sudden and unexpected large number of notifications from FM100 AFCI

Discussion about the FM100 AFCI Charge Controller
Post Reply
dasamara
Forum Member
Posts: 12
Joined: Tue Aug 10, 2021 10:22 am
My RE system: Radian Inverter 4048.
FM100-AFCI.
3 x 48V Fortress eFlex 5.4kWh batteries,
8xREC Solar 365AA Panels (in 2 x 4 wiring config),
4xOBFRS01 RS Units w/ RSI box and a generic 24VDC power supply (for raptors connected to incoming grid lines (with input AC and output DC fusing)).
Mate3S
loads on the downstream side of inverter include all kitchen loads, some other lighting loads, and the house's Air Conditioning compressor.
Efergy Engage wireless power sensors for monitoring a few of the branch circuits of home including the 240VAC circuit w/ the inverter
(no internet connection to the inverter or the mate3s)

(in addition, i have 4 other REC Solar panels with microinverters on a separate branch circuit.)

sudden and unexpected large number of notifications from FM100 AFCI

Post by dasamara » Wed Jul 17, 2024 9:24 am

Hi,

last evening there was a "storm" of events being published from my OpticsRE account related to the values recorded in the FM100 fluctuating nonsensically (for lack of better word).

I checked the system on OpticsRE page and see that there were about 3600 CONFIG EVENTS from the CC, a few from COMM, and a few dozen from INV.

At the same time i see that there are 2 consecutive notifications in NON CONFIG EVENTS that the firmware of the FM100 was updated at 7:04am today. the messages both say that initial state was 32768.0.65493 and final state is 2.0.1

I am guessing that some component in the system is failing or needs attention. i presume it is the FM100 based on the very unexpected and sudden large # of such notifications of config change with very strage values of parameters such as battery SOC fluctuating from 100% to 0% and back to 100%, 10kWh of PV appearing at 1am local time, etc.

Please advise.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by raysun » Wed Jul 17, 2024 9:45 am

That does seem strange.
I don't use the FM100, so can't point to it as the "smoking gun".
I think the first thing I would try would be to completely power down the system, then restart it.
Next I would be suspicious of the Mate3s. Reinstalling the latest firmware might clear any corrupted code in memory.
Firmware updates for the FM100, if available next.
Finally, updates for the inverter.
https://www.outbackpower.com/resources- ... re-updates

chrisski
Forum Czar
Posts: 536
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by chrisski » Wed Jul 17, 2024 6:05 pm

I am an FM100 user for six months and I have not had had a message anything like:

"32768.0.65493 and final state is 2.0.1"

I have nothing resembling IP addresses and all mine are related to float voltage, absorb voltage, or other commands that make sense.

dasamara
Forum Member
Posts: 12
Joined: Tue Aug 10, 2021 10:22 am
My RE system: Radian Inverter 4048.
FM100-AFCI.
3 x 48V Fortress eFlex 5.4kWh batteries,
8xREC Solar 365AA Panels (in 2 x 4 wiring config),
4xOBFRS01 RS Units w/ RSI box and a generic 24VDC power supply (for raptors connected to incoming grid lines (with input AC and output DC fusing)).
Mate3S
loads on the downstream side of inverter include all kitchen loads, some other lighting loads, and the house's Air Conditioning compressor.
Efergy Engage wireless power sensors for monitoring a few of the branch circuits of home including the 240VAC circuit w/ the inverter
(no internet connection to the inverter or the mate3s)

(in addition, i have 4 other REC Solar panels with microinverters on a separate branch circuit.)

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by dasamara » Wed Jul 17, 2024 11:09 pm

Hi,

The flood of events continues. And for each of the now many hundreds of emails I am receiving, this message appears in the email:

“ To unsubscribe from automated emails, click on the link below (or copy and paste the URL into your browser): …”

But the link does not work and I cannot figure out how to unsubscribe from the event notifications through the GUI of OpticsRE. I have searched the forums and FAQ’s unsuccessfully.

Can anyone help with this unsubscribe issue?

chrisski
Forum Czar
Posts: 536
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by chrisski » Thu Jul 18, 2024 7:12 am

Sounds like you have an error report being sent by system tools. AFIK, this is the only way to receive E-Mails.
OpticsRE System Tools.png

chrisski
Forum Czar
Posts: 536
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by chrisski » Thu Jul 18, 2024 7:25 am

If this is a continuous flood of errors, including at night, I would unplug the network cable for the Charge COntroller from the networking device to see if this stops the flood. I'd try this at night to prevent production from stopping.

In my Case I have two FM100s on port 8 and port 9 of my Flex Net DC. I'd unplug those just long enough to see if this makes the problem go away.

I don't know hte official term, I call this a soft reset. This does cause the device to reestablish a connection with the other Outback devices.

You could try to get a digital copy of your FM100 settings and posting here so we could take a look at it.

There is the option of doing the factory reset on the FM100, but you'd need to know what you want the settings to be redone to after the reset. Factory settings are probably for AGM, Litium, or FLooded Leaded acid, and unlikely to work with what you want.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by raysun » Thu Jul 18, 2024 9:38 am

I have two FM100s on port 8 and port 9 of my Flex Net DC
Should read:
I have two FM100s on port 8 and port 9 of my Hub 10.3

chrisski
Forum Czar
Posts: 536
Joined: Fri May 17, 2024 7:23 pm
My RE system: Dual 8048 Radian w/ Load Center
Mate 3
Flex max 100 afci X 4
Fortress eFlex 5.1 kWh Battery X 8
TP1000 for Internet Connectivity
Location: Central AZ, lowland desert

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by chrisski » Thu Jul 18, 2024 12:38 pm

@Raysun. Thanks. I'm still learning this system. This is what I see on my device map:
Hub 10.3.png
It is the Hub 10.3

dasamara
Forum Member
Posts: 12
Joined: Tue Aug 10, 2021 10:22 am
My RE system: Radian Inverter 4048.
FM100-AFCI.
3 x 48V Fortress eFlex 5.4kWh batteries,
8xREC Solar 365AA Panels (in 2 x 4 wiring config),
4xOBFRS01 RS Units w/ RSI box and a generic 24VDC power supply (for raptors connected to incoming grid lines (with input AC and output DC fusing)).
Mate3S
loads on the downstream side of inverter include all kitchen loads, some other lighting loads, and the house's Air Conditioning compressor.
Efergy Engage wireless power sensors for monitoring a few of the branch circuits of home including the 240VAC circuit w/ the inverter
(no internet connection to the inverter or the mate3s)

(in addition, i have 4 other REC Solar panels with microinverters on a separate branch circuit.)

Re: sudden and unexpected large number of notifications from FM100 AFCI

Post by dasamara » Tue Jan 14, 2025 1:50 pm

Hi. Thank you for the replies

In the end I just completely shut down system for 15 minutes then restarted. That caused the problem to stop.

The problem returned a month later and I shut down again. Happened a 3rd time in the late Summer. But not since then!

The reason I have returned to the Forum is because of another symptom/problem — for another posting.

Again. Thank you for the responses.