Overpaneling Safe Trip?

Discussion about the FM100, FM80, and FM60 Charge Controllers

Moderators: OutBack Moderator Team, OutBack

Post Reply
Echo5
Forum Guru
Posts: 107
Joined: Tue Aug 08, 2023 2:00 am
My RE system: FLEXmax 80, VFXR 3024, MATE3s, HUB10, FLEXnet DC, 2x150Ah Sterling LiFePO4 24V batteries, 8x220w panels in 4 strings of 2.
Contact:

Overpaneling Safe Trip?

Post by Echo5 » Fri May 03, 2024 3:06 am

Started this thread due to the interesting responses in the 2 or 3 fm80's thread viewtopic.php?t=18671 which got me thinking.

Is there such a thing as a safe "trip" device to remove overpaneled strings from an array if the current climbs too high?

If not, here's two ways I can imagine how it might work:

Method 1: A box with connections in and out that sits in between the wiring of the strings just before they enter the combiner box - simple to retrofit. The current from each string is measured as it flows through the box. A microcontroller sums all the currents and takes strings offline in a designated order as the total current climbs too high. This could be done by something simple like tripping a relay. As the current drops, the string is brought back in. Obviously a hysteresis mechanism would be introduced to avoid chattering the relays on and off.

Method 2: A box similar to Method 1 is placed between the wiring of the strings. All it does is contain a relay which can remove the panel from the circuit. The micocontroller talks to the Mate3s and gets the current on each Charge controller. Above a certain level it trips out the strings like in method 1 and later brings them back again. This method is much simpler to implement than Method 1 since it takes advantage of the measurement circuitry in the Mate3s/FM80 and the rest is just software. But, could it trip fast enough to avoid overcurrent hits to the FM80? The timings are dependent on how fast the web server in the Mate3s gets new data to report and how often it can be polled. I have found with the Kimono monitoring software that polling once per second is no problem and it could probably go more frequently than that. Any ideas how often the Mate3s gets its data and how long the FM80 can sustain an overcurrent before getting damaged?

Of course a ModBus based device could probably talk to the FM80 directly thus eliminating much of the polling delay.

So thats some thoughts - neither of these devices seem to be particularly difficult to engineer. I imagine this has already been done.
Kimono: Free and Open Source Outback Monitoring software
http://www.OfItselfSo.com/Kimono

fcwlp
Forum Emperor
Posts: 1416
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.

I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation.
Location: 80 miles NE of Phoenix at 5500'

Re: Overpaneling Safe Trip?

Post by fcwlp » Fri May 03, 2024 7:42 am

Echo5 wrote: ↑
Fri May 03, 2024 3:06 am
So thats some thoughts - neither of these devices seem to be particularly difficult to engineer. I imagine this has already been done.
Not that I am aware of.
.
It would be more cost effective to combine this capability with the combiner capability. A couple of challenges are going to be:
1) what is the increment of how many strings you will be able to monitor as that will drive the cost of your hardware.
2) Many of the new systems I am putting in do not use a combiner as they are a single string running 250-500 V and 10-20 amps.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Fri May 03, 2024 9:14 am

When I installed new pv panels several years ago, I ran a brief experiment overpaneling an FM80. Ten 440W half-cell panels for a modest 10% over rating. Fired the system up on a typical dynamic-weather day here in Hawaii. Within 10 minutes, the controller was reporting 5200W spike in pv input. These spikes generally occur during "cloud edge" events and happen extremely fast. I opened the pv disconnect. End of experiment.
I ended up, as originally planned, putting 3.5kW arrays on two FM80s. These have been in zero-issue operation ever since.
Even at 3.5kW, the FM80s have reported peaks of 4115W and 4353W. These tend to be highly transient episodes, but I've seen 4kW+ sustained for many minutes on occasion.
Everyone has their own approach, and mine is KISS. Coming from a process-control background, I've found it far better to eliminate potential points of failure, if possible, rather than attempting to regulate them.
I like keeping the magic smoke just where it is.

Here's Outback's approach: https://www.outbackpower.com/downloads/ ... p_note.pdf

Echo5
Forum Guru
Posts: 107
Joined: Tue Aug 08, 2023 2:00 am
My RE system: FLEXmax 80, VFXR 3024, MATE3s, HUB10, FLEXnet DC, 2x150Ah Sterling LiFePO4 24V batteries, 8x220w panels in 4 strings of 2.
Contact:

Re: Overpaneling Safe Trip?

Post by Echo5 » Sat May 04, 2024 1:01 am

>Everyone has their own approach, and mine is KISS. Coming from a process-control background, I've found it far better to eliminate potential points of failure, if possible, rather than attempting to regulate them.

I totally see your point. My problem is that I do not live close to the equator in an area with relatively constant isolation. I live in the UK on the north side of the hill. The weather (even in summer) is usually cloudy and rainy. In the winter, close to the solstice, the solar panels dont get a lot of exposure - some weeks it seems like it is barely enough to power the equipment. So, in this scenario, a system of safe overpanelling would be attractive and possibly worth the risk. For the few times it would actually trigger, maybe something simple like a fast blow fuse on the combined output of the strings into the FM80 could suffice as a fail safe?

>I like keeping the magic smoke just where it is.

Hard to disagree with that! No point in frying the equipment.

As always, thank you for the valuable insights and advice.
Kimono: Free and Open Source Outback Monitoring software
http://www.OfItselfSo.com/Kimono

User avatar
SandyP
Forum Czar
Posts: 601
Joined: Tue Jun 21, 2011 4:44 am
My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset
Location: Victoria, Australia

Re: Overpaneling Safe Trip?

Post by SandyP » Sat May 04, 2024 5:00 am

Echo5 wrote: ↑
Sat May 04, 2024 1:01 am
../..
So, in this scenario, a system of safe overpanelling would be attractive and possibly worth the risk. For the few times it would actually trigger, maybe something simple like a fast blow fuse on the combined output of the strings into the FM80 could suffice as a fail safe?
../..
Have a read of this note from Outback : https://atl.my.site.com/OutbackKnowledg ... on-feature

As I have mentioned on another topic (viewtopic.php?p=105736#p105736) if you do overpanel your FM80 make sure you change the default 80A output to something less and this will result in the FM80 clipping its output which it does not do when the output amps is left at the default maximum.
-------------------------
http://spwebcam.myddns.me/

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Sat May 04, 2024 10:41 am

In for a penny, in for a pound.
Sunny morning here. Some fine ghetto wiring and a 7kW array is attached to an FM80.
Current Limit:75A

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Sat May 04, 2024 11:07 am

To make the conversion, the FM80s were disconnected from the arrays, and the battery.
When brought back online, the active FM80 is behaving as expected, but Optics RE became confused in the process. I do not believe the production numbers for 0700 hour. 😊
Screenshot_20240504_080246_Chrome.jpg

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Sat May 04, 2024 1:44 pm

OK. That was fun and informative.

TL;DR:
Setting FlexMax Current Limit below 80A does cause the controller to clip the PV input.
(Thanks @SandyP for pointing the way.)

There are some caveats, however.

Connected 7kW array to an FM80 and waited for the sun. The morning was clear and sunny. Around 9AM the controller started reaching the 75A limit, and the array loitering around 4.3kW.
Thin overcast started moving in, so array output would vary.
Switched the FM80:Current Limit to 80A. Eventually saw the controller step past the 80A target. Then, during a "cloud edge" event, the array registered 5460W and controller read 101A.
Switched back to FM80:Current Limit 75A
Charger output dropped to 75A.
Another "cloud edge" event drove the array to 5200W+, and Charger output to 96A for about 10 seconds, until the FM80 started clipping and returning output to 75A.
Current Limiting does indeed work with an "overpanelled" array. However, the FM80's microcontroller isn't fast enough to immediately track fast transient events.
The FlexMax80 Extreme had a 10× faster microcontroller, and may have been OB's attempt to create a charge controller more capable of "overpanelling".
The FM80 ran noticeably hotter to the touch when clipping the "overpanelled" array. That may simply be an artifact of output near maximum rating.
Judging from the document specifying 113A as the FET shutdown Limit, 80A being the maximum rated current, and the clipping latency on transient events, it suggests an overpanelling margin of around 30%. If doing so: https://www.outbackpower.com/downloads/ ... p_note.pdf

samlegere
Forum Junior Member
Posts: 4
Joined: Wed Oct 04, 2023 6:10 am
My RE system: 2x FM80, 3x Longi LR4 345W + 3x Longi LR5 410W, 3x 314 Ah WattCycle LiFePO4 battery bank (paralleled for 12V), Trace DR2412 inverter, Trace T240 autotransformer/AC disconnect, Trace DC250 disconnect, Ryobi 3500W gas generator

Re: Overpaneling Safe Trip?

Post by samlegere » Wed Oct 09, 2024 10:33 am

So, I'm reviving this thread as I am looking at replacing/upgrading one of my two solar arrays. I am off-grid in Nova Scotia, Canada. My system is 12 volt because my old Trace DR2412 is what it is and it's what I have. I have two FM80 charge controllers feeding 600 Ah of AGM batteries (up-sizing to 900 Ah soon). 3 x 345 W panels in series feed one FM80 with the output set to 75 A and I have had zero issues with this unit. The second FM80 is fed by 5 x old Siemans 75w panels that I wish to replace. I can no longer source 345 W panels, so I am intending to use 3 x 410 W panels in series. I am also intending to clamp the output of this second controller at 75 A. It seems like the array's max output of 102.5 A should be safely below the FET shutdown current of 113 A and (hopefully) the 75 A max output setpoint on the FM80 will give the pokey microprocessor enough headroom to catch any transient 'overs' from temperature, cloud edge and other phenomena that drive the array's output unusually high. Am I sound in my reasoning or am I living dangerously? Also, am I right in assuming that the FM800 just dumps anything above the 75 A maximum setpoint as heat or else how does it deal with it?

Thanks for any thoughts; this forum is a treasure for us newbies.
Last edited by samlegere on Wed Oct 09, 2024 2:35 pm, edited 2 times in total.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Wed Oct 09, 2024 12:13 pm

What is the V(oc) of the 410W panels? If around 40V, 3 in series in a cold location is probably safe.
Larger panels will likely have a higher V(oc) so 3 in series may present issues. The FM80 has maximum input voltage rating of 150V.
As far as overpaneling is concerned, here's an app note from Outback on one aspect of the subject:
https://www.outbackpower.com/downloads/ ... p_note.pdf

samlegere
Forum Junior Member
Posts: 4
Joined: Wed Oct 04, 2023 6:10 am
My RE system: 2x FM80, 3x Longi LR4 345W + 3x Longi LR5 410W, 3x 314 Ah WattCycle LiFePO4 battery bank (paralleled for 12V), Trace DR2412 inverter, Trace T240 autotransformer/AC disconnect, Trace DC250 disconnect, Ryobi 3500W gas generator

Re: Overpaneling Safe Trip?

Post by samlegere » Wed Oct 09, 2024 12:41 pm

V(oc) is 40.2 V for 345 W panels and (I believe) 37.4 for the 410 W panels. Both are Longi. I read that technical note as it was linked somewhere else. They seem to be saying put 100 A fusing on the output of the FM800, but I don't see how that would be any protection for the CC? Anyway, I am aware of the Max V limitation. Was more wondering exactly how the 75 A output setting limit is achieved and whether there is any thermal sinking of excess PV output going on.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Wed Oct 09, 2024 1:11 pm

Was more wondering exactly how the 75 A output setting limit is achieved and whether there is any thermal sinking of excess PV output going on.
IDK how the FM handles current limiting. I presume it involves "detuning" the array MPP to restrict output, but that is purely speculation on my part.

samlegere
Forum Junior Member
Posts: 4
Joined: Wed Oct 04, 2023 6:10 am
My RE system: 2x FM80, 3x Longi LR4 345W + 3x Longi LR5 410W, 3x 314 Ah WattCycle LiFePO4 battery bank (paralleled for 12V), Trace DR2412 inverter, Trace T240 autotransformer/AC disconnect, Trace DC250 disconnect, Ryobi 3500W gas generator

Re: Overpaneling Safe Trip?

Post by samlegere » Wed Oct 09, 2024 1:18 pm

Thanks for your advice @raysun. I will keep an eye on it, maybe with some monitoring with my old fluke on a cold, sunny day but I doubt where I am located that the panels will get close to 'nameplate' output. I agree that the lead acid technology is a lot more forgiving and size and weight is not a consideration for the off-grid cabin. I have been hesitating to pull the trigger on LiFePo batteries for my boat, but the power to weight ratio sure is tempting...

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Overpaneling Safe Trip?

Post by raysun » Wed Oct 09, 2024 2:01 pm

For marine applications, I wouldn't hesitate installing LFP, along with Victron kit to charge/monitor it.