Can inverter be powered with 3-phase

Discussion about adding energy storage to grid-dependent inverters using OutBack Power technology
Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Can inverter be powered with 3-phase

Post by Don58 » Thu Mar 11, 2021 11:02 am

Our GS8048A requires split-phase 240Vac, per the manual. I only have 3-phase 240Vac available.

What are the ways to connect this correctly?

Thanks.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Can inverter be powered with 3-phase

Post by JRHill » Thu Mar 11, 2021 11:32 am

Don58 wrote: ↑
Thu Mar 11, 2021 11:02 am
Our GS8048A requires split-phase 240Vac, per the manual. I only have 3-phase 240Vac available.

What are the ways to connect this correctly?

Thanks.
You have an electrical engineer you trust? This isn't really unusual. But how did you get to this point?

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Thu Mar 11, 2021 11:56 am

I'm not familiar with electrical distribution, mostly a solar guy (and computers in the old days). So I have to ask basic questions. I accept that they might not be smart questions.

Can the Outback inverter, which specifies split-phase AC, tolerate the legs being 120° out of phase rather than 180°? If so I could use two of the three legs. That would be an unbalanced configuration but maybe it doesn't matter.

I don't know the topology of the facility's input 240Vac (wye, delta, high-leg delta etc) but should be able to find out. It'll be whatever 3-phase is typical of a utility feeding a commercial site.

Greg T Fordan

Re: Can inverter be powered with 3-phase

Post by Greg T Fordan » Thu Mar 11, 2021 1:24 pm

Don58 wrote: ↑
Thu Mar 11, 2021 11:02 am
Our GS8048A requires split-phase 240Vac, per the manual. I only have 3-phase 240Vac available.

What are the ways to connect this correctly?

Thanks.
Is the line to line voltage of your three phase source 240VAC, and does it have a fourth line N (center tap)?

GS8048A needs a neutral connection. If your 3-phase source has a neutral point (center tap) and the Line to Neutral voltage of approximately 138VAC you might be in luck.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Thu Mar 11, 2021 2:36 pm

There are isolation transformers out there that you can hook to 208 and they will output 230 with a center tap, which will re-create the neutral and give you the added benefit of fully isolating the Outback gear from whatever is also on the incoming feed. The higher the kva, the more $ you will spend.

Larson, Federal Pacific, Canada Transformers and others have various units that would work.

Not cheap, though.

Check with a local electrical engineer for specifics.
Information, you get not; if incorrect question, you ask..

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Thu Mar 11, 2021 3:24 pm

A quick overview of basic three phase systems..

https://electrical-engineering-portal.c ... easurement
(LMK if I should PM stuff like this, but I would hope anyone that is following this thread and is curious about the topic would find the info useful.)

Steve
Information, you get not; if incorrect question, you ask..

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Can inverter be powered with 3-phase

Post by JRHill » Thu Mar 11, 2021 4:25 pm

sbrownian wrote: ↑
Thu Mar 11, 2021 3:24 pm
A quick overview of basic three phase systems..

https://electrical-engineering-portal.c ... easurement
(LMK if I should PM stuff like this, but I would hope anyone that is following this thread and is curious about the topic would find the info useful.)

Steve
Steve, this is a really cool link.

wolfridge
Forum Member
Posts: 23
Joined: Mon Nov 05, 2018 10:27 am
My RE system: Manson Creek B.C.
36 Hanwha 300watt panels
2-FM100
Radian GS8048A
OUTBACK Load Center GSLC 175-PV-120/240
Outback FN-DC Flexnet
Mate3s
Sacred Sun 48 Volt 500 Ahr Carbon Battery Bank
Perkins 10kw and two Kubota 8kw
Way Off Grid
Location: Manson Creek B.C.

Re: Can inverter be powered with 3-phase

Post by wolfridge » Fri Mar 12, 2021 8:51 am

Don58
I unknowingly did this with my GS8048a. My generator was three phase but wired to put out two or split phase 240v. It was also labeled as a single phase generator. The GS8048a did not function well from the beginning as it could not match 120 degree split. It failed next day but support reset it over internet. Then it failed again. This time the main board on the GS8048 had to be replaced. I replaced that generator with a proper split or single phase 240v with no more problems.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Fri Mar 12, 2021 8:58 am

wolfridge wrote: ↑
Fri Mar 12, 2021 8:51 am
Don58
I unknowingly did this with my GS8048a. My generator was three phase but wired to put out two or split phase 240v. It was also labeled as a single phase generator. The GS8048a did not function well from the beginning as it could not match 120 degree split. It failed next day but support reset it over internet. Then it failed again. This time the main board on the GS8048 had to be replaced. I replaced that generator with a proper split or single phase 240v with no more problems.
If a single phase isolation transformer with a center tapped secondary is installed between the three phase source and the Outback, it will 'recreate' the proper 180 phase angle between the two 'hot' legs and the 'new' neutral, as well as kick up the 208v to 230v.
Information, you get not; if incorrect question, you ask..

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Mon Mar 15, 2021 5:29 pm

Greg T Fordan wrote: ↑
Thu Mar 11, 2021 1:24 pm
Is the line to line voltage of your three phase source 240VAC, and does it have a fourth line N (center tap)?

GS8048A needs a neutral connection. If your 3-phase source has a neutral point (center tap) and the Line to Neutral voltage of approximately 138VAC you might be in luck.
By investigating the panel I've determined we have a three-phase four-wire Wye. Only two of the three phases are distributed into the facility. The voltages read as expected.

L1 , L2 : 208Vac
L1 , N : 120Vac
L2 , N : 120Vac

How does a 138Vac Line to Neutral help if the unit requires the lines be 180deg apart? Or is 120deg okay so long as you have a high enough line to neutral voltage?

Another reply said the inverter "could not match 120 degree split," but you seem to imply that's not the issue.

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Mon Mar 15, 2021 5:32 pm

sbrownian wrote: ↑
Thu Mar 11, 2021 2:36 pm
There are isolation transformers out there that you can hook to 208 and they will output 230 with a center tap, which will re-create the neutral and give you the added benefit of fully isolating the Outback gear from whatever is also on the incoming feed. The higher the kva, the more $ you will spend.
Isn't that 208 across two legs that have a 120deg phase difference? Does this mean it will work with a 120deg phase difference so long as the resulting voltage is high enough? The transformer can't correct for phase unless I'm missing some fundamental.

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: Can inverter be powered with 3-phase

Post by JRHill » Mon Mar 15, 2021 7:13 pm

Does the GS8048 pass the 240 through when connected to an AC source while charging? This whole conversation makes me nervous.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Tue Mar 16, 2021 12:10 am

Don58 wrote: ↑
Mon Mar 15, 2021 5:32 pm
sbrownian wrote: ↑
Thu Mar 11, 2021 2:36 pm
There are isolation transformers out there that you can hook to 208 and they will output 230 with a center tap, which will re-create the neutral and give you the added benefit of fully isolating the Outback gear from whatever is also on the incoming feed. The higher the kva, the more $ you will spend.
Isn't that 208 across two legs that have a 120deg phase difference? Does this mean it will work with a 120deg phase difference so long as the resulting voltage is high enough? The transformer can't correct for phase unless I'm missing some fundamental.
It doesn't correct for phase differences, it creates an entirely "new" isolated sinewave.

Think of it as one primary winding across two phases. With no reference to neutral or another phase, all the primary winding "sees" is the differential voltage impressed upon it from the two phases. Remember, NO reference to neutral, or the other "leg." The voltage "change" is happening at a 60hz rate.

That voltage is magnetically coupled to two secondary isolated windings, (or one center tapped winding,) that has more turns than the primary, giving the voltage a "boost" (and reducing the available current.)

If left isolated, you now have two 120v outputs on the secondary.

If you connect the "negative" of one winding to the "positive" of the other, you have created a new "neutral" at that junction, and you will measure 240v from the "positive" of one winding to the "negative" of the other. (Look up transformer "phasing.")

Like the primary, the secondary winding has NO direct connection to the [Edit: rest of the] three phase system, and no "reference" to measure to.

By nature, a single winding is a 180 degree device..

You only get 120 degrees when you actually have an alternator that has three separate windings staggered correctly on the stator, and the proper magnetic field to excite it with. (Yeah, I know, there are all kinds of tricks with multiple transformer windings in LARGE rectifier stacks to produce 6 to 12 phase stuff for things like 10s of megawatt cruise ship drives and phase shift tricks with electronics, etc.)
Last edited by sbrownian on Tue Mar 16, 2021 9:15 am, edited 1 time in total.
Information, you get not; if incorrect question, you ask..

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Tue Mar 16, 2021 8:19 am

Found a screen shot of a wiring diagram of a 208 to 240 split phase transformer.

Hope this helps to clarify...
Attachments
3_phase_208_240_buck_boost_transformer_wiring_diagram_6.jpg
Information, you get not; if incorrect question, you ask..

Greg T Fordan

Re: Can inverter be powered with 3-phase

Post by Greg T Fordan » Tue Mar 16, 2021 8:52 am

Don58 wrote: ↑
Mon Mar 15, 2021 5:29 pm
By investigating the panel I've determined we have a three-phase four-wire Wye. Only two of the three phases are distributed into the facility. The voltages read as expected.

L1 , L2 : 208Vac
L1 , N : 120Vac
L2 , N : 120Vac

How does a 138Vac Line to Neutral help if the unit requires the lines be 180deg apart? Or is 120deg okay so long as you have a high enough line to neutral voltage?

Another reply said the inverter "could not match 120 degree split," but you seem to imply that's not the issue.
Your L1-L2 voltage is only 208.
It will NOT be accepted by GS8048A inverter

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Tue Mar 16, 2021 11:14 am

Greg T Fordan wrote: ↑
Tue Mar 16, 2021 8:52 am
Your L1-L2 voltage is only 208.
It will NOT be accepted by GS8048A inverter
What might symptoms be of doing so? Eventual overcurrent damage? Could it severely imbalance the source if the draw is high enough? Just curious. Thank you.

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Tue Mar 16, 2021 11:18 am

sbrownian wrote: ↑
Tue Mar 16, 2021 12:10 am

It doesn't correct for phase differences etc...
Thanks very much. This clarifies the situation. It seems if anyone finds they have a three-phase source and it cannot meet the needs of a GSx048A inverter then they need a transformer as you describe. This is important to me because our clientele doesn't necessarily have split-phases 240Vac available. These days there are more and more non-residential implementations. It might be that Outback has products in anticipation of this market, but in my particular case it's too late to switch out the core component. Besides, the client selected it.

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Tue Mar 16, 2021 11:27 am

sbrownian wrote: ↑
Tue Mar 16, 2021 8:19 am
Found a screen shot of a wiring diagram of a 208 to 240 split phase transformer.

Hope this helps to clarify...
Perfect! A good diagram is alway easier to understand. :-)

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Tue Mar 16, 2021 12:20 pm

Greg T Fordan wrote: ↑
Tue Mar 16, 2021 8:52 am
Your L1-L2 voltage is only 208.
It will NOT be accepted by GS8048A inverter
The spec says
AC Input Voltage Range: (L1 or L2) 85 to 140 Vac
Grid-Interactive Voltage Range (default): (L1 or L2) 106 to 132 Vac

I don't understand how 208 is too low. (I actually read 212, just thought providing the nominal was better for the discussion.)

Thank you.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Tue Mar 16, 2021 12:37 pm

Don58 wrote: ↑
Tue Mar 16, 2021 11:27 am
sbrownian wrote: ↑
Tue Mar 16, 2021 8:19 am
Found a screen shot of a wiring diagram of a 208 to 240 split phase transformer.

Hope this helps to clarify...
Perfect! A good diagram is alway easier to understand. :-)
Just to reiterate, you still need a proper GROUND, and for isolation purposes, you do not carry the neutral over from the 3 phase side of the house...
Information, you get not; if incorrect question, you ask..

Brian_B
Forum Member
Posts: 23
Joined: Fri Jan 29, 2021 8:33 am
My RE system: Skybox
3.25kW Canadian Solar
40kWh Samsung SDI
Predator 8.25kW Gas Backup

Re: Can inverter be powered with 3-phase

Post by Brian_B » Tue Apr 20, 2021 9:37 am

From the peanut gallery, and maybe a bit late to this conversation:

The 1p240AC you get from the Utility will be 120 deg out as well between phases - they distribute 3 phase, and just drop you two legs of the three for common residential service (through a step-down, usually out mounted on the nearest pole). You only get 180 deg on your 120V legs, between Hot and Neutral - since they are with reference to Neutral, which is usually bonded to ground.

The 8048A should work fine hooked up to just 2 of the 3 phases, even at 208VAC. You may need to adjust voltage protection some, and if you have a 3p generator or something on the other end you should be concerned about phase imbalancing (as you will be loading the 3 phases unequally - not a real concern if your just grid connected). According to the 8048A spec sheet, it's fully adjustable from 200 to 260VAC.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Tue Apr 20, 2021 10:08 am

Most, (not all,) distribution systems put out three phase on the distribution 'high side,' and tie the "average household" type transformer to one phase and the neutral line. Three phase is a different animal all together..

(7kv transformers are cheaper than 13 - 14kv transformers.)


It will STILL be 120 degrees though, since you are bringing in the NEUTRAL from the three-phase.

As has been indicated elsewhere on here, (Outback engineering,) the 8048 will probably NOT like it, ergo, the requirement to run it through an isolation transformer..
Information, you get not; if incorrect question, you ask..

Don58
Forum Expert
Posts: 67
Joined: Thu Jun 20, 2019 1:31 pm
My RE system: Radian system. GS8048A Inverter, GSLC, 2x FM80. Battery = 48VDC 700Ah Iron Edison LiFePo4 (lithium iron phosphate).

Re: Can inverter be powered with 3-phase

Post by Don58 » Thu Apr 29, 2021 1:45 pm

There seem to me to be contradictions. Outback told me straight out that the way we had it, two legs of a three-phase source, will not work. Yet it is intended to run on household 240Vac, which if as described above is two legs of a three-phase source.

When we ran on three-phase at the shop, the inverter / charger got very hot while charging the big battery. When on single-phase 240Vac at a house, it did not. I've wondered how a 120 degree phase difference could matter but I never found out.

I admit we did not acquire and hook up a scope to these AC sources to make certain. That seemed a little out of scope, as it were.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: Can inverter be powered with 3-phase

Post by sbrownian » Thu Apr 29, 2021 2:00 pm

Did you forget about, say, the >60< degree total TIMING differential?

Do you run your car with the spark timing off by 60 degrees?

I'd say getting HOT was a major clue.....

To NOT do that..


I would hazard a guess it has to do with phase angle timing / zero cross detection.
Information, you get not; if incorrect question, you ask..

provo
Forum Emperor
Posts: 1464
Joined: Thu Jul 27, 2006 4:34 pm
My RE system: 16 Evergreen EC-120 (4 strings, total 1920W)
2 SimpliPhi 3.8-m-24V (150Ah each)
One FM80
One VFXR3524A
Hub 10
Mate3s
FNDC
Honda EU3000is generator
Grid connection, no selling back
Location: Sierra foothills

Re: Can inverter be powered with 3-phase

Post by provo » Thu Apr 29, 2021 2:13 pm

Don58 wrote: ↑
Thu Apr 29, 2021 1:45 pm

There seem to me to be contradictions. Outback told me straight out that the way we had it, two legs of a three-phase source, will not work. Yet it is intended to run on household 240Vac, which if as described above is two legs of a three-phase source.
In my rural part of Calif, the neighbors and I have 2 of the 3 phases coming to the utility transformer on the pole. Say we have A and B. A few miles one way they have A and C, a few miles the other way they have B and C. The voltage on the 3 phases is whatever provides 240VAC across any 2 phases given the 120° shift and the step-down factor of the transformer. (I used to know the formula -- you can look it up.)

The 120° shift is transparent to the user. You end up with 240VAC 60Hz, and that's all that matters. The neutral comes from the transformer on the pole.

Post Reply