stops charging
I bought an off grid property. Solar pv, 24v battery bank with a propane backup generator. The solar array charges my batteries up to 29.7v then starts float mode. When power is low I switch on the generator and it brings up power to 24.8v and will not increase past no matter how long it runs. Is this a setting on the outback60 charge controller that I need to adjust? I'm very new to all this, any help is appreciated.
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
As noted, there are two chargers:
• The Outback solar charge controller. MX60 is an old model, FlexMax 60 (FM60) is the current model. This controller takes DC from the solar panels and converts it to charging current and voltages required by the battery.
• The generator / inverter charger. Certain inverter models have built-in battery charging circuits. The inverter accepts AC Input (from the generator in this case) and converts it DC charging current and voltages required by the battery.
Both chargers work independently. For them to both maintain the battery, they should be properly programmed.
If you would like more help in configuring the devices, list the equipment in detail in your profile: Exact charge controller model (MX60 or FM60), inverter model, battery model and configuration, generator model, solar panel model.
• The Outback solar charge controller. MX60 is an old model, FlexMax 60 (FM60) is the current model. This controller takes DC from the solar panels and converts it to charging current and voltages required by the battery.
• The generator / inverter charger. Certain inverter models have built-in battery charging circuits. The inverter accepts AC Input (from the generator in this case) and converts it DC charging current and voltages required by the battery.
Both chargers work independently. For them to both maintain the battery, they should be properly programmed.
If you would like more help in configuring the devices, list the equipment in detail in your profile: Exact charge controller model (MX60 or FM60), inverter model, battery model and configuration, generator model, solar panel model.
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
Ok, I didn't realize the generator went through the inverter to the batteries. I believe the charge controller is an flexmax60. The generator is a Cummins 13kw propane. The inverter is an AIMS 24v inverter charger, I don't know the actual model but I believe it's the one on this link
https://www.aimscorp.net/product/2000-w ... r-24-volt/
https://www.aimscorp.net/product/2000-w ... r-24-volt/
- SandyP
- Forum Czar
- Posts: 551
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: stops charging
Lets us know exactly what model inverter/charger you have.jitterz wrote: ↑Mon Sep 25, 2023 9:36 am I bought an off grid property. Solar pv, 24v battery bank with a propane backup generator. The solar array charges my batteries up to 29.7v then starts float mode. When power is low I switch on the generator and it brings up power to 24.8v and will not increase past no matter how long it runs. Is this a setting on the outback60 charge controller that I need to adjust? I'm very new to all this, any help is appreciated.
Looking at the instruction manual for the Aims Inverters I suspect that on your system the battery charging function may not enabled or if it is the charging "rate" is set very low.
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
What type/brand/model battery is being used?jitterz wrote: ↑Mon Sep 25, 2023 1:35 pm Ok, I didn't realize the generator went through the inverter to the batteries. I believe the charge controller is an flexmax60. The generator is a Cummins 13kw propane. The inverter is an AIMS 24v inverter charger, I don't know the actual model but I believe it's the one on this link
https://www.aimscorp.net/product/2000-w ... r-24-volt/
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
8 x Discover L16 - 6 Volt AGM 400ah batteries
They're wired into a 24v system. I'm going to the property tomorrow and will get you the exact controller model and photos. Thanks for everyone's help so far.
They're wired into a 24v system. I'm going to the property tomorrow and will get you the exact controller model and photos. Thanks for everyone's help so far.
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
The inverter model number is aims 24v
PICOGLF30W24V120VS
The dip switches are set
Sw1 = 1
SW2 = 1
SW3 = 0
Sw4 is 0
Battery selector is set at 2
Charge current control is max
I run the generator for 2 hrs. It hits 24.8w quickly and then won't move for over an hour. Once I shut it down the batteries drop to 23.9w.
Hope that makes sense to you.
PICOGLF30W24V120VS
The dip switches are set
Sw1 = 1
SW2 = 1
SW3 = 0
Sw4 is 0
Battery selector is set at 2
Charge current control is max
I run the generator for 2 hrs. It hits 24.8w quickly and then won't move for over an hour. Once I shut it down the batteries drop to 23.9w.
Hope that makes sense to you.
Last edited by jitterz on Fri Sep 29, 2023 6:36 pm, edited 2 times in total.
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
Just noticed there's an sw4 switch
Sw4 is 0
Sw4 is 0
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
The AIMS manual has a table showing the charging voltages for the different battery types that can be selected. Battery Type 7 is Lithium with a charge voltage: 28.8V.
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
I'm new at all this, and don't really understand the replies. I'm starting to think my batteries have sulphated. I certainly hope not, they're only 2 years old. Has anyone used the desulphate setting on their inverter? My inverter has the option but I've heard it's not recommended.
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
Yes, sorry my mistake. What is the Absorb voltage specified for the battery model?
[/quote]
I don't understand what your asking. Right now I'm sitting at 24.2v in the batteries, the pv is showing 24.7A coming in but the batteries are constant. They should be raising steadily.
[/quote]
I don't understand what your asking. Right now I'm sitting at 24.2v in the batteries, the pv is showing 24.7A coming in but the batteries are constant. They should be raising steadily.
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
What is the specific battery model?
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
L16 describes a case dimension. 400AH (hopefully) 20 Hour discharge capacity. I'll assume it's the battery above: 6VRE-2700FD. This from their line of home solar deep cycle "dry cell" AGM batteries.
If that's the battery block, here's the manual:
https://assets.discoverbattery.com/docu ... manual.pdf
For Bulk Charging (the initial charging stage), AES recommends a charge current between 10% and 25% of C20 battery capacity. For the 800AH battery: 80A - 200A of charge current.
At absolute maximum, the solar charger can provide 60A, likely much less on average. It would take a long time for the solar setup to put significant charge on the battery. During Bulk, the battery voltage would change slowly.
The 2nd charging phase is called "Absorb", and is a Constant Voltage charging profile. The Absorb Voltage for this battery is listed at 28.8V. That is the voltage to which the battery should be held while Absorb Charging. The charge current will start out high, but decline over time as the battery "fills".
Another important note. AGM batteries are sensitive to overcharging. As the battery internal temperature increases (due in part to ambient temperature) the charge voltage should be adjusted downward. Likewise, to avoid undercharging, as temperature decreases, charge voltage should be adjusted upward. Temperature Compensated Charging is possible with the FlexMax and AIMS by adding their Remote Temperature Sensors.
It was mentioned that the FlexMax is charging the battery to 29.7V (in Absorb). If the battery listed in this reply is being used, the Absorb Voltage should be 28.8V
To achieve 28.8V with the AIMS, battery selection #4 (Sealed Lead Acid) seems to be the best choice.
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
Seems to be similar style of battery. I found the link to the actual model I have
https://discoverbattery.com/products/search/evl16a-a-am
I'm out right now but will try setting the inverter to #4 and give it a try.
Thanks, hopefully this works.
https://discoverbattery.com/products/search/evl16a-a-am
I'm out right now but will try setting the inverter to #4 and give it a try.
Thanks, hopefully this works.
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
For this battery model, the Absorb Voltage is specified as 2.45V per cell, so 2.45 × 12 = 29.4V.jitterz wrote: ↑Sat Sep 30, 2023 12:12 pm Seems to be similar style of battery. I found the link to the actual model I have
https://discoverbattery.com/products/search/evl16a-a-am
I'm out right now but will try setting the inverter to #4 and give it a try.
Thanks, hopefully this works.
It sounds like the FlexMax is reasonably close to the target.
The AIMS profile that comes closest at 29.2V is actually labeled "AGM2" (#3).
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging

Again thanks for your help
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
Are Remote Temperature Sensor cables attached to the FlexMax and AIMS, and attached to the battery?
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
I don't know what I'dbe looking for. I don't think so. There are 2 thick cables from the aims to the batteries and there are 4 cables from the flexmax to the batteries. Nothing stands out to me as a sensor wire.
I've emailed a solar technician to come check it out. I think I'm way over my head here.
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
I did try battery selector number 3. Didn't seem to make any difference.
-
- Forum Overlord
- Posts: 10359
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: stops charging
The temperature sensors are important, but are not central to the charging issue you're experiencing. You may ignore temperature compensation for now.
It was mentioned that the system came with the property. How old is the battery?
It was mentioned that the system came with the property. How old is the battery?
-
- Forum Member
- Posts: 18
- Joined: Mon Sep 25, 2023 9:10 am
- My RE system: 6 x 250w LDK panels
Outback flexmax60 CC
Aims 24V inverter
8x6v discovery batteries 400ah
24v 800ah battery bank
Re: stops charging
I just bought them in 2021. The system was already in but the previous batteries were dead.