
Tigo TS4-A2F

Re: unexpected reset to fact defaults

Post by JRKsolar » Sat May 17, 2025 7:45 am

A few of us have seen the same thing. I have 2 fm100s and one of them resets some parameters on a reset. Absorb voltage and time are the ones that concern me. The other cc doesn't do it. Same firmware, purchased about a year apart. For me, it's just a glitch I live with.

chrisski
Forum Czar
Posts: 536
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: unexpected reset to fact defaults

Post by chrisski » Sat May 17, 2025 9:06 am

I have traced the problem you have to whenever a FM100 gets powered down with no solar or no 48 VDC, the charge parameters change.

Every time I power down and power up, at least one of my 4 FM100s charge parameter changed.

I have not caught that happening unless the FM100 loses all power, and it can be different MPPTs.

dtich
Forum Guru
Posts: 109
Joined: Mon Jul 17, 2023 2:47 pm
My RE system: 12x Sunpower e20 435; approx 5.2kW; Flexmax100 AFCI; FlexnetDC; Radian 8048; 2x Discover AES 48-6650 (260Ah); Kohler 12RES Gen; completely off-grid, island in NE U.S.

Re: unexpected reset to fact defaults

Post by dtich » Sat May 17, 2025 11:32 am

thanks for the replies guys.

well, that is concerning. that's not very robust, especially for an off-grid capable system, it should be much more fault tolerant than that. non-volatile memory is your friend.

hm.

so, is the expected behavior after a no-power shutdown that upon restoration of voltage the MATE will restore settings in the charge controller, or... are they just lost and have to be manually re-entered, as i had to do in this case?


thanks !

JRKsolar
Forum Guru
Posts: 162
Joined: Thu Aug 20, 2020 11:35 am
My RE system: Outback GS8048A
4) Kilovault HAB 7.5
2) Outback Flexmax 100 AFCI
12) Mission Solar 375W
8) Canadian Solar 395W
Tigo TS4-A2F

Re: unexpected reset to fact defaults

Post by JRKsolar » Sun May 18, 2025 3:55 pm

I've had it happen a couple times and had to go back and update manually.

dtich
Forum Guru
Posts: 109
Joined: Mon Jul 17, 2023 2:47 pm
My RE system: 12x Sunpower e20 435; approx 5.2kW; Flexmax100 AFCI; FlexnetDC; Radian 8048; 2x Discover AES 48-6650 (260Ah); Kohler 12RES Gen; completely off-grid, island in NE U.S.

Re: unexpected reset to fact defaults

Post by dtich » Thu May 22, 2025 8:09 am

quick question on a related topic:

i notice that the system flips between charge and no charge in the am and pm when sun is weak, it generally does this every few mins for about half hour. is there a setting that would keep this down, so it only flips once or twice. upping the solar array charging cut-in current (currently .6A i think?)? what setting might ameliorate this? or i think there is a time interval setting possible too, can't remember, so it might switch less often? i imagine, while it's not very hard on the system, fewer on/off cycles would likely be better.

thanks for any thoughts.

dtich
Forum Guru
Posts: 109
Joined: Mon Jul 17, 2023 2:47 pm
My RE system: 12x Sunpower e20 435; approx 5.2kW; Flexmax100 AFCI; FlexnetDC; Radian 8048; 2x Discover AES 48-6650 (260Ah); Kohler 12RES Gen; completely off-grid, island in NE U.S.

Re: unexpected reset to fact defaults

Post by dtich » Thu May 22, 2025 9:08 am

also, i note that the system says Absorb has duration of 6hrs when it is actually 3, as set. so it's fine, but curious that it always says 6. is it double the time because... i don't know why it would be.

anyone else see this issue?
Image-125.png
Attachments
Image-125.png

Post Reply