I just stumbled across this surge protector while doing some online shopping. It's odd I haven't seen it mentioned anywhere else. But would it still work if I put a Flexware 250 on both sides of the inverter?
https://readymaderesources.com/product/ ... fw-sp-aca/
Should I get a FW-SP-ACA ?
Moderators: OutBack Moderator Team, OutBack
-
pioneerMan
- Forum Czar
- Posts: 584
- Joined: Wed Jan 09, 2019 3:40 pm
- My RE system: 12 volt system
6 Lion Energy model 700 batteries, 12V each
12 solar panels (Mitsubishi 125 Watt)
Outback VFX2812 inverter and two FLEXmax 60 inverters
Mate 3s
Dual fuel 4500 watt generator - Location: Northern Utah
-
raysun
- Forum Overlord
- Posts: 13665
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Should I get a FW-SP-ACA ?
The Flexware Surge Protector is mostly meant to protect the inverter. It has 3 protection circuits that are typically connected to inverter:
AC OUT, AC IN, and DC IN. It is usually mounted on the "AC" end of the inverter.
AC OUT, AC IN, and DC IN. It is usually mounted on the "AC" end of the inverter.
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: Should I get a FW-SP-ACA ?
According to the manual
https://outbackpower.com/downloads/docu ... tector.pdf
"NOTE: The FW-ACA, which houses the surge protector, is designed as a wireway between FX
Series Inverter/Chargers and OutBack enclosures (508A Industrial Control Panels) including the
FLEXware 500 and FLEXware 1000. The FW-ACA’s knockouts are not intended for conduit, but can
accommodate flexible cables with appropriate strain relief."
It sounds like this device can be used stand alone without a FW250, although the flexware enclosure is a good, but not the only, way to provide the necessary breakers.
https://outbackpower.com/downloads/docu ... tector.pdf
"NOTE: The FW-ACA, which houses the surge protector, is designed as a wireway between FX
Series Inverter/Chargers and OutBack enclosures (508A Industrial Control Panels) including the
FLEXware 500 and FLEXware 1000. The FW-ACA’s knockouts are not intended for conduit, but can
accommodate flexible cables with appropriate strain relief."
It sounds like this device can be used stand alone without a FW250, although the flexware enclosure is a good, but not the only, way to provide the necessary breakers.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
raysun
- Forum Overlord
- Posts: 13665
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Should I get a FW-SP-ACA ?
There's several points on the system that are vulnerable to surge damage and that can benefit from surge protectors.
PV input lines from arrays to charge controllers. Lightning can cause high voltage surges on PV Arrays that would well exceed the 150V limit of charge controller input. Surge protectors are generally installed at the PV combiner boxes.
https://www.solar-electric.com/midnite- ... ector.html
Inverter AC Output, AC Input.
I've seen a couple inverters with failed power boards that were likely caused by high voltage surge backfed from the house wiring. AC Input surges would generally be from grid connections, but in some circumstances, a generator circuit might generate one.
Inverter DC Input.
I've not seen a surge impressed on the battery line, but it could happen in certain circumstances.
The FW-SP will address the inverter protection.
PV input lines from arrays to charge controllers. Lightning can cause high voltage surges on PV Arrays that would well exceed the 150V limit of charge controller input. Surge protectors are generally installed at the PV combiner boxes.
https://www.solar-electric.com/midnite- ... ector.html
Inverter AC Output, AC Input.
I've seen a couple inverters with failed power boards that were likely caused by high voltage surge backfed from the house wiring. AC Input surges would generally be from grid connections, but in some circumstances, a generator circuit might generate one.
Inverter DC Input.
I've not seen a surge impressed on the battery line, but it could happen in certain circumstances.
The FW-SP will address the inverter protection.