raysun wrote: ↑Sat May 29, 2021 1:13 pm
SimpliPhi (like pretty much every LiFePO4 vendor) specifies against Float and then specifies a "full on" Float voltage for the charge controller (and none for generator/grid.) Part of the reason for the apparent disparity is the FlexMax controllers automatically enter Float after Bulk/Absorb completes and remain in Float until the sun goes down, or a REBULK event.
If one chooses, its pretty easy to defeat Float (for the most part) by setting Float Voltage as low as possible, however, IME its not necessary or even desirable, as it wastes even more PV generation. (I am a life member of the Save the Photons Society. We have a spokesmodel and everything. Its really quite a deal.)
For my part, keeping the battery from the ravages of Float, while maximizing PV harvest, is the reason I experimented with the Float Voltage to find that "sweet spot". For my typical loads, Float=53.1V is perfect. As soon as the charge terminates at 56.4V, the charge controllers go Silent, and remain so until the Float Voltage is reached. That interval drains about 4-5AH off the battery, or about 1%. Holding Float at 53.1V typically drains 0.1A from the battery, though heavy loads may drain more. At no time does Float add net charge, unless the battery drops below Float Voltage. Float never returns the battery to 100% SoC, and at the end of Float, the battery typically sits at 96% SoC, though it may be as high as 98% on a very low load day.
The battery enters the end of daylight having been at 100% SoC for all of 60 seconds, and then gently discharges until nightfall.
You may wish to use a lower Float voltage, as your system is typically more lightly loaded than mine. Try 53.0V. The key for me is there is always a small discharge after 100% SoC.
Morning low voltage of 53V is pretty much in the ideal range. You are fretting over nothing.
Lowering CRA to 6A is going to be the Phi specified 2% end amps target for a 300AH battery.
Setting the Charge Controller End Amps to other than 0 is not useful on normal operation. Setting Charged Return Amps on the FNDC properly is quite useful.
My CRA target is 9A. I found, however, that starting the 1 Minute Charged Time countdown at 9A actually let the charging amperage go to 0A (BMS cutoff activated, I suspect.) I experimented with CRA, and actually have it set to 23A. At the end of 60 seconds, the charge current hits 9A as charging terminates. This little "sleight of hand" would likely have a different value for a 300AH battery.
REBULK is the last piece of the puzzle. The FM charge controllers wake up every day and automatically start a Bulk charge. REBULK does modify the Absorb Time setting (0.1H in my case), but it doesn't appear to have an impact. For some reason, my FMs have REBULK set to 51.2V, a voltage my battery rarely, if ever, reaches. In theory, Absorb Time would be decremented by the REBULK algorithm to the minimum allowed, but since Absorb Time is already at the minimum allowed, it seems to have no effect.