AGS with primary/secondary generators

Post by drstrip » Thu Dec 17, 2020 9:25 am

Can AGS on an original Mate be programmed to control two generators, falling back to the secondary if the primary fails to start?

User avatar
sodamo
Forum Emperor
Posts: 1511
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians 2 GG8048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
EG4 Chargeverter
10Kw MEP 803a Military gen

Honda EU7000i
Starlink w Eero Pro 6e network
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: AGS with primary/secondary generators

Post by sodamo » Thu Dec 17, 2020 9:33 am

I don’t think so, nor can the Mate3s. But if it can I hope someone details how.

I have 2 gens and the only way I found was a manual transfer switch both for the power output and the Aux signal.
David

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: AGS with primary/secondary generators

Post by sbrownian » Thu Dec 17, 2020 10:01 am

It would be pretty easy to build something if you had either an automatic transfer switch, or a manual one that could be switched with an external signal.

Add in a small PLC, a few lines of ladder logic code, and -poof-!
Information, you get not; if incorrect question, you ask..

User avatar
sodamo
Forum Emperor
Posts: 1511
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Adding 12 Hyundai 365 (4380) 18460w total
Radians 2 GG8048A w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
15 SimpliPhi 3.8 (57kw) (1125 AH)
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
EG4 Chargeverter
10Kw MEP 803a Military gen

Honda EU7000i
Starlink w Eero Pro 6e network
Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: AGS with primary/secondary generators

Post by sodamo » Thu Dec 17, 2020 11:00 am

sbrownian wrote: ↑
Thu Dec 17, 2020 10:01 am
It would be pretty easy to build something if you had either an automatic transfer switch, or a manual one that could be switched with an external signal.

Add in a small PLC, a few lines of ladder logic code, and -poof-!
Easy you 😁😁😁😁
David

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: AGS with primary/secondary generators

Post by sbrownian » Thu Dec 17, 2020 11:50 am

Could be done with discrete relay logic, but a PLC is soooo much nicer..

Don't like the way it works? Adding more stuff? Want to control a vent fan based on temperature and or if the generator is running?

Modify the timers, add / remove logic and plug in different I/O modules plus a few presses of some keys...

Some of the PLCs I've worked with are actually quite inexpensive (under $200) and are very versatile.

Once you learn some basic ladder logic stuff, and work out how to run the software, it is pretty easy.

Really!

Lots of online resources for teaching yourself ladder logic / PLC setups.

And some software allows 'logic block' type programming along with stuff that looks like you're writing code, but I pretty much stick to ladder logic.
Information, you get not; if incorrect question, you ask..

drstrip
Forum Guru
Posts: 201
Joined: Mon Jan 08, 2007 12:32 pm
My RE system: 32 x 400W Q-cell panels on Nuance Osprey fixed tilt ground mount
Sol-Ark 12K inverter/MPPT chargers
4 x 200Ah 48V Meritsun LiFePO4 batteries
Kohler 15RYG + Kohler 14RCA backup plumbed to natural gas + 1000gal propane tank.
Location: New Mexico - The land of enchantment and 76% of possible sunshine

Re: AGS with primary/secondary generators

Post by drstrip » Thu Dec 17, 2020 12:08 pm

sbrownian wrote: ↑
Thu Dec 17, 2020 10:01 am
It would be pretty easy to build something if you had either an automatic transfer switch, or a manual one that could be switched with an external signal.

Add in a small PLC, a few lines of ladder logic code, and -poof-!
A $2 Arduino, relays compatible with the generator remote-start circuit, and a couple of lines of C++ would do the job for a whole lot less money.
The bigger issue is detecting that the primary generator has failed.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: AGS with primary/secondary generators

Post by sbrownian » Thu Dec 17, 2020 12:54 pm

drstrip wrote: ↑
Thu Dec 17, 2020 12:08 pm
sbrownian wrote: ↑
Thu Dec 17, 2020 10:01 am
It would be pretty easy to build something if you had either an automatic transfer switch, or a manual one that could be switched with an external signal.

Add in a small PLC, a few lines of ladder logic code, and -poof-!
A $2 Arduino, relays compatible with the generator remote-start circuit, and a couple of lines of C++ would do the job for a whole lot less money.
The bigger issue is detecting that the primary generator has failed.
Yep.

Could do that too.

I'm thinking of a 'put the building blocks together' solution that a person with no programming or breadboarding experience could probably learn to do in under a week.

I used to mess with C on the Amiga 1000 platform, but I've completely forgotten it in the intervening 30 some odd years. :shock:

I've found that most people pick up pretty quickly on ladder logic once the basics are explained and they try their hand at writing a few simple rungs of code.

Stuff like read this switch, turn on that light type stuff. I've not looked into what is available in the way of simplified programming for the Arduino, but putting one together to run something like this requires a bit of knowledge of proper methods of I/O isolation, power supplies, etc.

The PLC I'm thinking of has a variety of I/O modules that just 'plug in' and are all properly designed with the aforementioned concerns in mind.

Maybe when I retire I'll have time to mess with things like that Arduino thingy! :mrgreen:
Information, you get not; if incorrect question, you ask..

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: AGS with primary/secondary generators

Post by raysun » Thu Dec 17, 2020 1:09 pm

sbrownian wrote: ↑
Thu Dec 17, 2020 10:01 am
It would be pretty easy to build something if you had either an automatic transfer switch, or a manual one that could be switched with an external signal.

Add in a small PLC, a few lines of ladder logic code, and -poof-!
Is that -poof-! accompanied by the smell of smoke?

🀣🀣

drstrip
Forum Guru
Posts: 201
Joined: Mon Jan 08, 2007 12:32 pm
My RE system: 32 x 400W Q-cell panels on Nuance Osprey fixed tilt ground mount
Sol-Ark 12K inverter/MPPT chargers
4 x 200Ah 48V Meritsun LiFePO4 batteries
Kohler 15RYG + Kohler 14RCA backup plumbed to natural gas + 1000gal propane tank.
Location: New Mexico - The land of enchantment and 76% of possible sunshine

Re: AGS with primary/secondary generators

Post by drstrip » Thu Dec 17, 2020 1:18 pm

raysun wrote: ↑
Thu Dec 17, 2020 1:09 pm
Is that -poof-! accompanied by the smell of smoke?

🀣🀣
that's referred to as "releasing the magic smoke" in hardware hacking circles. See here.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: AGS with primary/secondary generators

Post by sbrownian » Thu Dec 17, 2020 1:56 pm

drstrip wrote: ↑
Thu Dec 17, 2020 1:18 pm
raysun wrote: ↑
Thu Dec 17, 2020 1:09 pm
Is that -poof-! accompanied by the smell of smoke?

🀣🀣
that's referred to as "releasing the magic smoke" in hardware hacking circles. See here.
I've lost count of how many failed boards I've found using my nose... :mrgreen:
Information, you get not; if incorrect question, you ask..

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: AGS with primary/secondary generators

Post by JRHill » Sat Dec 26, 2020 11:32 am

drstrip wrote: ↑
Thu Dec 17, 2020 9:25 am
Can AGS on an original Mate be programmed to control two generators, falling back to the secondary if the primary fails to start?
One of the problems related to the original post is with generators of different sizes. A limitation of the MateX is that while you can set the maximum draw for Gen and Grid (2nd generator) you can not specify different charging rates between Gen and Grid. For example if Gen 1 can charge at the full 20aac with a total of, say 30aac and if Gen 2 can only charge at 12aac with a max of 20aac, you would have to set the charging rate to the lower of both. The only other to way get the max charging for the units is to go into programming each time and change the parameters for charging if using the other generator. This would also apply to any automated failover to a different generator. This is a messy thing unless both generators can handle your charge setting AND your max total amps.

drstrip
Forum Guru
Posts: 201
Joined: Mon Jan 08, 2007 12:32 pm
My RE system: 32 x 400W Q-cell panels on Nuance Osprey fixed tilt ground mount
Sol-Ark 12K inverter/MPPT chargers
4 x 200Ah 48V Meritsun LiFePO4 batteries
Kohler 15RYG + Kohler 14RCA backup plumbed to natural gas + 1000gal propane tank.
Location: New Mexico - The land of enchantment and 76% of possible sunshine

Re: AGS with primary/secondary generators

Post by drstrip » Sat Dec 26, 2020 11:50 am

JRHill wrote: ↑
Sat Dec 26, 2020 11:32 am

One of the problems related to the original post is with generators of different sizes. A limitation of the MateX is that while you can set the maximum draw for Gen and Grid (2nd generator) you can not specify different charging rates between Gen and Grid. For example if Gen 1 can charge at the full 20aac with a total of, say 30aac and if Gen 2 can only charge at 12aac with a max of 20aac, you would have to set the charging rate to the lower of both. The only other to way get the max charging for the units is to go into programming each time and change the parameters for charging if using the other generator. This would also apply to any automated failover to a different generator. This is a messy thing unless both generators can handle your charge setting AND your max total amps.
That's an excellent point that I had not thought about. However, in my case the existing generator is 15kW and the proposed new primary would be 14kW, both of which far exceed the charging draw of my dual VFX3524 inverters, so it's not an issue.

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: AGS with primary/secondary generators

Post by sbrownian » Sat Dec 26, 2020 2:51 pm

:neutral: Same issue with the system I keep an eye on..
The main gen is 7.5kw, (derated to about 6.8 due to altitude, ) but the backup that they bought is a 5kw, with the long term max (over 30 minutes,) as 4.5 kw. I told the owner he'll have to manually enter the max current and the max charger currents if the backup is pressed into service. He doesn't even have the option of using different inputs that are programmed for different capacities, as the electricians set up the gen feeds combining externally, then going into the load center. .. :neutral:
Information, you get not; if incorrect question, you ask..

raysun
Forum Overlord
Posts: 13665
Joined: Tue Jul 26, 2016 5:57 am
My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: AGS with primary/secondary generators

Post by raysun » Sat Dec 26, 2020 2:57 pm

sbrownian wrote: ↑
Sat Dec 26, 2020 2:51 pm
:neutral: Same issue with the system I keep an eye on..
The main gen is 7.5kw, (derated to about 6.8 due to altitude, ) but the backup that they bought is a 5kw, with the long term max (over 30 minutes,) as 4.5 kw. I told the owner he'll have to manually enter the max current and the max charger currents if the backup is pressed into service. He doesn't even have the option of using different inputs that are programmed for different capacities, as the electricians set up the gen feeds combining externally, then going into the load center. .. :neutral:
What inverter is being used?

sbrownian
Forum Czar
Posts: 660
Joined: Mon Nov 30, 2020 9:23 am
My RE system: GS8048 FM80 FNDC Mate3 4 port HUB
4kw solar
7kw Kubota propane gen
Off grid.
Originally installed with 1200 AH of FLA Locomotive batts.
Replaced after 9 years of service with 2 x 300 AH ReLion Lithium packs.
MUCH more efficient!!
Location: Central Washington State

Re: AGS with primary/secondary generators

Post by sbrownian » Sat Dec 26, 2020 3:16 pm

8048..
The original, not the 'A' version.

The irritating thing is they disconnected the internal bus wiring in the load center, so that will have to be reconnected to be able to use the second AC input...

Any rewiring will have to wait until spring, probably when the folks that installed the ReLions come back to add a 5kw array on pole mount, and a second FM80. (FM100? Not sure what is planned.)

The owner has decided to add another Kubota propane gen as well. Outback reccomend a 14kw unit originally, so that is what will probably be purchased. (I hope.)

Gotta wait until the roads clear and the surface water run off to subside a bit for the install of the pole anyway.
Information, you get not; if incorrect question, you ask..

JRHill
Forum Emperor
Posts: 3124
Joined: Thu Feb 17, 2011 11:12 am
My RE system: 48v OB inverter and charge controller, hub and mate3s.
Location: PNW
Contact:

Re: AGS with primary/secondary generators

Post by JRHill » Sat Dec 26, 2020 11:14 pm

Its given that the OB stuff is figured around lead acid batteries. And its known that it is good to draw them heavily from time to time and also to recharge them likewise. Plus the maintenance, etc. So if you have an AC source that can hit the batteries heavily that's usually a good thing. But if you have a smaller backup generator there is a bunch of buttons and wheel spinning.

There should be different charging allowances for GRID or GEN, not just one.