Battery SoC leaps up to 100%
Moderators: OutBack Moderator Team, OutBack
- kiwisolar
- Forum Expert
- Posts: 74
- Joined: Wed Jun 30, 2021 10:59 pm
- My RE system: VFXR3048E
FM80-150VDC
Flexnet DC
Hoppecke Sun Power VR-M 6V 250AH batteries (16 total, 48V).
Gentech EP8000HSRE-RS Generator with Honda 390GX engine.
Battery SoC leaps up to 100%
Hi all,
I'm a new user to solar and finding my way. Things have been going ok, until winter and it's grey days. Combined with a broken generator, means our batteries have had a bit of a hard time and def dipped low.
Anyway, a couple of weeks ago when I finally got a spare generator to charge, it ran for a few hours with the SoC tracking up slowly but at an assumed normal rate. It got to about 80%, then leapt up almost instantly to 100%.
Today, I noticed the same thing happened when we got a decent amount of sunshine after about a week of declining SoC (still no generator, sigh), spent all morning tracking up gradually, got to a bit over 80%, then leapt up to 100%.
I see it did bulk charging until about midday, then absorb for next 2.5 hrs as programmed.
My question is, is this normal? Is the SoC really 100%? Or does something need a reset?
I'm a new user to solar and finding my way. Things have been going ok, until winter and it's grey days. Combined with a broken generator, means our batteries have had a bit of a hard time and def dipped low.
Anyway, a couple of weeks ago when I finally got a spare generator to charge, it ran for a few hours with the SoC tracking up slowly but at an assumed normal rate. It got to about 80%, then leapt up almost instantly to 100%.
Today, I noticed the same thing happened when we got a decent amount of sunshine after about a week of declining SoC (still no generator, sigh), spent all morning tracking up gradually, got to a bit over 80%, then leapt up to 100%.
I see it did bulk charging until about midday, then absorb for next 2.5 hrs as programmed.
My question is, is this normal? Is the SoC really 100%? Or does something need a reset?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Battery SoC leaps up to 100%
You are witnessing my least favorite feature of the FNDC. Though the conversation with a former OB engineer is lost in the mists of time, the seeming leap to 100% was explained as a "battery protection" feature when the system doesn't think charging will actually result in a full charge.
This old app note may contain some clues:
https://us.v-cdn.net/6024911/uploads/ed ... pn40hq.pdf
An even older post on the subject: viewtopic.php?f=28&t=7448
This old app note may contain some clues:
https://us.v-cdn.net/6024911/uploads/ed ... pn40hq.pdf
An even older post on the subject: viewtopic.php?f=28&t=7448
- kiwisolar
- Forum Expert
- Posts: 74
- Joined: Wed Jun 30, 2021 10:59 pm
- My RE system: VFXR3048E
FM80-150VDC
Flexnet DC
Hoppecke Sun Power VR-M 6V 250AH batteries (16 total, 48V).
Gentech EP8000HSRE-RS Generator with Honda 390GX engine.
Re: Battery SoC leaps up to 100%
Thanks for that! Looks like I have a lot of reading and learning in my immidiate future :(
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Battery SoC leaps up to 100%
One of the takeaways is an older, or chronically undercharged battery may give the FNDC fits. Sulfate buildup in lead-acid batteries is the main bad actor.
If you are using Automatic Charge Termination, you might want to disable it and let the charge controller programming run its full (as possible) cycle.
Are these flooded or sealed batteries?
*EDIT* Look like sealed batteries. About the best that can be done is to charge them according to spec, then check voltage to get an idea if every block is roughly the same, voltage-wise.
If you are using Automatic Charge Termination, you might want to disable it and let the charge controller programming run its full (as possible) cycle.
Are these flooded or sealed batteries?
*EDIT* Look like sealed batteries. About the best that can be done is to charge them according to spec, then check voltage to get an idea if every block is roughly the same, voltage-wise.
- kiwisolar
- Forum Expert
- Posts: 74
- Joined: Wed Jun 30, 2021 10:59 pm
- My RE system: VFXR3048E
FM80-150VDC
Flexnet DC
Hoppecke Sun Power VR-M 6V 250AH batteries (16 total, 48V).
Gentech EP8000HSRE-RS Generator with Honda 390GX engine.
Re: Battery SoC leaps up to 100%
Thanks for the tips, I will check the voltage etc, and also find out more about this FNDC thing.
Looking remotely with negligible load on (it's a holiday home, so fridge and internet is about only thing on), voltage seems ok, compared with dates earlier on before my big battery discharges. I'm guessing I will need to check battery voltages when its disconnected completely though?
Learning curve, so you'll probably see me posting here again soon!
Looking remotely with negligible load on (it's a holiday home, so fridge and internet is about only thing on), voltage seems ok, compared with dates earlier on before my big battery discharges. I'm guessing I will need to check battery voltages when its disconnected completely though?
Learning curve, so you'll probably see me posting here again soon!
- kiwisolar
- Forum Expert
- Posts: 74
- Joined: Wed Jun 30, 2021 10:59 pm
- My RE system: VFXR3048E
FM80-150VDC
Flexnet DC
Hoppecke Sun Power VR-M 6V 250AH batteries (16 total, 48V).
Gentech EP8000HSRE-RS Generator with Honda 390GX engine.
Re: Battery SoC leaps up to 100%
A question about the "Automatic Charge Termination" in the above comment.
I can only see a checkbox that says "enable continuous charging" on the VXFR (in the float time setting). Is that what I want checked?
I see nothing under the FM80 or FNDC options along lines of Automatic Charge Termination.
Thanks!
I can only see a checkbox that says "enable continuous charging" on the VXFR (in the float time setting). Is that what I want checked?
I see nothing under the FM80 or FNDC options along lines of Automatic Charge Termination.
Thanks!
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: Battery SoC leaps up to 100%
Its in the Mate's Global Charge menu.
- kiwisolar
- Forum Expert
- Posts: 74
- Joined: Wed Jun 30, 2021 10:59 pm
- My RE system: VFXR3048E
FM80-150VDC
Flexnet DC
Hoppecke Sun Power VR-M 6V 250AH batteries (16 total, 48V).
Gentech EP8000HSRE-RS Generator with Honda 390GX engine.
Re: Battery SoC leaps up to 100%
Excellent thanks @raysun. So many options!
- SandyP
- Forum Czar
- Posts: 601
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Battery SoC leaps up to 100%
Not sure if you "need/have" to have your fridge on all the time but if not and only want it to be cold when you arrive there then maybe look at using one of the WiFi plugs so you can switch it on/off remotely (Philips, WeMo,DLink etc).
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
sbrownian
- Forum Czar
- Posts: 660
- Joined: Mon Nov 30, 2020 9:23 am
- My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!! - Location: Central Washington State
Re: Battery SoC leaps up to 100%
I judiciously AVOID cloud based 'solutions' like those. I prefer mapping a port out and setting up firewall rules plus encryption.
(DDNS for name resolution.)
Kinda depends on your ISP though. Some use a private cloud that NATs out to the internet, in which case you need to setup a VPN to be able to get to the 'public' IP addy...
(DDNS for name resolution.)
Kinda depends on your ISP though. Some use a private cloud that NATs out to the internet, in which case you need to setup a VPN to be able to get to the 'public' IP addy...
Information, you get not; if incorrect question, you ask..