FM60 and FM80 with new panels question

Discussion about the FM100, FM80, and FM60 Charge Controllers

Moderators: OutBack Moderator Team, OutBack

Post Reply
AlohaLife
Forum Member
Posts: 18
Joined: Sun Feb 13, 2022 6:03 pm
My RE system: Outback FXR3048A
Outback FM60
Outback FM80
MATE3S
MidNite Solar E-Panel MNE125AL-PLUS
MidNite Solar MNPV6 combiner
8 420w REC panels
6 285w SolarWorld panels
16 8GGC2-DEKA batteries in one bank
Honda EU3000iS generator not on AGS

FM60 and FM80 with new panels question

Post by AlohaLife » Sun Mar 02, 2025 2:15 pm

Aloha friends. Quick question on my charge controllers. I am looking at swapping my current panels out for the REC Alpha Pure 2 Series 420 watts. The 420s have a VOC of 49.1. My installer said we can do 3 strings with 3 panels each going to the FM80 and 2 strings with 3 panels each going to the FM60 with no issue because we are not going over 150 for the charge controllers. The total VOC of three panels is 147.3 which is indeed under the 150. My question is can the VOC total of the three panels be this close to 150 with no absolutely issue? It seems everything always has a +/- tolerance. I just wanted to check in here and get a second opinion from the experts. Much appreciated!

SumPowerRays
Forum Guru
Posts: 201
Joined: Tue Oct 11, 2022 7:48 pm
My RE system: Off Grid
(1) Flexpower Radian 8048A
MATE3s, HUB 10.3, FN-DC, RTS,
(2) FLEXmax 100 AFCI charge controllers
(12) Northstar Blue 190FT batteries 606 AH
(24) REC 365NP2 Panels.
(4) Arrays of 2190 watts each.
Location: Central Washington State

Re: FM60 and FM80 with new panels question

Post by SumPowerRays » Sun Mar 02, 2025 3:57 pm

If you lool at the "Correction factors for ambient temperatures below 77°F"
NEC Table 690.7.A

You will find that the factor for multipliplication for 76° F is 1.02 which would place you just over the 150 volt limit.

I wouldn't place these 3 panels in series.

AlohaLife
Forum Member
Posts: 18
Joined: Sun Feb 13, 2022 6:03 pm
My RE system: Outback FXR3048A
Outback FM60
Outback FM80
MATE3S
MidNite Solar E-Panel MNE125AL-PLUS
MidNite Solar MNPV6 combiner
8 420w REC panels
6 285w SolarWorld panels
16 8GGC2-DEKA batteries in one bank
Honda EU3000iS generator not on AGS

Re: FM60 and FM80 with new panels question

Post by AlohaLife » Sun Mar 02, 2025 4:18 pm

Much appreciated, and thanks for pointing me to this table. If I understand it correctly then I would be well under the 150 volts if I drop a panel and go with 4 strings of 2 panels in the FM80 and 3 strings of 2 panels in the FM60. Would that be correct?

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: FM60 and FM80 with new panels question

Post by raysun » Sun Mar 02, 2025 7:10 pm

AlohaLife wrote: ↑
Sun Mar 02, 2025 4:18 pm
Much appreciated, and thanks for pointing me to this table. If I understand it correctly then I would be well under the 150 volts if I drop a panel and go with 4 strings of 2 panels in the FM80 and 3 strings of 2 panels in the FM60. Would that be correct?
I've been using REC Alpha 440W panels 2S4P for several years with a pair of FM80s. They work great.
2S3P is perfect for FM60.

AlohaLife
Forum Member
Posts: 18
Joined: Sun Feb 13, 2022 6:03 pm
My RE system: Outback FXR3048A
Outback FM60
Outback FM80
MATE3S
MidNite Solar E-Panel MNE125AL-PLUS
MidNite Solar MNPV6 combiner
8 420w REC panels
6 285w SolarWorld panels
16 8GGC2-DEKA batteries in one bank
Honda EU3000iS generator not on AGS

Re: FM60 and FM80 with new panels question

Post by AlohaLife » Sun Mar 02, 2025 8:54 pm

Thanks for the info. I really appreciate it! I have been looking at those RECs.

Post Reply