Hi Provo, yes I could do that... ultra-slow grid charging would be fine in my application. Although a little higher rate would be nice when I have to go to generator.provo wrote: ↑Sun Sep 04, 2022 7:32 amFor me, this turned out to be the key. I regularly get to CPM after 4-5m in absorb using 2% CRA. When I first got the SimpliPhis it could take 11m !! Then I heard (probably from Raysun) about reducing the charge rate (particularly in the final hour or so). I use Global Charger Control set at 30A for my 300Ah 24V battery, which I know seems crazy low. If I start with fairly discharged batteries I'll raise that for the first few hours and dial it back to 30A for the final hour -- works every time.
SimpliPhi commissioning for UPS application
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
I think there is a perception issue here. Also, an incomplete understanding of the role and behavior of the FNDC.seanadams wrote: ↑Sun Sep 04, 2022 7:31 amHave I misunderstood the meaning of these settings? I thought that the charging cycle would operate according to what is in the Radians's charger settings, not the FNDC settings.
And the FNDC settings for CRA conditions were only used to drive the logic for how the FNDC establishes the SOC, for reporting purposes.
If I set it to 80 A, it still seems to complete the charging just the same, and I still see the current decay down through <9A. However, this happens very quickly in either case. If I had the FNDC set to 9A, then it would miss the condition. Setting it higher gives it more time to detect the condition.
The problem I'm having is that my FNDC is actually getting locked up... completely wedged at 100% SOC unless I do this to help it detect the CRA.
I have only had these batteries running for a couple days and I am really lacking in data points to fully understand this. It would help to know the exact semantics of the settings. I will RTFM again because I vaguely remember something about an option for the FNDC to influence charging behavior, or not. But I could not find that option in the settings.
First and foremost, the the FNDC does not control charging behavior in any way. It simply monitors current flow and battery voltage. It uses those values to derive State of Charge. It can also use certain sensed values to signal charge state to the Mate. The Mate can be configured to use the Charged Parameters Met signal to terminate charging by all chargers.
That the battery can transition from accepting a high rate of charge to accepting essentially no charge in the figurative blink of an eye is an artifact of LiFePo4 cell physics. When the cells are full, they essentially stop accepting charge. OpticsRE often misses the transition, but the FNDC doesn't.
Regarding the comment about the FNDC being "stuck", can you provide more details? The only condition similar to this that I've experienced has to do with small errors in the FNDC's cumulative SoC calculations. Deriving SoC is no simple task. On discharge, it must take Peukert's Law into account. For Lead Acid that's a challenge, for lithium even more so, as the Peukert Constant can't be adjusted for the battery chemistry. On charging, the FNDC must take Charge Efficiency into account. The manufacturers publish a figure, but its by no means set in stone, rather an estimate with its own built-in error. The net result of working with these to calculations and their margins of error, is the FNDC can indicate 100% SoC before the battery is actually fully charged. That's why its important to "sync" the meter by fully charging the battery, so that 100% SoC reading then reflects the true 100% battery state of charge. The best way to know that sync has occurred is having the FNDC sense the battery full charge conditions: battery voltage above 55.6V and charge current below 9A.
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
OK, yes I follow everything you just said.
The behavior I saw yesterday was that the FNDC was reading 100% continuously, even while I was drawing down the batteries. Let me run some more cycles and see if I can really understand it properly. I figured the FNDC had seen the voltage-met but not the CRA-met condition... and it was locked up in a bad state.
Or, I don't know if it can internally register a SOC > 100%, and maybe it was reporting the max of 100%. Like maybe it was counting down internally but it was still above 100%.
getting more data...
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
I am not worried about absolute precision here.... don't care about the precise correction factor or anything like that. I just want it to not be stuck at 100% when it should be dropping.... Because I am using this signal to control my load shedding. That's the main goal. It's nice to see the reading but I'm not worried about having some particular minutes of run-time or anything.
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
That's a long cycle followed by a shorter one, on the same settings. You can see the shorter cycle ends with some constant voltage and tapering of the current. Albeit VERY short... it only takes two minutes and does not hang out below 9A.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
What was the duration of the draw with the FNDC reading 100%?The behavior I saw yesterday was that the FNDC was reading 100% continuously, even while I was drawing down the batteries.
What was the rate of discharge?
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
Found this setting. It has been off.
Could be interesting to try it though? Because the Radian could be configured with some absorb time, and then the FNDC, when it detects the ending conditions could stop the cycle. Everyone should be happy, in theory?
Could be interesting to try it though? Because the Radian could be configured with some absorb time, and then the FNDC, when it detects the ending conditions could stop the cycle. Everyone should be happy, in theory?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
Yes Auto Charge Termination Control is designed to terminate charging when the Charged Parameters Met flag is set. I have it enabled, and it typically terminates charge between 1 and 5 minutes after the chargers switch to CV. (Absorb Time is set to 6 minutes, and FNDC/Charged Time is set to 1 minute.)seanadams wrote: ↑Sun Sep 04, 2022 8:44 amScreen Shot 2022-09-04 at 9.42.47 AM.png
Found this setting. It has been off.
Could be interesting to try it though? Because the Radian could be configured with some absorb time, and then the FNDC, when it detects the ending conditions could stop the cycle. Everyone should be happy, in theory?
A typical charge cycle.
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
Here's a couple pics of my install.
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
Still seeing premature termination of CV stage, despite FNDC not meeting parameters.
Surely this is an bug/undocumented behavior in the radian. It should stay in absorb for the programmed time unless FNDC terminates.
Surely this is an bug/undocumented behavior in the radian. It should stay in absorb for the programmed time unless FNDC terminates.
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
Long story... one is just sitting there for now and I'm running these Radians "stacked" in the normal way. But I am having a problem when running on generator that might motivate me to split them into two separate systems. One system would do charging, gen input, and power for my 3HP well pump. The other would power the house but not do any charging.
The problem I'm having is that my generator is undersized and noisy, so I can't get it to sync in "support" mode". And I can't seem to stop the breaker on the generator from tripping even though I set limits on the AC inputs. And my lights flicker and the fridge makes weird noises and all that. If I use the generator only for charging and running my well, then the rest of the house can be isolated via the DC rails... essentially a dual-conversion UPS when running on generator. I think it would work really well but I don't want to over-complicate things. So I might not do it. Now that I've got these phi batteries, my run time is good enough that I will hardly be using generator power ever.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
Looking at the graph, I'd suggest the battery voltage has risen sufficiently above the Absorb Voltage that the chargers are going idle. The inverter chargers may be responding slowly to the "twitchy" nature of LiFePo4 near full charge.seanadams wrote: ↑Sun Sep 04, 2022 9:58 amStill seeing premature termination of CV stage, despite FNDC not meeting parameters.
Surely this is an bug/undocumented behavior in the radian. It should stay in absorb for the programmed time unless FNDC terminates.
Screen Shot 2022-09-04 at 10.54.49 AM.png
Screen Shot 2022-09-04 at 10.50.29 AM.png
I'm not a Radian user, so don't know what's possible here, but the two GS8048 are comprised of four inverter modules, hence four chargers all working in parallel. As an experiment, if possible, disable charging from one of the GS8048s and see if there is different results.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
The generator is electrically "noisy" for sure:seanadams wrote: ↑Sun Sep 04, 2022 10:03 amLong story... one is just sitting there for now and I'm running these Radians "stacked" in the normal way. But I am having a problem when running on generator that might motivate me to split them into two separate systems. One system would do charging, gen input, and power for my 3HP well pump. The other would power the house but not do any charging.
The problem I'm having is that my generator is undersized and noisy, so I can't get it to sync in "support" mode". And I can't seem to stop the breaker on the generator from tripping even though I set limits on the AC inputs. And my lights flicker and the fridge makes weird noises and all that. If I use the generator only for charging and running my well, then the rest of the house can be isolated via the DC rails... essentially a dual-conversion UPS when running on generator. I think it would work really well but I don't want to over-complicate things. So I might not do it. Now that I've got these phi batteries, my run time is good enough that I will hardly be using generator power ever.
Total Harmonic Distortion ≤23%
It will need to run in "Generator" mode, and would definitely be an issue for delicate electronics, motors, and compressors. Isolating its use to charging only would be helpful.
I'm actually working on a "backup to the backup" charging scheme to integrate into my system using a stand-alone AC charger that would hopefully tolerate a "dirty" AC source. In my case, to accommodate a smaller portable generator than is connected to my inverters. (We are off-grid.)
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
Yep, the house doesn't like it. I might do this. However my well is a Franklin VFD "subdrive" system which does a conversion to 3-phase. So it doesn't seem to care if the input is dirty... it gets converted. It's ok to run on generator and they even give the specs for what generator is needed for it. So that load (4.7KW max) stays on one unit, and the rest of the house (5KW max) goes on the other unit. It's a bit complicated but it makes sense.
I will be curious to know if you find a good charger for this purpose. I looked a little bit into this (golf cart chargers etc) before figuring out that I could configure the Radians I already have in this way. I guess the Radian is a good charger in its own right, even if that's all you used it for.I'm actually working on a "backup to the backup" charging scheme to integrate into my system using a stand-alone AC charger that would hopefully tolerate a "dirty" AC source. In my case, to accommodate a smaller portable generator than is connected to my inverters. (We are off-grid.)
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
same result with one charger. I set it to run one charger at 24 AC amps, as opposed to two chargers at 12 amps each.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
I'll be curious if I find a good charger too. So far, I'm not impressed with the offerings.I will be curious to know if you find a good charger for this purpose. I looked a little bit into this (golf cart chargers etc) before figuring out that I could configure the Radians I already have in this way. I guess the Radian is a good charger in its own right, even if that's all you used it for.
I picked up a couple of Aims 48V chargers for cheap so I'll start with those. They do not have an ideal charging profile, so I'll have to implement some external control - essentially cutting off the charger at the target termination voltage. 37A charging capacity.
Mean Well makes some potentially promising battery charger modules founded on their switching power supplies. They can be programmed using an inexpensive hardware interface and PC software. They're not cheap, however, and building an 80A charger would run about US$1500 or so.
It might make sense for me to just buy another Outback inverter to use as a charger.
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: SimpliPhi commissioning for UPS application
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
Could try it, but I would need to halve the charging power - that would introduce another variable.
I've been trying something else here... I am seeing that with absorb time set to 0.2 hours, it behaves a lot better. I just ran two cycles in a row that both did a "parms met". It still ramps down quickly, but it gets the "parms met" event. I guess it's terminating per the FNDC.
I am suspecting an off-by-one error that makes the timer not work right at minimum setting. maybe
It could be a fluke so I will run a few more cycles.
-
provo
- Forum Emperor
- Posts: 1464
- Joined: Thu Jul 27, 2006 4:34 pm
- My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back - Location: Sierra foothills
Re: SimpliPhi commissioning for UPS application
Well, yes, and that's what I used to do when I "needed" 11m to meet the CPM settings. You can also raise the charge return amps, but that's just another workaround (so-called "lying to the system so that it will lie to you").
Have you tried dialing back on charge current?
-
seanadams
- Forum Expert
- Posts: 59
- Joined: Wed Oct 03, 2012 8:20 am
- My RE system: 2x GS8048, FNDC.
No PV. Using as UPS only.
6x SimpliPhi 3.8-48
Max real load is 10 KW
Westinghouse 7500DF generator - Location: Costa Rica
Re: SimpliPhi commissioning for UPS application
I just did 3 consecutive cycles that got a "parms met". Absorb time 0.2.
SOC is behaving as expected.
I will run some longer cycles also. will do more testing
SOC is behaving as expected.
I will run some longer cycles also. will do more testing