Shot in the dark:
My MATE failed yesterday. Replacement is on the way. But until then, is it possible to control AGS settings without the MATE? I thought maybe the CAT5 wire could plug into a PC, and maybe there is a software that would allow control of settings, sans the MATE.
Thank you
MATE control from PC?
Moderators: OutBack Moderator Team, OutBack
- intellact
- Forum Czar
- Posts: 806
- Joined: Mon Nov 28, 2005 3:20 am
- My RE system: GVFX 3624 and MATE/MATE3/AXS Port with four Surette flooded lead-acid batteries (24V). Deactivated wind turbine. System now acts as UPS back-up. Monitored by WattPlot, of course.
- Location: Ontario, Canada
- Contact:
Re: MATE control from PC?
Unfortunately, no. The CAT5 cable is simply used to transmit proprietary signals between the MATE and the devices.
There are other Outback devices that could take the MATE's place (MATE3, AXS Port, etc.), and good software that can monitor and control your system through the MATE or other device, but something has to be there to do the translation.
There are other Outback devices that could take the MATE's place (MATE3, AXS Port, etc.), and good software that can monitor and control your system through the MATE or other device, but something has to be there to do the translation.
Andrew Welch, creator of WattPlot
- intellact
- Forum Czar
- Posts: 806
- Joined: Mon Nov 28, 2005 3:20 am
- My RE system: GVFX 3624 and MATE/MATE3/AXS Port with four Surette flooded lead-acid batteries (24V). Deactivated wind turbine. System now acts as UPS back-up. Monitored by WattPlot, of course.
- Location: Ontario, Canada
- Contact:
Re: MATE control from PC?
Yes and No.Mumphi wrote: ↑Fri Aug 11, 2023 12:50 amNo, the MATE (Monitoring and handle) system is required in order to handle AGS (Automatic Generator Start) settings. The AGS settings and other features of the power system can be monitored and managed through the MATE system's user-friendly interface. It could be essential to manually operate the generator without the MATE system or to use a different monitoring and control system.
You need an intermediary device to control your OutBack equipment, but it does not have to be a MATE. An AXS Port would suffice (including offering AGS), if you have good software to control it. Such software is readily available - software that FAR exceeds the capabilities of the MATE/MATE3/MATE3S, and that has the much friendlier user interface that you may be looking for on a PC.
The AGS functionality can also be replicated and surpassed by a program that offers full (a very user-friendly) programming of triggers and actions, using your PC - functionality that can not only control your generator, but can alter any setting on your MATE3(S) in response to system conditions/time-of-day/etc.
(Full Disclosure: WattPlot is the only software that I am aware of with this functionality.
Andrew Welch, creator of WattPlot