Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, Tired of wasting diesel fuel with generator not shutting off because relay sticks in FNDC so I replaced it with a brand new Outback power FNDC battery monitor. But after programming the set points it just shows 73% and stays there all day. With the old FNDC it would show the battery % rising all day till it got to 100% but now with new FNDC it won't. The battery voltage did rise from 52.3 v to 53.6 VDC. So no matter what set points I change it to still no rise in %.
I will see what happens tonight if Voltage drops down to 50 v to start the generator and watch to see if it charges normally like it use to. I am using the Mate3s to monitor everything from inside my house. I will update tomorrow. David
I will see what happens tonight if Voltage drops down to 50 v to start the generator and watch to see if it charges normally like it use to. I am using the Mate3s to monitor everything from inside my house. I will update tomorrow. David
Last edited by HawaiianDrummer on Wed Nov 01, 2023 5:00 pm, edited 2 times in total.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73%
It sounds like a wiring error in the installation of the FNDC.
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73%
Aloha, Thanks for reply. I did make certain to attach the 3 sets of 2 wires ea. in the same exact order that they were on the original FNDC, I even wrote the wire markings down on paper but I can recheck them tomorrow. I originally used only 1 shunt for everything in and out.
thanks David
thanks David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73%
The original FNDC had three sets of shunt wires attached? Only one shunt was active?
Now more than one shunt is enabled?
Now more than one shunt is enabled?
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73%
Aloha, Yes i was the installer and did not care to see individual power in and power out etc. I just wanted cumulative data with more interest in getting generator to start automatically by voltage and or percentage set values and it has worked well for me over the many years! David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73%
Is the same single shunt enabled now?
Or is it more than one shunt?
Or is it more than one shunt?
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73%
Yes the same single shunt A is enabled and the shunt B and C are disabled as they have been and were never connected up to FNDC. This morning the gen ran a couple times and shut off but the last time it ran while the bright morning sun was out and did not shut off when over the shut off voltage and was up to 54.8 VDC. But to my dismay nothing I pressed would shut down the gen again like my previous problems that led me to replacing the FNDC. So I now changed auto start voltage and % settings to be different from each component, i.e.. Inverter charger, charge controller, battery monitor and Mate3s AGS as there were one or two that had similar start voltage settings.
Yesterday I changed out the cat5e cable when it was staying at 75% and voltages 52.3 to 53.6 but wouldn't get higher than 53.6 v and obviously the state of charge went to 100% But of of the problems is that the % stayed at 100% per cent all day yesterday, all night and all day today. I am stuck for ideas of what to try next.... maybe shut down complete system and return all back on, I really don't know. David
Yesterday I changed out the cat5e cable when it was staying at 75% and voltages 52.3 to 53.6 but wouldn't get higher than 53.6 v and obviously the state of charge went to 100% But of of the problems is that the % stayed at 100% per cent all day yesterday, all night and all day today. I am stuck for ideas of what to try next.... maybe shut down complete system and return all back on, I really don't know. David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73%
If you take a picture of the shunt wiring (at the shunts) and post it, another set of eyes might catch something.
-
fcwlp
- Forum Emperor
- Posts: 1416
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
Re: Replaced FNDC with new unit but % won't rise past 73%
I am a bit confused by what you did with, "i.e.. Inverter charger, charge controller, battery monitor."HawaiianDrummer wrote: ↑Wed Nov 01, 2023 1:41 pmSo I now changed auto start voltage and % settings to be different from each component, i.e.. Inverter charger, charge controller, battery monitor and Mate3s AGS as there were one or two that had similar start voltage settings.
.
Stick with the Mate3s AGS and FDNC relay function:
- On the Mate 3s AGS page, is the port number shown the port for the FNDC?
- On FNDC, relay mode should be "off" and inverter logic "yes."
I just tested a remote start on a dual VFXR system which uses the FNDC to start a 2-wire gen. After starting the FNDC will display "on."
.
raysun will help you figure out the battery charge % issue.
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73%
Aloha, fcwlp in response to your questions: AGS is set to port 1 and FNDC relay mode is always set to auto with reverse logic Yes.
If by chance nothing can shut the generator off I change invert logic to no, then set gen to off and it shuts the gen off. then I set it back to invert logic yes and then set relay mode back to auto. (I thought if it was left set to relay mode off that it would never turn on.) So now I set relay mode to OFF and it shows MANUAL OFF, normally I leave it in AUTO and it shows AUTO OFF I sure hope it starts next time when needed set like this.
This morning I did open the wiring cabinet and checked physical connections to Shunt A and everything is tight and secure and wired correctly as per installation specs. Thanks for your response. David
If by chance nothing can shut the generator off I change invert logic to no, then set gen to off and it shuts the gen off. then I set it back to invert logic yes and then set relay mode back to auto. (I thought if it was left set to relay mode off that it would never turn on.) So now I set relay mode to OFF and it shows MANUAL OFF, normally I leave it in AUTO and it shows AUTO OFF I sure hope it starts next time when needed set like this.
This morning I did open the wiring cabinet and checked physical connections to Shunt A and everything is tight and secure and wired correctly as per installation specs. Thanks for your response. David
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, hey fcwlp I reread manual and so I now put relay mode back to AUTO OFF because otherwise Mate3s AGS will be used and not the set points of the FNDC battery monitor David
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, Here are pics of my shunt and FNDC wire hook ups.
P.S. sorry had trouble sizing the photos down to be able to submit
A note about the way the shunt is wired up is, this is how it has been wired for the past12+ years and has always displayed percentages through the old FNDC but this new one was stuck at 73% but the voltages rose as normal and now after replacing the cat5e cable to the FNDC to Hub 10 now stays at 100% day and night for two days and nights now. David
P.S. sorry had trouble sizing the photos down to be able to submit
A note about the way the shunt is wired up is, this is how it has been wired for the past12+ years and has always displayed percentages through the old FNDC but this new one was stuck at 73% but the voltages rose as normal and now after replacing the cat5e cable to the FNDC to Hub 10 now stays at 100% day and night for two days and nights now. David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Looking at the shunt. Please confirm:
• Heavy black lead on left is battery negative
• Heavy white wire on right is inverter bat (-).
• Terminal bus bar attached to right side of shunt has two black charge controller bat (-) leads. There are also 3 white wires attached - for misc. loads?
• The green shunt sense wire (on top left) is clear of the battery negative terminal (not shorted.)
• Heavy black lead on left is battery negative
• Heavy white wire on right is inverter bat (-).
• Terminal bus bar attached to right side of shunt has two black charge controller bat (-) leads. There are also 3 white wires attached - for misc. loads?
• The green shunt sense wire (on top left) is clear of the battery negative terminal (not shorted.)
- sodamo
- Forum Emperor
- Posts: 1511
- Joined: Mon Apr 03, 2006 1:55 am
- My RE system: Totally off grid - Hamakua side, Big Island, Hi
36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians 2 GG8048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane
Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
EG4 Chargeverter
10Kw MEP 803a Military gen
Honda EU7000i
Starlink w Eero Pro 6e network
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2 - Location: Ninole, Hi
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha Dave
Reading with interest, but no advise as I only use AGS with a relay. I did try many years ago, but reverted.
Reading with interest, but no advise as I only use AGS with a relay. I did try many years ago, but reverted.
David
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, gen did not need to auto run yesterday by voltage setting and didn't start on per centages because like I said it stuck on 100%. I did notice this morning that the percent was reading 100 but not flashing but a few hours later it was flashing 100% so I decided to try unplugging FNDC from the system and it is Full sun all day here. thinking when it gets to above 56.4 VDC then I will plug the FNDC back in so it will act normal again. BUTalthough the sun is still out a full the battery voltage once again won't rise above 53.6 VDC which is part of the problem after installing new FNDC battery monitor and putting all the normal same settings yesterday and today never above 53.6 when it should be. I notice a reading when checking mate3s Charger button and inverter button that shows voltage and to the right of that HOTC there are no temp warnings all are no but I have never seen this before . Can this be what is not allowing the chargers to charge over 53,6 VDC??? let me know what you think and a side note I do know cooling fans stopped working at least 10 months ago, I tried disassembling FM charge controller to get to fan but could not get it out to work with or replace...For now a put a large free standing Fan aimed at the batteries and equipment hoping that might cool things down to charge above 53.6 and now it super heavy clouds again will wait till tomorrow to continue this nightmare! David
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
1. And my next dilemma the 6 ea. 48 v LIPO batteries are not holding a charge through the night as of recently.
2. The other oddity of this new FNDC battery monitor is the setting for Time at High needs to be set with how long the gen runs!
With it set to "0" mins. the generator starts at low voltage setting and immediately shuts off. Again and again this happened.
My old FNDC never had the time at High set, it was always left at "0" for the past decade and performed as needed.
3. I set my high setting at 30 mins at first for an experiment and yes after auto starting this time it ran and shut off exactly 30 mins. later but not up to high V. setting/
4. The worst news is that after the gen shuts off at time set at high then VDC drops one full volt and each few seconds keeps dropping 1/10th at a time until low V is reached and gen restarts. Not Good
5. Right now I am running gen with time at high set to 90 mins. and will see what V. is reached and how quick it drops again.
Looks bleak right now. David
2. The other oddity of this new FNDC battery monitor is the setting for Time at High needs to be set with how long the gen runs!
With it set to "0" mins. the generator starts at low voltage setting and immediately shuts off. Again and again this happened.
My old FNDC never had the time at High set, it was always left at "0" for the past decade and performed as needed.
3. I set my high setting at 30 mins at first for an experiment and yes after auto starting this time it ran and shut off exactly 30 mins. later but not up to high V. setting/
4. The worst news is that after the gen shuts off at time set at high then VDC drops one full volt and each few seconds keeps dropping 1/10th at a time until low V is reached and gen restarts. Not Good
5. Right now I am running gen with time at high set to 90 mins. and will see what V. is reached and how quick it drops again.
Looks bleak right now. David
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, Generator ran twice last night for set high time of 90 mins. This morning I turned large fan back on aiming at equipment and batts. Full sun shine and charging at 3500 watts with voltage maintained at 54.4 VDC which better than the 53.6 it was stuck at yesterday but I would like to see it get to 55 and 56 v charging in the daylike it use to, so I unplugged the FNDC to get the percentage back to reality when I plug it back in later. I still hope I can save this system. David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
raysun wrote: ↑Thu Nov 02, 2023 10:05 amLooking at the shunt. Please confirm:
• Heavy black lead on left is battery negative YES
• Heavy white wire on right is inverter bat (-). YES
• Terminal bus bar attached to right side of shunt has two black charge controller bat (-) leads. YES There are also 3 white wires attached - for misc. loads? (one ea. go to ea. charge controller and one to an electric outlet) don't quote me on the outlet because I didn't open up the right side electrical panel.
• The green shunt sense wire (on top left) is clear of the battery negative terminal (not shorted.) No it was touching so I moved it away to the left now, thanks for pointing that out.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
That was likely causing the FNDC to be confused.• The green shunt sense wire (on top left) is clear of the battery negative terminal (not shorted.) No it was touching so I moved it away to the left now, thanks for pointing that out.
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, sorry rayson it is still flashing 100% tonight at 52.5 VDC but at least the gen does run and stop by itself so that is a good thing and charging earlier was charging 3,500 watts and tapered off as it got to 56.4 VDC so that makes me happy.
And I did see how easy it is to replace that cooling fan, the reason I didn't change it last time was because I was trying to use a fan from an unused FM60 but could not get it out to use then just forgot about getting a new one, should be easy to find one local I hope. Thanks David
And I did see how easy it is to replace that cooling fan, the reason I didn't change it last time was because I was trying to use a fan from an unused FM60 but could not get it out to use then just forgot about getting a new one, should be easy to find one local I hope. Thanks David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
I'd try a couple things:it is still flashing 100%
• The FNDC has 3 shunt sense ports: A, B, and C. If there are sense wires connected to the other two unused ports, remove them.
• Relocate the Green/Green-White wire pair from its current sense port (e.g. Port A) to one of the other ports. Disable the old port (via the Mate, or in Optics) and enable the newly installed port.
Fully recharge the battery. Then reset the FNDC by power cycling it.
Glad to hear the battery came back up to full capacity voltage. I was hoping the battery had been discharged to a low level, and was simply taking a good deal of charging to bring back to full capacity.
Solar Man in Puna usually has a good inventory of repair parts.
If you have trouble locating a vent fan, I have a dead FM80 here I could probably scavenge the fan from.
-
HawaiianDrummer
- Forum Guru
- Posts: 382
- Joined: Thu Apr 02, 2009 1:42 am
- My RE system: 2-FM80's 2- FX3048's, Mate3s, Hub 10, 12 Kyocera
175 W panels, 21 Kyocera 225 W panels, 6- Ruixu 100 AH 48V. LIFEPO4 batteries for 600 AH Battery
bank, FNDC battery monitor and Kubota 11 KW Diesel Generator - Location: Ninole, Hawaii
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Aloha, Rayson in reference to use other shunts: When I installed the upgrades to the small existing system that was in place when I purchased this house it had 2 cabinets and the cabinet that has the one shunt in it is too cramped to add 2 more shunts so as a newby to solar, I just decided to use the one shunt for all measurements as opposed to one for in, one for out,....etc.
So that's why I can't try your experiment. Thanks again, David
So that's why I can't try your experiment. Thanks again, David
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
What I'm suggesting is moving the existing, active single shunt to a different FNDC port.HawaiianDrummer wrote: ↑Sat Nov 04, 2023 4:54 pmAloha, Rayson in reference to use other shunts: When I installed the upgrades to the small existing system that was in place when I purchased this house it had 2 cabinets and the cabinet that has the one shunt in it is too cramped to add 2 more shunts so as a newby to solar, I just decided to use the one shunt for all measurements as opposed to one for in, one for out,....etc.
So that's why I can't try your experiment. Thanks again, David
However, it may not be necessary, as the FNDC "metering weirdness" may just be interpretation error. Now that the battery has received an actual full charge, and the seeming PV power issue has sorted itself out, perhaps the FNDC metering will as well.
-
fcwlp
- Forum Emperor
- Posts: 1416
- Joined: Wed Jan 22, 2020 9:40 am
- My RE system: GS8048A, FM80 w/3,600W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed.
I install and maintain grid-tied and off-grid systems in my area and consult on solar system design/operation. - Location: 80 miles NE of Phoenix at 5500'
Re: Replaced FNDC with new unit but % won't rise past 73% so replaced cat5e now it is always 100% day and night
Late reply as I was at some very remote locations without internet the last couple of days. You are better off using the AGS function of the Mate3s and setting the port used on the AGS tab to the FNDC port.HawaiianDrummer wrote: ↑Wed Nov 01, 2023 5:04 pmAloha, hey fcwlp I reread manual and so I now put relay mode back to AUTO OFF because otherwise Mate3s AGS will be used and not the set points of the FNDC battery monitor David