Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by mattyxp@yahoo.com » Tue Jan 09, 2024 11:39 am

Hi All,
The Mate 3S Automatic Generator Start (AGS) 2-Minute Voltage Start setting only allows increments of .4 VDC.
Is there any valid reason for this besides something like "this is just the way it's always been" or "the VDC reading isn't that accurate anyway."???
With lithium batteries now, a more precise AGS Voltage Start voltage setting would be very helpful in reducing wasted generator fuel and wasted generator run time wear and tear.
More importantly, by not allowing AGS Voltage Start setting increments of .1 VDC it is causing generators to come on before actually needed and can force a generator to run about twice as long as needed when an AGS Voltage Start is initiated versus a SOC Start, which can end up wasting twice the fuel actually needed to bring the batteries back up enough to get to the morning light.
Hoping Outback techs will give some real feedback here and see if a simple update to allow .1 VDC increments in AGS Voltage Start can be implemented. Saving wasted generator fuel and generator wear & tear is not a bad thing for anyone.
It would definitely also be useful to allow an AGS Voltage Start end VDC setting to terminate the AGS Voltage Start run at a predetermined VDC. This would solve the problem of the generator being forced to run longer than necessary.
Thank you for the comments and help!
Matt P :)

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by raysun » Tue Jan 09, 2024 1:05 pm

I'm not an AGS user, so will have limited help for your conundrum. Looking at the AGS Voltage Start configuration it does indeed show the parameter values increment in 0.4V steps - for a 48V inverter. IDK if "that's the way its always been", but suspect so, as the inverter itself operates at that precision.
If this causes operational heartburn, why not switch to SoC start? That would seem to have two advantages: it avoids LFP battery flat voltage/discharge curve as a trigger, and SoC needn't complete an "Absorb" cycle in order to stop charging.
https://atl.my.site.com/OutbackKnowledg ... -the-Mate3

User avatar
intellact
Forum Czar
Posts: 806
Joined: Mon Nov 28, 2005 3:20 am
My RE system: GVFX 3624 and MATE/MATE3/AXS Port with four Surette flooded lead-acid batteries (24V). Deactivated wind turbine. System now acts as UPS back-up. Monitored by WattPlot, of course.
Location: Ontario, Canada
Contact:

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by intellact » Tue Jan 09, 2024 8:18 pm

My knowledge of the history of these settings (across hundreds of client systems) is that 24V systems change most voltage settings in increments of .2V, and 12V systems by .1V.

I somehow doubt that it is related to the accuracy going down as the voltage goes up - although I could be wrong. It seems possible that this is done either for ease of firmware implementation (not a great excuse in my books), or to make it easier to changes settings on the corresponding wider scale (another excuse that would not rate high in my books).

Perhaps this information is helpful though.
Andrew Welch, creator of WattPlot

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by raysun » Tue Jan 09, 2024 8:33 pm

I somehow doubt that it is related to the accuracy going down as the voltage goes up - although I could be wrong. It seems possible that this is done either for ease of firmware implementation (not a great excuse in my books), or to make it easier to changes settings on the corresponding wider scale (another excuse that would not rate high in my books).
Exactly right. Inverter voltage:
12V:+/-0.1V, 24V:+/-0.2V; 48V:+/-0.4V.
I love semantics. As noted, accuracy is not the likely the issue. Precision is the issue.
Interesting insight on firmware space and precision that is 1×, 2×, and 4×, factored with the battery voltage.

User avatar
intellact
Forum Czar
Posts: 806
Joined: Mon Nov 28, 2005 3:20 am
My RE system: GVFX 3624 and MATE/MATE3/AXS Port with four Surette flooded lead-acid batteries (24V). Deactivated wind turbine. System now acts as UPS back-up. Monitored by WattPlot, of course.
Location: Ontario, Canada
Contact:

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by intellact » Wed Jan 10, 2024 6:44 am

raysun wrote: ↑
Tue Jan 09, 2024 8:33 pm
Interesting insight on firmware space and precision that is 1×, 2×, and 4×, factored with the battery voltage.
That insight comes from the fact that WattPlot uses exactly the same logic.

Since WattPlot supports the user adjusting system settings from the PC, I use what I call the vDC multiplier to reproduce the MATE3 functionality so that the setting increments match for the full range of nominal battery sizes. :cool: (It also sometimes allowed me to predict setting minimums and maximums when I did not have easy access to systems other than my personal 24V one.) :smile:

In particular, if you are writing code that can respond to normal vs. warning vs. critical battery voltage levels, the use of the vDC multiplier saves me a lot of code. :wink:
Andrew Welch, creator of WattPlot

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by raysun » Mon May 25, 2026 8:53 pm

The inverter internal voltmeter does indeed have +/-0.4V precision at 48V.
The FlexNetDC battery monitor, on the other hand, has a very precise voltmeter which properly attached will post exact battery voltage at the primary terminals. The FNDC connected to the Outback Hub automatically provides battery voltage to the system.
I don't do any AGS or grid stuff, so never studied it, but I'd be surprised if the FNDC couldn't be employed for triggering events

Echo5
Forum Guru
Posts: 107
Joined: Tue Aug 08, 2023 2:00 am
My RE system: FLEXmax 80, VFXR 3024, MATE3s, HUB10, FLEXnet DC, 2x150Ah Sterling LiFePO4 24V batteries, 8x220w panels in 4 strings of 2.
Contact:

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by Echo5 » Mon May 25, 2026 10:50 pm

herrylauu wrote: ↑
Mon May 25, 2026 7:44 pm
I think this excerpt highlights a very specific but important technical limitation that could matter a lot for users trying to fine-tune their power systems. Having the Mate 3S AGS voltage start setting restricted to increments of .4 VDC may feel inconvenient for people who want more precise battery management and generator activation control. [URL=https://ragdollXYZhitXYZgame.org[color=#272f3e[size=1RagXYZdollZ+XYZHit[/size[/color[/URL
Herrylauu is a bot shilling for SEO. Note the hidden size 1 URL in the comment - you can easily see it if you press the double quote button to include the comment in your reply. I have inserted the XYZ and removed the trailing ] character on the markup to make it visible avoid giving them even more exposure. This account really should be banned.
Kimono: Free and Open Source Outback Monitoring software
http://www.OfItselfSo.com/Kimono

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Mate 3S - AGS 2-Minute Voltage Start setting by .4 VDC increments only

Post by raysun » Tue May 26, 2026 6:23 am

Good catch!