I’ve just installed the GS-AC-Gen-Kit GT Inverter isolation relay on one of my AC Coupled Systems. The relay itself is a mechanical contact type switch. The switch uses two sense wires hooked up to the 240volt Generator buss bars to activate it and disconnect the GT inverter to protect the generator. That said, my client’s generator only has 120volt output. I was assuming that the one hot leg would trigger it, but it does not seem to. Perhaps as there is no neutral or second Hot Leg energized it cannot complete the circuit. Does anybody have any experience getting this relay to work with a 120 volt generator?? Thanks in advance.
4kw in dc solar
3kw SMA GT inverter
Radian 8048A
SimpliPhi Batteries
GS-AC-Gen-Kit help
-
sbrownian
- Forum Czar
- Posts: 660
- Joined: Mon Nov 30, 2020 9:23 am
- My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!! - Location: Central Washington State
Re: GS-AC-Gen-Kit help
A quick RTFM reveals the relay hooks across L1 and L2 in the load center, implying the relay coil is 240 vac rated...
Information, you get not; if incorrect question, you ask..
-
raysun
- Forum Overlord
- Posts: 13665
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: GS-AC-Gen-Kit help
I don't use a Radian, so can only ask. The manual specifies a split phase generator, which I assume means 240V split phase. Does a 120V single phase generator even work?That said, my client’s generator only has 120volt output.