Battery to PSDC wiring

Discussion about the Power System DC Disconnect (PSDC)

Moderators: OutBack Moderator Team, OutBack

Post Reply
DavidB
Forum Guru
Posts: 246
Joined: Sun May 19, 2002 11:01 pm
Location: Minnesota

Battery to PSDC wiring

Post by DavidB » Wed Nov 01, 2006 12:22 pm

I wanted to verify that this is correct since I am installing my new batteries.. It is a 48V battery bank.

I am pairing 2/0 copper from the battery bank back to the PSDC. The positive cables will be connected via 2 lugs to the 175A breaker for the 3648 inverter. From the 175A breaker I need to connect a cable back to the DC positive bus bar. Question is what size should this cable be? DC positive bus bar can take up to 1/0.. and I have left over 1/0.. perhaps I should just use that.. :smile:

I originally thought with 3 lugs on the breaker I would have to deal with cables going in three orthogonal directions but it looks like I can simply flip one upside down so they can stack one on top of the other and only have 2 different directions..

Have to say again how nice it is to have studs on the breakers!

User avatar
mvrck
Forum Czar
Posts: 624
Joined: Mon Oct 17, 2005 10:03 am
My RE system: Solar Commander since 2005, Maverick Solar Enterprises, Inc.
NABCEP Certified Solar PV Installer (formerly)
House: Radian GS8048A, 1600Ah LiFePO4 (Pytes & eFlex), 13.5kW Solar
Office: Fortress ENVY12k, 19.2kWh eForce LiFePO4, 9.0kW Solar
Shop: XW6048, 510Ah AGM, 3.1kW Solar
Cabin: XW6048, 800Ah AGM, 8.1kW Solar
Location: San Marcos, Texas
Contact:

Post by mvrck » Wed Nov 01, 2006 1:11 pm

The size should match the current requirements of the items connected the positive bus, like MX60s, etc...

If the 1/0 is the proper type like THWN-2 and you have a good lug for it to bolt onto the buss plate, then let 'er rip...

Thanks
Maverick MacGyver