I ❤ my LiFePo4 battery

provo
Forum Emperor
Posts: 1464
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: I ❤ my LiFePo4 battery

Post by provo » Thu Jan 19, 2023 3:45 am

raysun wrote: ↑
Wed Jan 18, 2023 11:36 pm
They actually could set the Absorb Time to 0.5H and trust Automatic Charge Termination Control to terminate at the point CPM is reached. I'm not advocating that, 0.1H is the manufacturer spec, and I'm sticking to it.
I understand :grin: . I just wonder if there's an important difference, or if they wrote the spec that way just for the sake of simplicity (particularly when many systems will easily achieve CPM within the 0.1H).

I keep my absorb time set for 0.2H, and with a slow charge, Automatic Charge Termination Control always terminates with CPM in 8m or less.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Thu Jan 19, 2023 5:29 am

Constant current, one stage charging is a pretty common profile for lithium ion batteries. With LiFePo4, the most common termination point is 3.6V / cell, which is essentially 99% capacity. (The extra 1% isn't had until the cell voltage reaches 4.2V which is really hard on them.)
3.6V / cell = 28.8/57.6 for 24V/48V nominal batteries. SimpliPhi specifies a termination voltage well below full capacity. It's a good strategy - derate the capacity of the cells to 3.525V and charge to that capacity. The resulting "fast charge" to the lower capacity has less "wear and tear" on the cells.
My theory (so far untested sufficiently to be more than speculation) as to why some batteries reach CPM within the allotted 3.525V @ 0.1H target cutoff while other batteries do not has to do with cell balancing. I've watched my own battery closely (using the Mate3s web app, and a Victron BMV700 monitor, both of which provide "near real-time" voltage/current tracking with the BMV700 being the faster) and notice at termination voltage a steady decline in charge current, until it touches the neighborhood of 2%. At that point, a notable "oscillation" of charge current occurs. The charge will drop to or near the 2% value, then in the next moment increase measurably, only to decline, then subsequently increase in a "wavy pattern" until finally settling at or below 2%. This occurs during the 0.1H "Absorb Time". I believe the oscillation is caused by the BMS's performing "top balancing" to bring all cells in the battery to the same capacity.
My battery completes this process regularly in the 6 minute interval. Other batteries do not. Case in point @Provo taking a reported 8 minutes, and others taking as long as 30 minutes. The variation may be due to the cells' capacity variations when the termination voltage is reached. This may be due to the cells starting out at different capacities at the end of commissioning; or it may be different rates of discharge cause a variation during daily usage. In either event, the Phi "full charge" is less than maximum cell capacity, so if it takes longer than specified to bring all cells into balance, it shouldn't cause any stress. Phi themselves seem pretty blasé about changing the "Absorb Time" to 12 or more minutes. My "strategy" of leaving it at 6 minutes and repeating the charge profile is a (pedantic) effort you stay within the language of the warranty. There is a documented charge termination limit (0.1H), but there is no documented limit on how many times in succession one can repeat the charge profile. Also, the time limited (0.1H) termination doesn't depend on Automatic Charge Termination Control working. The "sync charge" requires manual intervention and monitoring, rather than "set and forget". For the batteries that take an extended time (like 30 minutes) I prefer my Kindly Ol' Uncle Wally's maxim:
"Trust everybody, but always cut the cards."
I want to keep an eye on the anomalies.

User avatar
EA6LE-ONE
Forum Czar
Posts: 952
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: I ❤ my LiFePo4 battery

Post by EA6LE-ONE » Thu Jan 19, 2023 5:38 am

raysun wrote: ↑
Thu Jan 19, 2023 5:29 am
The charge will drop to or near the 2% value, then in the next moment increase measurably, only to decline, then subsequently increase in a "wavy pattern" until finally settling at or below 2%. This occurs during the 0.1H "Absorb Time". I believe the oscillation is caused by the BMS's performing "top balancing" to bring all cells in the battery to the same capacity.
I think that the CCs are doing that. I've seen the same behavior with acid batteries when close to the end of absorb cycle. even in float is observable. might just be from a small difference in the calibrations of CCs.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Thu Jan 19, 2023 6:11 am

That's something to check into.
I know the calibration on my 2 FM80s are well aligned. I keep them in lock-step, and if there's any indication (voltage transitions) that aren't in sync, I recalibrate. That doesn't happen often, though. My Fluke meter is more precise than the FM80 front panel, of course, and I can get the two FM80s in sync to 0.01V (as read from the Fluke at the FM80 Bat terminals during a front panel 0.1V transition. So at least that part is accounted for to a reasonable degree.
Current calibration of the FM80s isn't possible (as far as I know). The Constant Voltage precision may be unable to maintain current output at low levels certainly.
Two speculatons on an observed condition. I don't think either can be proved conclusively with the current setup. I think a precision power supply capable of Constant Voltage at 15A current would cover the range of current variation I observe. I can connect that to my external charging circuit and switch to it when the battery is at termination voltage. I'll be able to capture the current curve through the 2% target. At least, will be able to see if the oscillation follows the charger, or is endemic to the battery.

provo
Forum Emperor
Posts: 1464
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: I ❤ my LiFePo4 battery

Post by provo » Thu Jan 19, 2023 7:03 am

raysun wrote: ↑
Thu Jan 19, 2023 5:29 am

The charge will drop to or near the 2% value, then in the next moment increase measurably, only to decline, then subsequently increase in a "wavy pattern" until finally settling at or below 2%. This occurs during the 0.1H "Absorb Time". I believe the oscillation is caused by the BMS's performing "top balancing" to bring all cells in the battery to the same capacity.
My battery completes this process regularly in the 6 minute interval. Other batteries do not. Case in point @Provo taking a reported 8 minutes, and others taking as long as 30 minutes.
Yes, I see that every time ... in my case the batteries have always "touched" the 2% return amps well within the 6m setting, but then they can take quite a while to settle down and finally reach CPM.

I feel better about the overtime if it's doing balancing!

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Thu Jan 19, 2023 12:29 pm

Confession time:

I initialized 3ea PHIs in Nov '20. Did the original config changes and got used to them. Absolutely impressed so I added a 4th in Mar '21 and reconfigured bus bars, etc. into a 2x2. I never changed low battery cut out from the original 50.4 at install. Its never triggered and frankly I don't recall ever getting barely into a lower 51vdc range. And that only happened when I was trying to pull them down and got impatient watching. Fast forward two years and this thread.

There have been bunches of CPM posts related to the PHIs. I just never paid much attention. Everything is fine cause I don't take them low and I don't fill them either. I just stayed with all the settings all along. The inverter at a higher charge voltage in the winter just in case and the charge controller in the summer set lower because of the longer days with not risk. I just blew off CPM as being when I completed a bulk with .1 Absorb and it ended. All charged. I did have the CC at .2 because it was a lower voltage and determined safe to do so. This is the absolute definition of maintenance free after all the years of lead batteries.

Now this thread. Oh, Gee, I have never used return amps. I had just blown it all off with the .1 or .2 absorb being sufficient. For two years. So after reading this I realized my neglect. Previously I pushed the EQ button to fix it because it was time. 56.4 for .1 hr. It took all of 3-4 minutes. I thought this is all BS. Then this recent conversation and what to call balancing the cells was the wake up call. I'VE NEVER DONE THAT WITH END AMPS. NEVER. TWO YEARS.

So typical on generator time a few days ago I set the absorb at 56.4 for an hour and hit EQ with new settings. It overshoots that to 56.75 at the end. Then I saw it - the up and down of the Absorb. I thought I saw that on the CC but dismissed it as clouds. This time I was ready because I was watching for CPM CYCLE. I hit it in a really short time, like 10 minutes. Now I see that I may have to repeat it a few times....

And then there is the 57.4 max. Really, apparently, they can go higher

Gosh I appreciate these batteries. They are so forgiving. But to me is the 'ramp' where they charge. At discharge they pull like a diesel under load. And for recharge they pull like a diesel under load needing the power. But they are efficient in both directions. Just using the comparison.

If you can swing the PHIs you will join the thread. OR, you'll live with lead blocks.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Thu Jan 19, 2023 12:58 pm

If you always drive your battery down the middle of the road, it's lots easier to keep 'em between the ditches. 🤣
LFP is quite partial to Partial State of Charge. One might say it's its happy place.
The question of Top Balancing only comes into play if:
• Maximum capacity is needed. Those of us with the luxury of more capacity than is needed on a daily basis can safely eschew the charge to maximum capacity, and Top Balancing. The cells themselves aren't particularly bothered by being at slightly different capacities (and voltages) as long as the battery isn't fully discharged. Using 20% SoC as the "discharge floor" leaves plenty of capacity for the cells to have very different capacities without issue.
• Precision meter synchronization is desired. All "coulomb counting" meters are prone to drift, and SoC readings benefit from periodic meter sync - at 100% SoC. Charging the battery to full capacity is unambiguous when the charge current rate (at charge termination voltage) reaches the vendor specified 2% of C20AH capacity. Outback calls it Charged Return Amps, Victron Calls it Tail Amps. Whatever irs called, reaching that value at the end of the charge cycle assures the battery is at 100% SoC and the meter is synchronized to that SoC.
A periodic sync is fairly easy to do. If the battery doesn't charge to full capacity in the normal charge session, repeating with Start Bulk Charge usually takes care of it (after a time or two, or five.)
Using EQ to execute the "Sync Charge" would be a good hack if it wasn't for one issue: one the FMs, the minimum EQ Time is 1 Hour. I'd be nervous about leaving the battery at the termination voltage that long, especially unattended.
For my system, the whole issue is academic. The battery reaches "CPM" almost every day. On the rare occasion it does not, I enjoy the diversion. For batteries the need a bit more time to reach CPM in the normal course of charging, @provo demonstrates a good solution: extend Absorb Time to 0.2H. The "tortoise" batteries that only reach CPM with manual prodding, may end up outlining the "hares" that reach CPM at thr end of every fast charge.
Last edited by raysun on Thu Jan 19, 2023 1:14 pm, edited 1 time in total.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Thu Jan 19, 2023 1:08 pm

Diesels don't pull downhill. My oops. But they do have engine brakes.

How can we capitalize on the sun going down?

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Thu Jan 19, 2023 1:18 pm

Before i was old enough to drive, my diesel truckin' uncle taught me to go downhill in the same gear you go uphill.
With the sun going down, our Phis get to show what they're made for. IME, they do it without so much as blinking.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Thu Jan 19, 2023 3:38 pm

raysun wrote: ↑
Thu Jan 19, 2023 1:18 pm
Before i was old enough to drive, my diesel truckin' uncle taught me to go downhill in the same gear you go uphill.
With the sun going down, our Phis get to show what they're made for. IME, they do it without so much as blinking.
Good answer. Of course teasing. But we, in our club, understand it.

I appreciate drivers+.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Sat Jan 21, 2023 4:15 pm

Having turned over a new leaf I have done a few charges to CPM. Of course there is nothing noticeable. I did make one change and dropped the top of the bulk down to 55.2v. That hasn't made any difference either except the SOC from the Victron is down a few points in the morning (around 74-5% instead of 78-79).

So here is a question: when end amps hit the 2% target, what is the effect of doing that at a lower definition of 'full charge'? Like lower than 56.4, 57.x or whatever? The Victron may could be tweaked a bit as I have to force an additional bulk for the reset. But I'm not gonna screw with it though. As it is now I don't have to change a thing, summer to winter except the obvious generator run time.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Sat Jan 21, 2023 5:45 pm

Charging LFP cells is simple, and complex.
The easy stuff to (sort of) understand is the relationship between cell voltage and capacity. Some voltage "benchmarks" -
• Absolute maximum: 4.2V
• (Almost) Full capacity: 3.6V
• The difference in capacity between 4.2V and 3.6V < 1%
• Recommended charge termination: 3.5 - 3.6V

For a 48V nominal battery, the recommended "Full Charge" voltage is 56 - 57.6V.

The simplest charge profile is Constant Current until the desired termination voltage is reached. When the battery cells are "full" they increasingly resist accepting charge, and there is a steep decline in charge current. The "Bulk until full" single-stage profile is the fastest method to bring the battery to full charge.
Alternately, a two-stage profile - Constant Current then Constant Voltage - can be used. Typically, Constant Current (Bulk) is executed to about 80% capacity, then Constant Voltage (Absorb) is executed until the charge current falls to a target rate (e.g.: 2%). Phi recommends 54.6V as the phase switch point between CC & CV, and 1.5H "Absorb Time" to reach full charge.
Executing Constant Current to an "in between" voltage would bring the cells to less than full capacity. Switching to Constant Voltage and holding the "Absorb Voltage" for a period should eventually fill the cells, and at that point, a charge current decline should be evident. The charge cycle will take longer than "Bulk until full", but take less time than "Absorb at 54.6V".

I use "Bulk until full". The charing routine is pretty much clockwork. When 56.4V is reached, and Constant Voltage takes over, the charge current is typically quite high, on the order of 35 to 130A, and generally always reaches the 2% cutoff within 5 minutes.
I've found the FNDC and BMV700 both indicate 100% SoC slightly before CPM - generally 5 - 10AH shy of "full capacity". I could "tweak" the monitors' parameters, but I don't bother. On the rare occasion 100% SoC coincides with CPM, it appears after a session of modest discharge rate, followed by a modest charge rate. My guess is Peukerts Law makes aligning the SoC with actual charging current a moving target.

User avatar
sodamo
Forum Emperor
Posts: 1511
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians 2 GG8048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
EG4 Chargeverter
10Kw MEP 803a Military gen

Honda EU7000i
Starlink w Eero Pro 6e network
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: I ❤ my LiFePo4 battery

Post by sodamo » Sat Jan 21, 2023 7:27 pm

Sometimes, you guys just make my head hurt :grin:

So I added 3 SimpliPhi 3.8 and even this season I’m still hitting CPM almost daily, usually Noonish.
Guessing when I get my new solar panels I’ll have a new challenge, find a reasonable use for the excess solar.

Note on my additional battery capacity I expected to see a nice jump in my overnight SOC, but not so, a couple percentage points only.
David

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Sat Jan 21, 2023 7:39 pm

sodamo wrote: ↑
Sat Jan 21, 2023 7:27 pm
Sometimes, you guys just make my head hurt :grin:
I sometimes make my head hurt.
So I added 3 SimpliPhi 3.8 and even this season I’m still hitting CPM almost daily, usually Noonish.
Its always amazing how quickly these batteries charge, and how much PV energy goes unharvested.
Guessing when I get my new solar panels I’ll have a new challenge, find a reasonable use for the excess solar.
I think we should get together and form a network of free roadside charging stations for homeless Tesla owners.
Note on my additional battery capacity I expected to see a nice jump in my overnight SOC, but not so, a couple percentage points only.
Law of Large Numbers?
FNDC needs reconfiguring?
Spousal unit reveling in new-found energy?
Neighbors suddenly sprouting extra-long extension cords?

User avatar
sodamo
Forum Emperor
Posts: 1511
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians 2 GG8048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
EG4 Chargeverter
10Kw MEP 803a Military gen

Honda EU7000i
Starlink w Eero Pro 6e network
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: I ❤ my LiFePo4 battery

Post by sodamo » Sat Jan 21, 2023 8:39 pm

Fortunately, my usage hadn’t increased.
I was used to seeing seeing about 40% drop in SOC overnight. That would be about 18.24 kwh. That same use would be about 32% of the increased capacity. I’m seeing around 35-36%.
FNDC was updated.
Not really concerned, just surprised.
David

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Sat Jan 21, 2023 8:41 pm

sodamo wrote: ↑
Sat Jan 21, 2023 7:27 pm
I’ll have a new challenge, find a reasonable use for the excess solar.
Take an A/C unit on hi, blowing over the top of the hot tub with the jets on and pretend you had a long day of snow skiing. Or another tub of refrigerated water so you can dip back and forth.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Sun Jan 22, 2023 2:29 pm

Gung Hay Fat Choy!
Gong Xi Fa Cai!
Happy New Year!!!!!
Screenshot_20230122_122331_Chrome.jpg
The Lunar New Year tradition of leaving lights on in every room over night to ward off evil and invite good into one's home can draw a lot of extra battery current.
No matter! 🤙

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Mon Jan 23, 2023 10:45 am

Screenshot_20230123-083209.jpg
A Red Letter day! (Actually Yellow Icon day, but that doesn't have the same panache.)
At sunset yesterday, battery charge was 65%. We typically use about 45% overnight, so figured it would be at 20% SoC when charging started in the morning. Spot on!
Screenshot_20230123-084704.jpg
If I hadn't been subscribed to Event Notification, I might have forgotten to look!

Got me thinking about my very brief stint as navigator in predictive log road rallying. Very brief. I found that I don't care to ride with other drivers in break-neck situations, too Type-A, I guess. Not that I didn't trust Josh and his Opal Cadet with my life (I didn't, I guess), I just couldn't get the hang of the Welsh swear words in the heat of battle.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Thu Jan 26, 2023 10:03 am

Looks like we are headed into a cloudy/rainy period. (Almost guaranteed, as I decided to re-pursue my Astronomy hobby, and bought a fancy computerized telescope mount. That should guarantee at least 30 days of unrelieved cloudy weather.) One consequence is needing to run the generator yesterday. It's been a while!
Screenshot_20230126-075602.jpg

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Mon May 22, 2023 12:31 pm

Coming up to the longest day of the year, even where we still have rainy and cloud craziness, this is the programming I have settled on:
Untitled.png
Of course winter is different. But to the Subject, I love my batteries. In the summer/winter I can completely exclude any maintenance or oversite except for a few programming changes. This is not necessarily a good thing. A guy can get lazy. I have the Victron programmed to reset 100% when these parameters are met. It works OK for a month. Then I do an EQ to 56.4, maybe another the next day to balance the batteries. I understand that.

But. Hah, the But! I wish the PHIs had a way for feed back. Frankly, I would love to know what is counted as a cycle. Theoretically I should have very few (full) cycles over these two years. Who would know?

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: I ❤ my LiFePo4 battery

Post by raysun » Mon May 22, 2023 1:05 pm

Frankly, I would love to know what is counted as a cycle.
I saw Phi's explanation of a cycle once, but don't recall where, or its full details. I dismissed the notion because the next sentence stated Phi does not warrant its batteries on cycles, rather on time in service. (Their pro-rated warranty is basically not worth pursuing after 5 years.)

54V is somewhere in the 80% SoC range. If that's enough capacity, then well and good.

When executing "EQ", is the actual Start EQ charge function executed? If so, the 1 Hour timer is going to be in play. I'm not sure I'd want to hold the battery (on purpose, or incidentally) at 56.4V for 1 hour.
Perhaps an "EQ" voltage of 54.6V @ 1H might fill the bill.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: I ❤ my LiFePo4 battery

Post by JRHill » Mon May 22, 2023 2:16 pm

raysun wrote: ↑
Mon May 22, 2023 1:05 pm
Frankly, I would love to know what is counted as a cycle.
When executing "EQ", is the actual Start EQ charge function executed? If so, the 1 Hour timer is going to be in play. I'm not sure I'd want to hold the battery (on purpose, or incidentally) at 56.4V for 1 hour.
Perhaps an "EQ" voltage of 54.6V @ 1H might fill the bill.
No, Buddy. When I do an EQ I am watching and waiting with time set aside to watch the system. IT DOESN'T"T TAKE TO LONG. I start it after the batteries have finished the Bulk and .2 Absorb. I'd say less than a half hour. Certainly easier than taking SGs and I never have holes in my clothes any more (wink).

JoeLeng
Forum Junior Member
Posts: 1
Joined: Wed Jul 24, 2024 4:22 am

Re: I ❤ my LiFePo4 battery

Post by JoeLeng » Wed Jul 24, 2024 4:25 am

Image
Image
I purchased three sets of batteries from Neexgent, each set containing 4 cells, and they’ve been performing well so far. However, the delivery of the final set was delayed by a few weeks due to supply issues.

I assembled each set of 4 cells into a 12V battery with a BMS and tested them at a 25-amp discharge rate, resulting in a voltage of 11.1 volts at the BMS(-) and battery (+) terminals.

The capacities tested ranged from 309Ah to 314Ah. The slightly lower test results could be attributed to several factors, such as undercharging, stopping the test at too high a voltage, or potential inaccuracies in my testing equipment. One cell was slightly larger than the others, but otherwise, the physical condition of all cells was good. I haven’t put them into service yet, so I will provide updates if any significant issues arise.

https://www.neexgent.com/product/neexge ... -rate.html
Last edited by JoeLeng on Wed Jul 24, 2024 4:28 am, edited 1 time in total.

Post Reply