Stacking Issue

OutBack's newest innovation in balance-of-system components

Moderators: OutBack Moderator Team, OutBack

Post Reply
ohiodeerejohn
Forum Member
Posts: 14
Joined: Tue Feb 06, 2024 11:59 am
My RE system: VFXR 3648 double stacked with 2 FM 80. 5KW Solar and 1000AH Lithium battery with 20 kw backup natural gas generator.

Stacking Issue

Post by ohiodeerejohn » Tue Oct 29, 2024 4:04 am

Hello every one,
I have FW-500 with 2 VFXR3648 and when I pull try to use a 240 load off of it goes down to 120 off both legs.
Both legs show 120 volt with neutral but if I test both hot legs together it shows 120v.
I tries to change the stacking to master and L2 master but it just gives me a stacking error so I have both on master.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Stacking Issue

Post by raysun » Tue Oct 29, 2024 9:50 am

FX inverters can be stacked in parallel for 120VAC output or in series for 240VAC output.
In parallel stacking, the "L" output leads are wired to the same terminal bus bar. (L1 Out TBB). The inverter "L" input leads are similarly wired to the same terminal bus bar (L1 In TBB).
In series stacking, both "L" output leads (L1 and L2) are wired to separate terminal bus bars (L1 Out TBB and L2 Out TBB.) The inverter "L" input leads (L1 and L2) are wired to separate terminal bus bars (L1 In TBB and L2 In TBB.)
Neutrals are passed through in both configurations. There must be one and only one Neutral to Ground bond. Typically at the main load panel. Alternately, within the FW500 AC panel.

For 240VAC split phase:
• The L1 Master must be plugged into Port 1 of the Hub.
• The L2 Sub phase Master must be plugged into any Hub port, except Port 1 (Port 4 or 7 are frequently used.)

When the inverters are confirmed to be wired correctly, the configuration should be able to be changed to Series stacking (240VAC split phase) without a stacking error.
AC Output Voltages should read:
L1 - N 120VAC
L2 - N 120VAC
L1 - L2 240VAC

Outback FlexPower Two wiring diagram
https://www.outbackpower.com/downloads/ ... id-tie.pdf

User avatar
Mike Curran
Forum Emperor
Posts: 3602
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Stacking Issue

Post by Mike Curran » Tue Oct 29, 2024 1:14 pm

Further clarification:
Master in Port 1 - Stack mode = Master
Screenshot_20241029_160910_Samsung Internet.jpg
Slave in Port 7 - Stack mode = L2 Phase Master
Screenshot_20241029_160929_Samsung Internet.jpg
These settings work for me. Just be sure to wire the outputs as Raysun describes.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

ohiodeerejohn
Forum Member
Posts: 14
Joined: Tue Feb 06, 2024 11:59 am
My RE system: VFXR 3648 double stacked with 2 FM 80. 5KW Solar and 1000AH Lithium battery with 20 kw backup natural gas generator.

Re: Stacking Issue

Post by ohiodeerejohn » Wed Oct 30, 2024 2:29 am

Hey thanks for the help. I double checked the wiring and it was correct so I decided to move the l2 from port 5 to port 4 and that took care of the issue.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Stacking Issue

Post by raysun » Wed Oct 30, 2024 9:20 am

ohiodeerejohn wrote: ↑
Wed Oct 30, 2024 2:29 am
Hey thanks for the help. I double checked the wiring and it was correct so I decided to move the l2 from port 5 to port 4 and that took care of the issue.
Good news!