Re: Guess the SoC prediction game

Post by raysun » Sun May 30, 2021 1:25 pm

set Float back to 51.0
That seems very low to me. Does the battery get to that voltage?

I think when the manufacturers say not to Float charge an Li battery, they mean don't hold it at 100% SoC (via Float in this case.) That's the reason I carefully select a Float voltage that always has the battery dropping 1%-2% and always discharging a small amount for the full Float phase.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Sun May 30, 2021 6:13 pm

This is my take on charging SimpliPhi 3.8-48 battery blocks using Outback FM80 charge controllers, and the Outback FNDC/Mate3s for charge termination.

The charge profile is essentially a constant current (Bulk) charge to a termination voltage of 56.4V and end current equalling 2% of C20 (9A for the 450AH battery.)

After the Bulk phase terminates, the FM80 charge controllers automatically enter a Float phase until sunset. This cannot be defeated, and while SimpliPhi recommends against Float charging the battery, they do specify a Float voltage of 54V. I don't care to hold the battery at 100% State of Charge, so modify Float to allow a small, continuous discharge during the Float phase.

Prior posts detail the charging parameters used.

The screen captures are annotated with time stamps.

1:13 System shows 100% SoC, but battery voltage says otherwise.
20210530_145857.jpg

1:14 56.4V termination voltage reached, but net amps are above Charged Return Amps.
20210530_145926.jpg

1:15 Charged Return Amps = 23A reached. 60 second count down starts.
20210530_150746.jpg
Continued next...
Last edited by raysun on Mon May 31, 2021 1:01 am, edited 2 times in total.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Sun May 30, 2021 6:36 pm

1:16 A little too slow to capture the 60 second cutoff. Net charging amps at cutoff = 10.2. I can lower the CRA another volt to try for 9A @ cutoff.

Controllers will go silent until Float voltage is reached.
20210530_150059.jpg

1:31 Float voltage = 53.1V.
20210530_150130.jpg

1:51 Float maintains a continuous small discharge throughout the phase
Screenshot_20210530-150233_DuckDuckGo.jpg

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Mon May 31, 2021 9:04 am

raysun wrote: ↑
Sun May 30, 2021 1:25 pm
set Float back to 51.0
That seems very low to me. Does the battery get to that voltage?
It was around 3:30pm when I saw this email. I studied OpticsRE and it showed exactly what I was curious about: After finishing the Bulk and the .1 Absorb the controller went completely silent and the battery voltage dropped back steadily. It was 52.9 at ~4pm. So I set the float back to 53.0 and it began shortly after for the waning usable sunlight. Not a lot of charge was added. Even at that the next morning's low voltage was 52.0 and we used some extra power watching some old classic war movies with the surround sound on later into the evening.

I was also curious about End Amps and wanted to observe it real time. Its obvious now that at .1hr Absorb the End Amps are a non-issue. The thought that floating the PHIs at a ~53 voltage is clear now too and also that a whole afternoon at 99 to 100% SOC is just the way it is to be.

Raysun, thank you for all the info you've shared recently as it greatly helps me and I'm sure some others too.

At this point I am sure I have the optimum summer profile and can print and save the settings in the system docs.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Mon May 31, 2021 9:30 am

YW. That profile runs like clockwork for me and I'm happy with the results.

I'd try sneaking the Float voltage down in a 0.1V increment per day (start at 53V, next try 52.9V, etc.) until you find the "sweet spot". I see about 2-5AH drain off the battery before Float kicks in. The battery stays around 98-99% SoC usually, which is fine for me. My main metric is to see that there is a slight, continuous net discharge during Float. (A heavy load may draw more off the battery, and Float may 'step up' to replace charge, but at the lowered voltage, I don't think the cells are being stressed in any way.)

It works well even in what would pass for winter here. Actually, we have (hopefully) just exited the rainy season where it dumped on us daily for over two months. During that time, I'd have (rare) occasion to run my generator, which I do manually. If I was an AGS guy, I'd likely use SoC Start around 50% and SoC Stop at 80%. Once every couple of weeks, I'd do a 100% charge to reset the meters. I find they are pretty accurate for my purposes.

No I have to get out into the gardens and start hacking things back. After all the rain, I'm kind afraid of what I'll find. 😆😆 I'm taking a machete. Seriously its been a weird year (or we're getting back to normal after 30 years of volcanic eruption.) I see Avocado trees I planted 4 years ago loaded with fruit. The true "this can't be moment" however is a mango tree a friend gave me that he started from seed. Those are usually "junk" trees that don't produce fruit for 12 - 15 years, if ever. This year, it has fruit as a 4 year old. I'll never understand.

Hopefully hurricane season will be as mild as is predicted.
Last edited by raysun on Mon May 31, 2021 3:00 pm, edited 1 time in total.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Mon May 31, 2021 10:09 am

We're in our 8th or 9th year of drought - maybe more, I can't remember. Gardening has become a joke. Even if we have some fruit set the mice, seeking something anything green ruin it before its ready to pick. As of today we've have 11.34" since the rain year began last Oct 1 and that's about it for this year. Being in the rain shadow the sun intensity and low humidity cause everything to cook right in the garden. There is no adequate watering technique. Oh, and wherever you water expect a rattlesnake or more to come in for relief and the get a mouse seeking the same.

But screw the garden. We just hope to go another year with no wildfire. But we love it here anyway.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Tue Jun 01, 2021 11:32 am

raysun wrote: ↑
Mon May 31, 2021 9:30 am
YW. That profile runs like clockwork for me and I'm happy with the results.
So after all that messing around I'm back to exactly where I was beforehand. Still 56.4/.1 and 53.0 float. The only changes are the End Amps are at 0 and Rebulk is set back slightly more to 51.0 but those should matter not. But this is the curious part and one of the reasons I started the experiment.
Untitled1.png
Notice the charge input and SOC being held for hours in the afternoon. And now this:
5-31-21.png
After the charge cycle has completed the system heads to Float with a trickle in to keep voltage at 53.0 as before. All other settings are the same except as stated above. But the SOC?!? Before and after the Days Since Parameters Met have been satisfied and SOC reset. But now the kW into the batteries isn't as much through the afternoon and the bars/lines look like what I always thought they should be.

The only thing that I can think of is that even though the SOC has been reset in both before and after attachments, there must be something in the recent history that the FNDC is factoring into the day's SOC display. In no recent time have I hard reset the FNDC so the history must be involved? But also the inputs through the afternoon are lower. Humm.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Tue Jun 01, 2021 1:59 pm

After Charge Termination, the FNDC has nothing to do with the action of the Charge Controllers, other that reporting current flow.

Looking at the two graphs, it would appear the first has Float more closely satisfying the load, so the SoC looks to be in the very high 90s for the duration.

The second seems to be "short of demand" so more is being drawn from the battery. Either the PV panels are not producing as much due to cloud cover, etc., or the Float voltage needs to be "tweeked".

I'd double check the charge controller calibration.

Empirically, setting Float Voltage a bit higher (try 53.1V) will permit more available charge to flow from the PV array.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Tue Jun 01, 2021 2:25 pm

raysun wrote: ↑
Sat May 29, 2021 1:13 pm
SimpliPhi (like pretty much every LiFePO4 vendor) specifies against Float and then specifies a "full on" Float voltage for the charge controller (and none for generator/grid.) Part of the reason for the apparent disparity is the FlexMax controllers automatically enter Float after Bulk/Absorb completes and remain in Float until the sun goes down, or a REBULK event.

If one chooses, its pretty easy to defeat Float (for the most part) by setting Float Voltage as low as possible, however, IME its not necessary or even desirable, as it wastes even more PV generation. (I am a life member of the Save the Photons Society. We have a spokesmodel and everything. Its really quite a deal.)

For my part, keeping the battery from the ravages of Float, while maximizing PV harvest, is the reason I experimented with the Float Voltage to find that "sweet spot". For my typical loads, Float=53.1V is perfect. As soon as the charge terminates at 56.4V, the charge controllers go Silent, and remain so until the Float Voltage is reached. That interval drains about 4-5AH off the battery, or about 1%. Holding Float at 53.1V typically drains 0.1A from the battery, though heavy loads may drain more. At no time does Float add net charge, unless the battery drops below Float Voltage. Float never returns the battery to 100% SoC, and at the end of Float, the battery typically sits at 96% SoC, though it may be as high as 98% on a very low load day.

The battery enters the end of daylight having been at 100% SoC for all of 60 seconds, and then gently discharges until nightfall.

You may wish to use a lower Float voltage, as your system is typically more lightly loaded than mine. Try 53.0V. The key for me is there is always a small discharge after 100% SoC.

Morning low voltage of 53V is pretty much in the ideal range. You are fretting over nothing.

Lowering CRA to 6A is going to be the Phi specified 2% end amps target for a 300AH battery.

Setting the Charge Controller End Amps to other than 0 is not useful on normal operation. Setting Charged Return Amps on the FNDC properly is quite useful.

My CRA target is 9A. I found, however, that starting the 1 Minute Charged Time countdown at 9A actually let the charging amperage go to 0A (BMS cutoff activated, I suspect.) I experimented with CRA, and actually have it set to 23A. At the end of 60 seconds, the charge current hits 9A as charging terminates. This little "sleight of hand" would likely have a different value for a 300AH battery.

REBULK is the last piece of the puzzle. The FM charge controllers wake up every day and automatically start a Bulk charge. REBULK does modify the Absorb Time setting (0.1H in my case), but it doesn't appear to have an impact. For some reason, my FMs have REBULK set to 51.2V, a voltage my battery rarely, if ever, reaches. In theory, Absorb Time would be decremented by the REBULK algorithm to the minimum allowed, but since Absorb Time is already at the minimum allowed, it seems to have no effect.
[above emphasis mine]

The one last thing I have on the plate is the determination/tuning of the float voltage as you mention above. I have a lot of summer to play with this. As I follow your info, on a normal day I don't want an instant but normal load to pull the batteries below Float voltage (faster than the CC can respond?). But whether I have float set at 53.1, 53.0 or 52.9, and given that I'm already Floating, what's the difference? Whether 53.1 or 52.9 that load is just as likely to pull below Float voltage, one setting from another? To me it is more an issue of how fast the CC responds to stay at Float voltage given there is solar to support it. And that's curious because the Mate3 shows me hitting highs and lows that have to be quite instantaneous and you'd never detect that from OpticsRE. If its that instantaneous its gonna be faster than the CC can respond?

So how exactly is that tuning determined regardless of 53.1, 52.9, etc. I'm missing something.

This recent stuff should really be in the PHI tuning thread.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Tue Jun 01, 2021 2:32 pm

I think you gave me the hint I was looking for as I was typing the above.

Seriously, that 0.1, 0.2 or 0.3 really makes that much difference to the CC?

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Tue Jun 01, 2021 3:55 pm

JRHill wrote: ↑
Tue Jun 01, 2021 2:32 pm
I think you gave me the hint I was looking for as I was typing the above.

Seriously, that 0.1, 0.2 or 0.3 really makes that much difference to the CC?
As I was "dialing in" Float, I found that 0.1V increments made a good deal of difference.

For me,

53V was too low. Too many load demands drew excessively from the battery. (Goldilocks sez: Too cold.)

53.2 was too high. The battery would bump along at 100% SoC. (Gl sez: Too hot.)

53.1V allowed a small charge ~ 5AH to drain off before Float engaged. Nominal loads draw about 100ma more than the charge controllers are providing. (Gl sez: Just right!)

If a large load comes along, or clouds reduce output, the battery provides more current. Its generally always made up when conditions change.

At the end of Float, I like the battery to be in the 96-98% SoC range.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Tue Jun 01, 2021 8:44 pm

20210601_173854.jpg
A busy day. Summer sun is definitely on us on clear days. My carpenter was busy ripping and planing 1000 sq/ft of Caledonian Pine fence boards. Painter was power sanding. The racket was enough to make us close all the windows and run the air conditioner.

Through that, the system was maintaining Float @ 53.1V until quitting time at 4PM. SoC 97%.

That's pretty good for us.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Wed Jun 02, 2021 9:24 am

raysun wrote: ↑
Tue Jun 01, 2021 8:44 pm
A busy day.
That's got to feel good to work the system really hard with no hiccups. I have two portable planers and while I don't run them at the same time, with even one I fire up the welder/gen to plane boards - which I don't do to often as I like the rough cut.

Anyway, on my system with regard to the tuning, I am finishing the solar day at ~90% with float set at 53.0. I'm going to let a few more days pass to get a better average but its looking that I may bump the float up an 'notch.' This time of the year the system is charged and going to float well before noon so the SOC has quite a while to stair step down before evening comes on.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Wed Jun 02, 2021 9:47 am

Its funny. In the past, my first reaction would be to keep a close eye on the battery, and on the inverter peak output.

Now, my first reaction was how to deal with the noise. (Add another power-hungry device to the mix.)

I gave away some gas the other day because it had been sitting around longer than I care to store it. There's folks around who, through no fault of their own, chronically have more month than money. The modern "gas cans" are useless when it comes to fueling vehicles. My generator sits idle far more than before. Instead of buying 25 gallons on a Costco run, these days I'm down to buying 10.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Wed Jun 02, 2021 10:00 am

raysun wrote: ↑
Wed Jun 02, 2021 9:47 am
I gave away some gas the other day because it had been sitting around longer than I care to store it.
Can you not find non-ethanol gasoline? With all the boating around there has to be ethanol free fuel. You will end the aging issue for a good part of a year. This probably deserves its own thread but there are many other forums that cover small engines and ethanol mix fuel.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Wed Jun 02, 2021 10:36 am

I only use E-free gas in my generator. TBH, I just wanted my stored fuel reduced to 10 gallons.

It makes more room for hoarding toilet paper for the next pandemic.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Wed Jun 02, 2021 1:29 pm

raysun wrote: ↑
Wed Jun 02, 2021 10:36 am
I only use E-free gas in my generator. TBH, I just wanted my stored fuel reduced to 10 gallons.

It makes more room for hoarding toilet paper for the next pandemic.
Don't you have sugar cane, banana, coconut and avocado leaves? BTW, I don't think you should flush them.

If worst came to worst we would fire up the poddy tree stool. Maybe you should have one. Every morning EVERYTHING was cleaned out.

Its the closest way we have of getting even with wire harness eating critters. Mary's pickup is in the shop now. The Ford dealer may get a wiring harness before the end of July.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Wed Jun 02, 2021 4:05 pm

Screenshot_20210602-125807_Chrome.jpg
We have 'Ilima so all good.

6.15kW coming off 12 panels rated at 5.28kW. Glad I set up lots of shaded work areas or I'd be coming home to deep-fried carpenter.

I guess I should hook up the other 4 panels and see if I can hit 8kW.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Fri Jun 04, 2021 11:32 am

So the carpenters and painter were happily burning electrons all day. Consumption went from our usual 12kWH to 29kWH. It was part sun, part clouds so the battery SoC never got above 73% and at 5PM was 68%. The old "better run the generator" impulse kicked in, but I thought "yo no necesitar".

This morning the battery is at 31%. Pretty much as low as it ever gets. It's recharging now and is at 37%.

It will be interesting to see how conditions unfold today.

User avatar
sodamo
Forum Emperor
Posts: 1511
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians 2 GG8048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
EG4 Chargeverter
10Kw MEP 803a Military gen

Honda EU7000i
Starlink w Eero Pro 6e network
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: Guess the SoC prediction game

Post by sodamo » Fri Jun 04, 2021 1:46 pm

Great story Ray. Old habits I guess, but at 31% I watch the volts a bit more to steady my itchy finger.
David

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Fri Jun 04, 2021 2:25 pm

sodamo wrote: ↑
Fri Jun 04, 2021 1:46 pm
Great story Ray. Old habits I guess, but at 31% I watch the volts a bit more to steady my itchy finger.
True that. The battery was at 52.1 @ 31% so figured it was OK.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Fri Jun 04, 2021 4:54 pm

sodamo wrote: ↑
Fri Jun 04, 2021 1:46 pm
Great story Ray. Old habits I guess, but at 31% I watch the volts a bit more to steady my itchy finger.
53.1

Gosh, that number just won't go away. Amps in, amps out and the same the next morning or almost the same.
Still 53.1 or, gasp 53.0. Then recently with two ceiling fans on we have hit 52.7.

This is a whole new game. I watch the PHIs closely. Other than the watchfulness there's nothing to do but to watch for 53.1. People may think we're nuts but it is really the inverse.

To me, however you have to swing it, if your FLA batteries are at end of life, you really have to cash in your pop cans and get the lithiums.

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Fri Jun 04, 2021 5:12 pm

To me, however you have to swing it, if your FLA batteries are at end of life, you really have to cash in your pop cans and get the lithiums.
Let's not lose sight of the fact Phi specs the nominal voltage at 51.2V.

Yes, if one wasn't digging in the couch for loose change and collecting cans off the side of the highway before switching to lithium, its likely one will after.

To quote Ferris Bueller: "It is so choice. If you have the means, I highly recommend picking one up."

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Guess the SoC prediction game

Post by raysun » Fri Jun 04, 2021 5:56 pm

20210604_145329.jpg
I really like how easily this battery charges, and for the first time since I put it in, getting to see how much charge the PV panels might collect after 11:30AM.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Guess the SoC prediction game

Post by JRHill » Tue Jun 08, 2021 1:32 pm

As unusual as it seems for the season we are in a 3rd day of overcast - and actually some sprinkles. And not this:

https://www.youtube.com/watch?v=vDAg3VkZPg8

But with the repressed solar the system is not hitting CPM until hours later. The PHIs end later in the afternoon and are much better the next morning. It is what it is....