Settings to charge batteries when generator turns on
-
porch13
- Forum Junior Member
- Posts: 3
- Joined: Tue Jan 03, 2023 11:55 am
- My RE system: Off-Grid using FLEXpower ONE FXR. Transitioning from 48V Rolls bank to Discover Lithium Ion Bank.
Settings to charge batteries when generator turns on
I have a FP1-VFXR3648A connected to a pair of Discover AES 7.4KwH batteries. I interact with the batteries via a Discover Lynk II, which has relays that are programmed to start a generator (Kohler 14KW) based on SOC of the batteries. All of this works perfectly, but when the generator is running it will not charge the batteries unless I force the bulk charge to start by accessing the menu through the Charger Hot-Key. How would I go about getting the Outback equipment to charge any time the generator is turned on by the batteries? I prefer to use the Lynk II to start and stop the generator since it knows the true SOC of the batteries. Thanks in advance for any guidance.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Settings to charge batteries when generator turns on
At best, any battery monitor, including one built into the battery, can only derive an estimate of the SoC, however it can be precise enough for operational purposes....Lynk II to start and stop the generator since it knows the true SOC of the batteries.
But that's not your question.
In order for the inverter charger to automatically start charging (on AC Input) the battery voltage must be lower than the Re-Bulk Voltage value set on the inverter's battery charging menu: In your scenario, there's no harm in setting Re-Bulk to some arbitrarily high voltage - less than the charge cutoff voltage, but higher than it is currently set.
-
porch13
- Forum Junior Member
- Posts: 3
- Joined: Tue Jan 03, 2023 11:55 am
- My RE system: Off-Grid using FLEXpower ONE FXR. Transitioning from 48V Rolls bank to Discover Lithium Ion Bank.
Re: Settings to charge batteries when generator turns on
Raysun, you are my hero! I adjusted Re-Bulk voltage and now it works like a charm. Thank you so very much!
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid