H2 detector and AGM batteries

Discussion about the OutBack Energy Cell Batteries
Post Reply
User avatar
EA6LE-ONE
Forum Czar
Posts: 952
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

H2 detector and AGM batteries

Post by EA6LE-ONE » Mon Apr 12, 2021 4:45 am

Under normal circumstances AGM batteries should not generate hydrogen. I thought my batteries are operating normally without problem. always watching the charge and discharge voltage. comparing the SOC to voltage and checking the general AGM battery voltage to SOC table and always coming above the chart. also checking the temperature which lately is between 72F and 80F.
Recently I ordered "RIDGID 36163 Model micro CD-100 Combustible Gas Detector, Gas Leak Detector" to see if there is any hydrogen in my battery room. and it did detect something with 160ppm concentration. The only logical explanation was hydrogen gas.
I purchased a proper hydrogen gas detector and this one was reporting about 200ppm hydrogen. I vented the room a bit until it went down to 70. next day I checked the ppm before batteries are starting to charge and was about 50. when i came home after the charge cycle was finished the value when about 150ppm. so there was hydrogen gas generated which suggest that there is overcharge event. this weekend I started to check the voltage on each battery while charging. I did found one that was 2.66V which is a difference for about 0.3V more than absorb charge per cell of 2.32V. when the batteries were new during freshening charge the values I seen were between 2.25 and 2.45. while resting the difference between cells was about 0.02V which was in the recommended parameters.
This morning when the batteries were down to 84% SOC and a constant draw of power I started to check the batteries and the surprise is that the battery that was at 2.66V is voltage was in the middle of the pack. 2.098V. the other batteries were between 2.085V and 2.113V which suggest a difference of 0.03V between the cells which is still in normal parameter.
I did reduced my absorb voltage on my system yesterday and from 55.6V to 55V and that brought the battery down to 2.34V and the rest stayed around the voltage before the reduction. The general documentation of AGM batteries suggest that AGM cells will start gassing at 2.35V. So might be a good idea to inspect your batteries if you have 2V cells and try to see if they are lower than 2.35V during the absorb cycle and eventually adjust the absorb voltage down until you have 2.35V maximum on any cell.
for 6V or 12V batteries will not be possible to check the voltage on individual cell and probably the best bet is to get a hydrogen detector and see if any is generated. if hydrogen is detected during a normal charging cycle then dial down the absorb voltage and check again next day. The goal should be no hydrogen generation during charging cycle.

this is just an opinion based on my experience with my batteries. I will keep an eye on my batteries and when I will have some bad weather will let the batteries go down to 50-60% SOC and check them at that time as well. meantime I will check them every weeked from now on. also I will check the hydrogen detector every afternoon. will report more when new info will be available.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: H2 detector and AGM batteries

Post by raysun » Mon Apr 12, 2021 9:43 am

That's a neat piece of detective work.

In the aspect of overcharge and venting, VRLAs are harder to maintain than flooded batteries as the latter provide a recovery mechanism of sorts - add lost water - while in VRLA cells water loss is permanent.

The 6V / 12V monoblocks, as you observe, further obfuscate cell overvoltage because the cells' voltages can't be directly measured.

I believe you have hit upon a tool that everyone with a sizeable VRLA bank should consider installing.

User avatar
EA6LE-ONE
Forum Czar
Posts: 952
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: H2 detector and AGM batteries

Post by EA6LE-ONE » Tue Apr 13, 2021 6:44 am

It seems that you can decrease the absorb voltage and and also decrease the return amps to reach the same SOC for the battery with the higher voltage and higher return amps. the only down side is that will take a bit longer to reach float. in my case is like 20-30 min. but there was no more hydrogen created. I do think that a hydrogen detector is worth it if you have an expensive battery.
if you want to try do this: check the return amps once you reach float and the next day reduce the voltage by 0.4V and reduce the return amps by 10%. check again the return amps once reach float if is matching with the previous value, if is higher then reduce more the return amps until the reading is matching or close. might need to be sure that you have at least 2 hours of float remaining, or how much is advised by the manufacturer, if is more the better.

raysun
Forum Overlord
Posts: 13666
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: H2 detector and AGM batteries

Post by raysun » Tue Apr 13, 2021 10:05 am

When I was using a VRLA battery, I did something similar, but used temperature as the control. Hydrogen emission would have been a better metric, but it didn't occur to me to get a detector.

User avatar
EA6LE-ONE
Forum Czar
Posts: 952
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: H2 detector and AGM batteries

Post by EA6LE-ONE » Wed Apr 14, 2021 5:52 am

raysun wrote: ↑
Tue Apr 13, 2021 10:05 am
When I was using a VRLA battery, I did something similar, but used temperature as the control. Hydrogen emission would have been a better metric, but it didn't occur to me to get a detector.
I did used the logic that if a battery is overcharging should put more heat out and I was using from time to time a thermal camera on my iPhone to check for difference in temperature between the batteries. there was none and yet some do overcharge.
Last time I checked there was about 20ppm hydrogen difference from the morning reading, it went down for about 5 times. good sign. now I reduced a bit more the voltage and see the reading later today. if no hydrogen and the discharge curve is close to the days before then should be ok.
I whish that we could find a programable charger that can do 2.32V or even 2.35V with variable current to charge each cell performing a individual equalization. I would need something capable to reach 20A minimum. I did used on 2 of my old batteries (sun xtender 2V) a programmable charger for lithium batteries that I set at 5V and 5A charging.

User avatar
EA6LE-ONE
Forum Czar
Posts: 952
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: H2 detector and AGM batteries

Post by EA6LE-ONE » Wed May 05, 2021 5:12 am

just got one of this: https://doug-gilbert.github.io/rd60xx-u ... isoft.html

I assembled it yesterday and test it on a RBC2 battery and works perfectly. I can set any voltage between 0V to 60V and current from 0A to18A. it will hold the voltage and will decrease the current like a charge controller. Now I will have to digest the documentation to see if it can be programmed to terminate charge according to current.

regardless if can terminate or not the charge like a CC is still a better solution to charge 2V AGM batteries in attempt to do an equalization without overcharging some cells.

this weekend I will use it on the cells that have the lowest voltage when they reach absorb. this task might take a while. I will post here the results in time.

Also I was thinking if there is possibility to create a new king of BMS for acid batteries. Like each 2V cell to have one connected that will follow the voltage and once it reach 2.35V(or the highest voltage before overcharge event) and apply a load or bypass to keep it at that voltage and give a chance for other cells to catch up. This might work to have a AGM battery to last as long as the lithium. Any ideas if is possible?

provo
Forum Emperor
Posts: 1464
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: H2 detector and AGM batteries

Post by provo » Wed May 05, 2021 5:59 am

EA6LE-ONE wrote: ↑
Wed May 05, 2021 5:12 am

Also I was thinking if there is possibility to create a new kind of BMS for acid batteries. Like each 2V cell to have one connected that will follow the voltage and once it reach 2.35V(or the highest voltage before overcharge event) and apply a load or bypass to keep it at that voltage and give a chance for other cells to catch up.
Like the old (ancient) Rudman Regulator:

http://www.manzanitamicro.com/old/parts.htm

Screen Shot 2021-05-05 at 5.48.15 AM.png

But these were for 12V batteries or 2 x 6V in series. I had 10 of them, one on each Optima in the Honda Civic I converted to electric in 1999 :grin: ... Big old heater with 10 huge wire-wound resistors to dissipate the power.

Hard to do one per 2V cell, though, even if you were willing to build a 2V version.

User avatar
EA6LE-ONE
Forum Czar
Posts: 952
Joined: Tue May 05, 2020 7:51 am
My RE system: System 1:
MATE3s, 3 x Radian GS8048A,
6 x FLEXmax 100, HUB10,
24 x SimpliPhi 48V,
1 x FLEXnet DC, 6 x FLEXware ICS Plus,
78 x PANASONIC VBHN325SA17 325W

System 2:
MATE3s, Radian GS8048A,
2 x FLEXmax 100, HUB10
15 x SimpliPhi 48V,
1 x FLEXnet DC, 2 x FLEXware ICS
21 x PANASONIC VBHN325SA17 325W
Location: Providenciales, Turks & Caicos Isl.

Re: H2 detector and AGM batteries

Post by EA6LE-ONE » Tue May 18, 2021 3:29 pm

So I used the buck charger to charge the lowest batteries and the results are promising, those batteries are now in the middle of the pack. The strange thing about the batteries is that they do fluctuate, some reaching very high values at times and then later getting to a lower value with other reaching higher values. there will be few that will keep lower and those are the ones I mark to charge them next weekend.
I got a second charger and will be easier to equalize more batteries. Luckily the system with one battery is not showing a significant difference between cells so I concentrate more on the system with the 2 batteries where I can switch to grid over night keeping the batteries charged and disconnecting one battery string to equalize the lowers ones.
I kept the absorb voltage at 0.4v more than float (54V) on the double battery and it seems to charge and discharge in the same values with the setting at normal absorb value (55.6V) the difference is the lower end amps and it takes longer to reach it. there is still a bit of hydrogen created but is like 15-20 times lower than before. Is now about 10 ppm difference from before charging cycle and after the finish.
Will keep working on this and report back with more info.