Re: Fortress Power eVault Max

Post by raysun » Mon Feb 13, 2023 8:57 am

Auto Charge Termination Control ends the Absorb phase when charging targets are met.

According to the Fortress manual "Terminate when charge current drops below
0.05C".

Set the ACTC parameters In the FNDC / Battery Charging menu:
Charged Voltage: 0.4V below the lowest Absorb Voltage used on the chargers in the system.
Charged Time: 1 minute
Charged Return Amps: 5% of the (C20) Battery Capacity.