200 Watts at idle?!!!

True Hybrid Energy System
User avatar
Mike Curran
Forum Emperor
Posts: 3602
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: 200 Watts at idle?!!!

Post by Mike Curran » Thu Mar 12, 2020 12:26 pm

I still have the high grid power draw @ idle (no PV input) problem, and had been planning to go "off-grid" and try firing up my genny to see if the high draw is still there.

Voila! Power draw with PV off is down to 130 watts! Next step is to install an isolation transformer between my grid connection and the Skybox. Hoping that solves it, but if not it'll be an expensive experiment. Stay tuned.
Generator operation w no PV.JPG
Edit:. Don't know where I got 130 watts, 440-370= 70 watts. Even better!
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

mhspohr
Forum Guru
Posts: 189
Joined: Sun Jun 30, 2019 8:56 am
My RE system: Skybox "Bristlecone" with 14.3 kWh LiFePO4 (power outage backup)
Skybox "Bristlecone2" with 5 kWh SLA (not currently active since "stacked" operation not working)
6.6 kW SolarWorld/Enphase and 2.6 kW Sunpower/SMA
Skybox "Cottage1" with 14.3 kWh LiFePO4 (power outage backup)4.4 kW REC string (with Tigo Optimizers) into Skybox in Cottage
3.4 kW CSUN string (with Tigo Optimizers) into Skybox in Cottage
Tesla 2022 Model S LR and Tesla 2022 Model Y charged from the sun.

Re: 200 Watts at idle?!!!

Post by mhspohr » Tue Aug 04, 2020 2:15 pm

I thought I'd update this thread with my latest experience.
I finally installed a PV string and turned on the inverter.
The 200 W constant draw (without PV) has gone away. I now get a more reasonable approx 50 W loss from PV to grid during the day and nothing at night. I don't know why but I'm happy with this new situation.
Screenshot from 2020-08-04 14-09-34.png

User avatar
Mike Curran
Forum Emperor
Posts: 3602
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: 200 Watts at idle?!!!

Post by Mike Curran » Tue Aug 04, 2020 3:52 pm

Thanks for your update. It's good to hear your high grid draw has gone away with your addition of PV input.

I've gotten around the problem by setting up Skybox to use time of use rates to run my loads off the battery at night, when there's no PV input. My experience has been similar to yours in that when there's PV input, grid draw is minimal. My overnight loads are minimal so by morning there's still 85% of my battery left in case it's needed for backup, so this has worked fine, although it's obviously not the best solution. If my utility ever actually implements time of use, I expect I won't be able to use it as it was intended, unless something has changed for me as it has for you.

Maybe it's time to try disabling TOU and see if high grid use is still a problem. Stay tuned... - Mike
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

mhspohr
Forum Guru
Posts: 189
Joined: Sun Jun 30, 2019 8:56 am
My RE system: Skybox "Bristlecone" with 14.3 kWh LiFePO4 (power outage backup)
Skybox "Bristlecone2" with 5 kWh SLA (not currently active since "stacked" operation not working)
6.6 kW SolarWorld/Enphase and 2.6 kW Sunpower/SMA
Skybox "Cottage1" with 14.3 kWh LiFePO4 (power outage backup)4.4 kW REC string (with Tigo Optimizers) into Skybox in Cottage
3.4 kW CSUN string (with Tigo Optimizers) into Skybox in Cottage
Tesla 2022 Model S LR and Tesla 2022 Model Y charged from the sun.

Re: 200 Watts at idle?!!!

Post by mhspohr » Wed Nov 04, 2020 2:39 pm

Another update here. As you may recall, I was getting a 200W draw from the grid x 24 hrs until I connected my PV string.
As soon as I connected my PV, the sundown draw went to close to zero. I was happy. :grin:
However, on 27 October I started to get the ~200W draw x 24hrs again. I was not happy. :sad: I hadn't changed anything. PV still connected.
I noticed these entries in the log on the 27th
Screenshot_2020-11-04 OPTICSRE.png
Even after the "recovery" from battery cutout, it continued to draw about 3 kWh/day... 150 to 200 W all day and night. I was still not happy. :sad:
Yesterday I turned off the Skybox. Disconnected everything and had it reboot.
Today I noticed that I did not have the parasitic draw overnight although during the (sun) day the inverter seems to have an overhead draw of 150W to 200W whereas before it was less than 100W.
So, I still don't know what is going on but it is at least tolerable since I don't have the overnight parasitic draw. ](*,)

FrancoV
Forum Junior Member
Posts: 1
Joined: Fri Dec 29, 2023 4:28 pm
My RE system: Non-Skybox Hybrid Inverter 5.5kw/10kw peak, 4x455 panels, 4x200mah battery pack 48v

Re: 200 Watts at idle?!!!

Post by FrancoV » Fri Dec 29, 2023 4:50 pm

After reading and reading and trying to learn about how electric power works (btw, I have the same problem):

I've learned something about Kwh / Kvah. So, I have a digital rele that is telling me that my inverter is draining 1.2/1.5 Amperes from the grid 24/7 and I automatically assumed that it was consuming 1.5ax220v = 330 W/h but then I saw a video called "Power factor and Solar Energy" (something like that, in Spanish). It seems that inverters "reserve" some reactive power from the grid, in order to power engines or devices that need some instant power to work and the batteries or panels can't provide (also because they deliver DC and that energy need to pass through the inverter to be converted to AC). So that "reserve" of reactive power is expressed in terms of current but not volts (at least that's what I've understood).

So I bought another rele with an advanced meter (also wifi), and I saw that even I have that 1.2/1.5A, the "real power consumption" was 13Wh /20Wh.
I need to investigate a bit more about reactive power and real power, 'cause i've learned there is penalization from the Power company if your Power factor main component is reactive (power you reserve but not used).

Could this be the answer of our problems? (not sure if I'm n the right track, I'm just a beginner level about this things)
Attachments
Screenshot_20231229_214730_Smart Life.jpg

User avatar
Mike Curran
Forum Emperor
Posts: 3602
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: 200 Watts at idle?!!!

Post by Mike Curran » Tue Jan 02, 2024 9:36 am

I found the answer with much help from OB tech support, described in this thread: viewtopic.php?p=81172&hilit=Idle#p81172

It's normal for Skybox to draw 100-150watts at idle, sad to say.