I understand
I keep my absorb time set for 0.2H, and with a slow charge, Automatic Charge Termination Control always terminates with CPM in 8m or less.
I understand
I think that the CCs are doing that. I've seen the same behavior with acid batteries when close to the end of absorb cycle. even in float is observable. might just be from a small difference in the calibrations of CCs.raysun wrote: ↑Thu Jan 19, 2023 5:29 amThe charge will drop to or near the 2% value, then in the next moment increase measurably, only to decline, then subsequently increase in a "wavy pattern" until finally settling at or below 2%. This occurs during the 0.1H "Absorb Time". I believe the oscillation is caused by the BMS's performing "top balancing" to bring all cells in the battery to the same capacity.
Yes, I see that every time ... in my case the batteries have always "touched" the 2% return amps well within the 6m setting, but then they can take quite a while to settle down and finally reach CPM.raysun wrote: ↑Thu Jan 19, 2023 5:29 am
The charge will drop to or near the 2% value, then in the next moment increase measurably, only to decline, then subsequently increase in a "wavy pattern" until finally settling at or below 2%. This occurs during the 0.1H "Absorb Time". I believe the oscillation is caused by the BMS's performing "top balancing" to bring all cells in the battery to the same capacity.
My battery completes this process regularly in the 6 minute interval. Other batteries do not. Case in point @Provo taking a reported 8 minutes, and others taking as long as 30 minutes.
Good answer. Of course teasing. But we, in our club, understand it.
I sometimes make my head hurt.
Its always amazing how quickly these batteries charge, and how much PV energy goes unharvested.So I added 3 SimpliPhi 3.8 and even this season I’m still hitting CPM almost daily, usually Noonish.
I think we should get together and form a network of free roadside charging stations for homeless Tesla owners.Guessing when I get my new solar panels I’ll have a new challenge, find a reasonable use for the excess solar.
Law of Large Numbers?Note on my additional battery capacity I expected to see a nice jump in my overnight SOC, but not so, a couple percentage points only.
Take an A/C unit on hi, blowing over the top of the hot tub with the jets on and pretend you had a long day of snow skiing. Or another tub of refrigerated water so you can dip back and forth.
I saw Phi's explanation of a cycle once, but don't recall where, or its full details. I dismissed the notion because the next sentence stated Phi does not warrant its batteries on cycles, rather on time in service. (Their pro-rated warranty is basically not worth pursuing after 5 years.)Frankly, I would love to know what is counted as a cycle.
No, Buddy. When I do an EQ I am watching and waiting with time set aside to watch the system. IT DOESN'T"T TAKE TO LONG. I start it after the batteries have finished the Bulk and .2 Absorb. I'd say less than a half hour. Certainly easier than taking SGs and I never have holes in my clothes any more (wink).raysun wrote: ↑Mon May 22, 2023 1:05 pmWhen executing "EQ", is the actual Start EQ charge function executed? If so, the 1 Hour timer is going to be in play. I'm not sure I'd want to hold the battery (on purpose, or incidentally) at 56.4V for 1 hour.Frankly, I would love to know what is counted as a cycle.
Perhaps an "EQ" voltage of 54.6V @ 1H might fill the bill.