I'm asking for verification that I am understanding a few setting correctly:
Looking at the Mate3S settings using OpticsRE, under the "AC Input" tab, I see a setting called "System Charger Input Limit". I have two VFX3524 Inverters, so during generator run both will be charging batteries. Is this setting the max Amps that both inverters can be drawing combined from the generator?
Now, looking at the inverter settings, under the "AC Input" tab, I see another setting called "Charger AC Limit" Is that the max amperage each inverter will deliver to the battery bank when charging?
The specs on my batteries (8G27-DEKA) state "Max Bulk Charge Current (Amps) = 30% of 20HR Rate" Since these are 88AH @ 20hr, I'm calculating that to mean 26.4 amps (30% of 88 AH). Knowing that, should each inverter's "Charger AC Limit" be set to half of that amount (13.2 Amps)?
Thanks
Bryant
AC Limit - Battery Charging Parameters
Moderators: OutBack Moderator Team, OutBack
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AC Limit - Battery Charging Parameters
There's a lot to unpack here. Let's break it down in reverse order.
Battery Charge Rate
The individual battery blocks' 26A charge rating will total 9 × 26A = 234A total maximum charge current for the battery (9 parallel branches.)
The entire charging infrastructure: FM80, FM60, and 2 VFX3524 inverters can deliver maximums of 80A, 60A, (2x) 85A DC charge current.
Inverter Configuration
Since the X240 Autotransformer is listed, it's assumed the inverters are configured for "Outback Stacking", 240VAC split phase output, load balanced with the autotransformer.
Each inverter's AC input should, in turn, be fed from a leg (L1, L2) of a 240VAC split phase output generator. This will put AC input at 120V across each inverter's input, but 180° out of phase. The total current delivered is in series across the two legs. Note the Onan is rated 52A@240V.
Inverter AC Input and Current Limit
The inverters' rated AC Input current maximum = 60A. The generator's rated maximum appears to be 52A. Set the AC Input Current Limit to 52A (or the generator's rated maximum continuous output current.)
Charger AC Input Limit
The inverter chargers' maximum AC input is 20AAC. This converts to a maximum charge current of 85ADC per charger. (X2 = 170ADC max.) The Charger AC Limit can be safely set to 20A if desired.
Theoretical Maximum Charge Rate
All four chargers: FM80, FM60, 2xVFX3524, if all charging simultaneously, would have a theoretical maximum charge rate of 80A + 60A + (2x85A) = 310A. This exceeds the recommended battery charge spec of 234A max. The Mate3 and FNDC can provide dynamic charge limiting by monitoring the inverter chargers rate, and adjusting the FlexMax chargers' output accordingly. The Mate Global Charge/Global Charger Control: Enabled, and Maximim Battery Charge: 234A. The FlexMax charge controllers Misc/Grid Tie Mode: Enabled. This doesn't mean the system is grid tied, rather it enables a library of functions the Mate uses to dynamically throttle the chargers' output.
Battery Charge Rate
The individual battery blocks' 26A charge rating will total 9 × 26A = 234A total maximum charge current for the battery (9 parallel branches.)
The entire charging infrastructure: FM80, FM60, and 2 VFX3524 inverters can deliver maximums of 80A, 60A, (2x) 85A DC charge current.
Inverter Configuration
Since the X240 Autotransformer is listed, it's assumed the inverters are configured for "Outback Stacking", 240VAC split phase output, load balanced with the autotransformer.
Each inverter's AC input should, in turn, be fed from a leg (L1, L2) of a 240VAC split phase output generator. This will put AC input at 120V across each inverter's input, but 180° out of phase. The total current delivered is in series across the two legs. Note the Onan is rated 52A@240V.
Inverter AC Input and Current Limit
The inverters' rated AC Input current maximum = 60A. The generator's rated maximum appears to be 52A. Set the AC Input Current Limit to 52A (or the generator's rated maximum continuous output current.)
Charger AC Input Limit
The inverter chargers' maximum AC input is 20AAC. This converts to a maximum charge current of 85ADC per charger. (X2 = 170ADC max.) The Charger AC Limit can be safely set to 20A if desired.
Theoretical Maximum Charge Rate
All four chargers: FM80, FM60, 2xVFX3524, if all charging simultaneously, would have a theoretical maximum charge rate of 80A + 60A + (2x85A) = 310A. This exceeds the recommended battery charge spec of 234A max. The Mate3 and FNDC can provide dynamic charge limiting by monitoring the inverter chargers rate, and adjusting the FlexMax chargers' output accordingly. The Mate Global Charge/Global Charger Control: Enabled, and Maximim Battery Charge: 234A. The FlexMax charge controllers Misc/Grid Tie Mode: Enabled. This doesn't mean the system is grid tied, rather it enables a library of functions the Mate uses to dynamically throttle the chargers' output.
- Wanbli
- Forum Expert
- Posts: 61
- Joined: Mon Oct 14, 2013 6:35 am
- My RE system: System Name: OutBack Power Technologies
System Type: Backup
System Nominal Voltage:24 VDC
PV Array Wattage: 6.12Kw
Battery: 6-Tesla 5.3kw Lithium Ion Model S Modules (31.8kw)
Battery Ah Capacity:1392AH
Flexware 500
1-Mate3s
2-VFX3524
1-FM60
2-FM80
FNDC
Generac Propane Generator kW Rating:12.0 kW
Max Inverter Output kW:7.2 kW
Max Charger Output kW:2.8 kW - Location: George Washington National Forest, Virginia
Re: AC Limit - Battery Charging Parameters
RaySun;
I've reconfigured my system with 6-Tesla L-Ion battery packs (see attached specs) and am having my Generator tuned to the system on Friday. My system is similar to the one above, but different voltage and battery configs and I'm hoping to fine tune the chargers correctly for the batteries and the generator. Here's the layout:
System Type: Backup
System Nominal Voltage:24 VDC
PV Array Wattage: 6.77Kw
Battery: 6-Tesla 5.3kw Lithium Ion Model S Modules (31.8kw)
Battery Ah Capacity:1392AH
Flexware 500
1-Mate3s
2-VFX3524
1-FM60
2-FM80
FNDC
Generac Propane Generator kW Rating:12.0 kW
Max Inverter Output kW:7.0 kW
Max Charger Output kW:2.8 kW
I currently have this setup as a "Backup" system, tho I use it to offset my grid use by only using 50% of my battery capacity, saving the other half for emergencies (grid loss in bad weather mostly).
Can you please look this over and advise the best setup for this system? I'm having a Generac tech out Friday afternoon to setup my genset, I know that's short notice, if you don't have enough time, that's no problem.
Any help will be appreciated.
I've reconfigured my system with 6-Tesla L-Ion battery packs (see attached specs) and am having my Generator tuned to the system on Friday. My system is similar to the one above, but different voltage and battery configs and I'm hoping to fine tune the chargers correctly for the batteries and the generator. Here's the layout:
System Type: Backup
System Nominal Voltage:24 VDC
PV Array Wattage: 6.77Kw
Battery: 6-Tesla 5.3kw Lithium Ion Model S Modules (31.8kw)
Battery Ah Capacity:1392AH
Flexware 500
1-Mate3s
2-VFX3524
1-FM60
2-FM80
FNDC
Generac Propane Generator kW Rating:12.0 kW
Max Inverter Output kW:7.0 kW
Max Charger Output kW:2.8 kW
I currently have this setup as a "Backup" system, tho I use it to offset my grid use by only using 50% of my battery capacity, saving the other half for emergencies (grid loss in bad weather mostly).
Can you please look this over and advise the best setup for this system? I'm having a Generac tech out Friday afternoon to setup my genset, I know that's short notice, if you don't have enough time, that's no problem.
Any help will be appreciated.
- Attachments
-
Current config_Outback Power.pdf- (102.71 KiB) Downloaded 176 times
-
Tesla S85 Battery Module Specs.pdf- (861.4 KiB) Downloaded 148 times
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: AC Limit - Battery Charging Parameters
The listing of the system settings has blank parameter values, odd.
I've never used these reconditioned packs, but charging looks pretty straight-forward. They are NMC cells so more sensitive to thermal runaway issues than LFP. Hopefully they will be installed away from your domicile.
Looking at the specs, a typical Constant Current (Bulk) / Constant Voltage (Absorb) charge cycle is listed at s 0.5C maximum charge rate. With a 1392Ah capacity, that's nearly 700A max, so no problem exceeding that. Lower charge rates are perfectly acceptable, they will simply take longer.
The maximum charge voltage of 25.2V would be the Absorb voltage. A duration of 4 hours is listed. I'm guessing a long Absorb to top balance the cells? I don't know for sure, it would be a question for the battery vendor.
The FX inverter's internal voltmeter is +/-0.2V so in order not to exceed maximim charge voltage it would seem setting Absorb Voltage to 25V would be safest. Again, a question for the vendor.
The FNDC plays a role in charge termination if configured to do so. The necessary parameters are Charged Voltage, Charged Return Amps, and Charged Time. Charged Voltage should be 0.2V below the lowest Absorb Voltage setting, Charged Return Amps is probably around 1-2% of the total battery Ah capacity (check with vendor, they may refer to it as end amps, tail current, etc.). Charged Time of 1 - 3 minutes is likely adequate.
The chargers (FX and FM) should be calibrated. The FX can be calibrated (more or less) using the Calibrate menu in the inverter setup menus. The FMs calibration here: viewtopic.php?t=15400
I've never used these reconditioned packs, but charging looks pretty straight-forward. They are NMC cells so more sensitive to thermal runaway issues than LFP. Hopefully they will be installed away from your domicile.
Looking at the specs, a typical Constant Current (Bulk) / Constant Voltage (Absorb) charge cycle is listed at s 0.5C maximum charge rate. With a 1392Ah capacity, that's nearly 700A max, so no problem exceeding that. Lower charge rates are perfectly acceptable, they will simply take longer.
The maximum charge voltage of 25.2V would be the Absorb voltage. A duration of 4 hours is listed. I'm guessing a long Absorb to top balance the cells? I don't know for sure, it would be a question for the battery vendor.
The FX inverter's internal voltmeter is +/-0.2V so in order not to exceed maximim charge voltage it would seem setting Absorb Voltage to 25V would be safest. Again, a question for the vendor.
The FNDC plays a role in charge termination if configured to do so. The necessary parameters are Charged Voltage, Charged Return Amps, and Charged Time. Charged Voltage should be 0.2V below the lowest Absorb Voltage setting, Charged Return Amps is probably around 1-2% of the total battery Ah capacity (check with vendor, they may refer to it as end amps, tail current, etc.). Charged Time of 1 - 3 minutes is likely adequate.
The chargers (FX and FM) should be calibrated. The FX can be calibrated (more or less) using the Calibrate menu in the inverter setup menus. The FMs calibration here: viewtopic.php?t=15400
- Wanbli
- Forum Expert
- Posts: 61
- Joined: Mon Oct 14, 2013 6:35 am
- My RE system: System Name: OutBack Power Technologies
System Type: Backup
System Nominal Voltage:24 VDC
PV Array Wattage: 6.12Kw
Battery: 6-Tesla 5.3kw Lithium Ion Model S Modules (31.8kw)
Battery Ah Capacity:1392AH
Flexware 500
1-Mate3s
2-VFX3524
1-FM60
2-FM80
FNDC
Generac Propane Generator kW Rating:12.0 kW
Max Inverter Output kW:7.2 kW
Max Charger Output kW:2.8 kW - Location: George Washington National Forest, Virginia
Re: AC Limit - Battery Charging Parameters
Thank you so much for this info, really appreciate you taking the time for this!