AGM Batteries
-
droneflyer14
- Forum Member
- Posts: 5
- Joined: Mon Jul 01, 2019 2:08 pm
- My RE system: 2)VFXR3648A- Inverters
2)FLEXmax 80 Solar Controllers
2)FW - SP - ACA Surge Protectors
HUB10
3 Strings of 8, 6V AGM PV06V27 220ah Batteries.
12 Roof Mounted Solar Panels 330W
6 Ground Based Solar Panels 360W
AGM Batteries
Can you use any AGM Battery with a vfxr3648A inverter?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AGM Batteries
It has to have sufficient Ah rating to meet discharge energy demands, and be a true deep cycle battery, but yes, most any AGM can be used.droneflyer14 wrote: ↑Mon Dec 02, 2024 8:07 amCan you use any AGM Battery with a vfxr3648A inverter?
However, AGM has the shortest cycle life, and highest cost per cycle of all the lead acid configurations. In fact, by those metrics, it's more expensive than LFP. The Chinese 12V @ 100Ah "drop in replacement" batteries, or better yet, the flood of commodity "server rack" batteries at 48V @ 100Ah are good values right now.
By "right now" I mean when Trump starts adding tariffs to Chinese imports, battery prices will skyrocket. Since pretty much all batteries, lead and lithium alike, are made in China, do whatever needs doing before then.
-
droneflyer14
- Forum Member
- Posts: 5
- Joined: Mon Jul 01, 2019 2:08 pm
- My RE system: 2)VFXR3648A- Inverters
2)FLEXmax 80 Solar Controllers
2)FW - SP - ACA Surge Protectors
HUB10
3 Strings of 8, 6V AGM PV06V27 220ah Batteries.
12 Roof Mounted Solar Panels 330W
6 Ground Based Solar Panels 360W
Re: AGM Batteries
Thank you soo much for that heads up!
The rack mounted units that I have seen are lifep04 48v 100ah
They are not compatible with Outback are they?
The rack mounted units that I have seen are lifep04 48v 100ah
They are not compatible with Outback are they?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AGM Batteries
I use 6 SimpliPhi 3.8-48 batteries on my dual FXR3048A-01 and that works great.droneflyer14 wrote: ↑Mon Dec 02, 2024 12:49 pmThank you soo much for that heads up!
The rack mounted units that I have seen are lifep04 48v 100ah
They are not compatible with Outback are they?
My neighbor is using 1 Ruixu LFP48100 on an FX3048T and it works fine too. (This battery has a built-in pre-charge circuit, so starts the inverter no problem.)
I don't have an opinion about ChiComm commodity batteries, other than to say they've improved from total crap to not. Pretty much all of them are made from the same parts, so it's 6-6 and pick 'em when it comes to brands.
This isn't the worst I've seen:
https://www.ruixubattery.com/product-pa ... acket-rack
Free shipping if you drop $3k.
Inverters R Us sells the battery alone for $1095.
My neighbor bought one in Hawaii out of a guy's garage for $1200
EG4, SOK, Pytes, Pylontech, Ruixu. All those ChiComm batteries look alike to me.
-
706jim
- Forum Virtuoso
- Posts: 79
- Joined: Tue Apr 28, 2020 10:52 am
- My RE system: 7x330 watt Canadian solar panels four 470A-h Enerwatt AGM's Flexmax 80 Trace DR1524 Msw inverter Insignia 11.5 cubic foot fridge, 1/4hp GSW piston pump.
My 31st year on solar. - Location: Thunder Bay Canada
Re: AGM Batteries
I switched from Trojan FLA cells to Enerwatt AGM's this summer. I couldn't be more pleased. They have given me more usable power at 468 Ah than my 8 L16's did at 740 Ah. Their price was slightly less than similar sized Trojan FLA's.
As always the real truth will be in the years to follow. My system is fallow for 6 months and then used for the 6 month summer season. The Trojans lasted 9 seasons and I'd be pleased if these lasted even close to this long. I have to consider the winter months when temperatures may go down to -40 which is one reason I haven't looked at lithium cells.
An I do have to mention that I had a 660 Ah set of 12 golf cart FLA's that lasted 19 seasons. The biggest difference this time around is my electric fridge which I installed with the Trojan FLA's. Previously I had a propane fridge that cost nearly $2/day to operate.
As always the real truth will be in the years to follow. My system is fallow for 6 months and then used for the 6 month summer season. The Trojans lasted 9 seasons and I'd be pleased if these lasted even close to this long. I have to consider the winter months when temperatures may go down to -40 which is one reason I haven't looked at lithium cells.
An I do have to mention that I had a 660 Ah set of 12 golf cart FLA's that lasted 19 seasons. The biggest difference this time around is my electric fridge which I installed with the Trojan FLA's. Previously I had a propane fridge that cost nearly $2/day to operate.
-
fyrmd
- Forum Member
- Posts: 5
- Joined: Thu Feb 13, 2025 10:21 pm
- My RE system: FX inverter, Victron 150/70 charge controller, 5 SOK 24v 100AH batteries.
Re: AGM Batteries
What kind of hardware changes/additions need to happen to switch from AGM to Lifep04? Currently have 8 L16 AGM's that need to be replaced.
Thanks
Thanks
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AGM Batteries
LFP are pretty close to AGM in charging profiles, so not much needs changing for FX charging. The MX may or may not be compatible, depending on the LFP battery management system (BMS).
If you depend on the FX Low Battery Cut Out (LBCO) to shut down the inverter to keep from over discharging the battery, it won't work for LFP, because the LBCO Voltage can't be set high enough.
A good battery monitor, like the Victron SmartShunt, or BMV712 will be a valuable addition. If the BMV712 is used, it's relay can control LBCO (and HBCO) for the FX inverter.
-
fyrmd
- Forum Member
- Posts: 5
- Joined: Thu Feb 13, 2025 10:21 pm
- My RE system: FX inverter, Victron 150/70 charge controller, 5 SOK 24v 100AH batteries.
Re: AGM Batteries
Mahalo raysun! I did order a BMV712 yesterday based on some information you shared on another forum. Looks like I can just add this and upgrade my charge controller.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AGM Batteries
I'm using my FXR inverters with Victron SmartSolar 150/85 charge controllers. If replacing the MX, a SmartSolar 150/70 is more than enough with headroom for solar array expansion. If simply replacing the MX60 the SS 150/60 is more than enough. There's not a lot of difference in price between the two.
Coupled with the BMV712, the SmartSolar chargers become high-speed, precision chargers that use the BMV712 for remote battery voltage and current sense.
They are, TBH, a superior match with LFP batteries.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AGM Batteries
If you install VictronConnect on your smartphone, you can easily configure and monitor all Victron "Smart" devices.
Even before having the equipment installed, you can run VictronConnect in the Demo Library and see the features of the whole "Smart" catalog.
*PRO TIP* The BMV712 is about a million times easier to set up using VictronConnect than using the panel display and buttons.
Even before having the equipment installed, you can run VictronConnect in the Demo Library and see the features of the whole "Smart" catalog.
*PRO TIP* The BMV712 is about a million times easier to set up using VictronConnect than using the panel display and buttons.
-
fyrmd
- Forum Member
- Posts: 5
- Joined: Thu Feb 13, 2025 10:21 pm
- My RE system: FX inverter, Victron 150/70 charge controller, 5 SOK 24v 100AH batteries.
Re: AGM Batteries
I'm using my FXR inverters with Victron SmartSolar 150/85 charge controllers. If replacing the MX, a SmartSolar 150/70 is more than enough with headroom for solar array expansion. If simply replacing the MX60 the SS 150/60 is more than enough. There's not a lot of difference in price between the two.
Coupled with the BMV712, the SmartSolar chargers become high-speed, precision chargers that use the BMV712 for remote battery voltage and current sense.
They are, TBH, a superior match with LFP batteries.
[/quote]
Raysun,
This is very helpful and much appreciated!
Coupled with the BMV712, the SmartSolar chargers become high-speed, precision chargers that use the BMV712 for remote battery voltage and current sense.
They are, TBH, a superior match with LFP batteries.
[/quote]
Raysun,
This is very helpful and much appreciated!