AC coupled - batteries not charging from solar array during outage
-
Greg T Fordan
Re: AC coupled - batteries not charging from solar array during outage
So you got it! That is the only screen you have to deal with regards to AC coupling. Do not even touch the Grid Interface Protection menu.
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
OK. No worries... I never change any setting without clear guidance.... hence my myriad posts and emails. Doesn't help my struggle to have inconsistencies between documentation and display menus.
Question remains: Do I change the Frequency Shift Response Time (Battery Sample Time) to 3 seconds, or not (currently .02 s).
References:
1) acc_freq_app_note.pdf: This document states: "Change AC Coupling from N to Y, and change the Freq Shift Response Time (0.02 to 5.0 seconds) if desired. This setting adds/subtracts delay in the frequency steps between 60.0 and 64.5 Hz."
2) Ian McClusky stated in an email communication: "We recommend the minimum (0.02 seconds) Frequency Shift Response Time for lithium ion batteries only, and about 3 seconds for most lead-acid batteries." (I have 220GH batteries)
S/D
Question remains: Do I change the Frequency Shift Response Time (Battery Sample Time) to 3 seconds, or not (currently .02 s).
References:
1) acc_freq_app_note.pdf: This document states: "Change AC Coupling from N to Y, and change the Freq Shift Response Time (0.02 to 5.0 seconds) if desired. This setting adds/subtracts delay in the frequency steps between 60.0 and 64.5 Hz."
2) Ian McClusky stated in an email communication: "We recommend the minimum (0.02 seconds) Frequency Shift Response Time for lithium ion batteries only, and about 3 seconds for most lead-acid batteries." (I have 220GH batteries)
S/D
-
Greg T Fordan
Re: AC coupled - batteries not charging from solar array during outage
I recommend staying with .02s since it is obviously working at this time, when you are AC coupled with the grid and the Radian.
Now, when the next grid outage comes around, and you encounter the issue of the SolarEdge inverter not syncing with the Radian, maybe that is the time to tinker the setting from the default .02s.
But here's the Here and Now -->Your system is doing good, selling a daily average of 15 kWh + to the grid. The "Buy" times are very few and far between. If I own that system, I will be quite satisfied and not worry about tweaking other settings, for now :-"
Apologies for the literature that were not updated. Yes, from the old way of doing AC Couple, the menu was inside the MATE3/MATE3s menus.
Now, when the next grid outage comes around, and you encounter the issue of the SolarEdge inverter not syncing with the Radian, maybe that is the time to tinker the setting from the default .02s.
But here's the Here and Now -->Your system is doing good, selling a daily average of 15 kWh + to the grid. The "Buy" times are very few and far between. If I own that system, I will be quite satisfied and not worry about tweaking other settings, for now :-"
Apologies for the literature that were not updated. Yes, from the old way of doing AC Couple, the menu was inside the MATE3/MATE3s menus.
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
OK. Yes... system is doing better than ever since I resolved my water system leak (under concrete driveway). If you didn't read that... it was short-cycling my well pump, obviously using a lot of power, for what could have been years... likely started as a dribble and then increased to a gusher over time. No above-ground evidence of leakage.
I don't anticipate any S/E or battery issues not that the well pump issue has been resolved, but if that occurs... I will recognize it and have a much better understanding of why and how to resolve.
So... the as yet unanswered, hanging questions...
1) FLEXnet DC Advanced Control-Enable Auto Grid-Tie Control... Yes or No. I would prefer charging to be the priority over selling. If Yes... will not my issue with FNDC Days ChargeParmsMet affect that?
2) OpticsRE-FNDC-Days Since Parms Met = 34 days. How can I correct this?
S/D
I don't anticipate any S/E or battery issues not that the well pump issue has been resolved, but if that occurs... I will recognize it and have a much better understanding of why and how to resolve.
So... the as yet unanswered, hanging questions...
1) FLEXnet DC Advanced Control-Enable Auto Grid-Tie Control... Yes or No. I would prefer charging to be the priority over selling. If Yes... will not my issue with FNDC Days ChargeParmsMet affect that?
2) OpticsRE-FNDC-Days Since Parms Met = 34 days. How can I correct this?
S/D
-
clarkef
- Forum Guru
- Posts: 149
- Joined: Wed Oct 31, 2018 9:43 am
- My RE system: Radian 8048A w/PV GSLC
FM100 CC x3
10KW of 72 cell panels (5S3P x2)
2200AH (usable) of Li-Ion modules @48v with SIMP-BMS
Midnite Combiners, SPDs
MilSurp MEP-802A ‘5K’ Generator
Off-grid - Location: South Central KY
Re: AC coupled - batteries not charging from solar array during outage
Swampdog,
Did you get your question answered? It’s a month later - have your batteries met charge parms yet?
I’ve found that that my charge parms met doesn’t always reset “days since..” unless the batteries sit at their float setting (and presumably the float timer expires). This came up for me in the last two days - for the first time in 10 days I hit my 100% SOC and immediate added a bunch of load to take advantage of a full charge. The “days since” did not trip over. Yesterday I hit full charge and did not add load and the “days since...” did trip over.
P.s. if you. Still have the ROCB that was removed from your system when you went AC coupled with the new firmware, I’d be interested in buying it from you. I need one for another project and haven’t been able to source one cheaply.
Clarke
Did you get your question answered? It’s a month later - have your batteries met charge parms yet?
I’ve found that that my charge parms met doesn’t always reset “days since..” unless the batteries sit at their float setting (and presumably the float timer expires). This came up for me in the last two days - for the first time in 10 days I hit my 100% SOC and immediate added a bunch of load to take advantage of a full charge. The “days since” did not trip over. Yesterday I hit full charge and did not add load and the “days since...” did trip over.
P.s. if you. Still have the ROCB that was removed from your system when you went AC coupled with the new firmware, I’d be interested in buying it from you. I need one for another project and haven’t been able to source one cheaply.
Clarke
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
Although maintaining 99-100% SOC, Charge parms met as reported by FNDC cites over 60 days.
I do not have the removed ROBC.
S/D
I do not have the removed ROBC.
S/D
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC coupled - batteries not charging from solar array during outage
This FNDC application note http://outbackpower.com/downloads/docum ... p_note.pdf describes the settings for charge parameters met as follows: The 3 important parameters for meeting charge parameters are charged voltage, charged return amps and charge time. The app note explains how a combo of these 3 set point determines if charge parameters are met. If your system isn't meeting all 3, it won't meet charge parameters.
My 2007 system routinely meets charge parameters when there's sufficient sun. Here's a screenshot from 12/27:Here's a screenshot of my charge parameters: Hope this helps.
My 2007 system routinely meets charge parameters when there's sufficient sun. Here's a screenshot from 12/27:Here's a screenshot of my charge parameters: Hope this helps.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
Mike, et al;
Attached are my settings and today's data. Sun is a bit low this time of year, but weather was pretty clear. As my Grid-tie inverter is SolarEdge, I included today's SolarEdge panel array production.
I read that the FNDC Charge Voltage should be lower than the GS8048A Absorb Voltage. Both those settings are 57.6VDC (default for both). Could that be my issue with Parms Met (now 67 days)?
S/D
Attached are my settings and today's data. Sun is a bit low this time of year, but weather was pretty clear. As my Grid-tie inverter is SolarEdge, I included today's SolarEdge panel array production.
I read that the FNDC Charge Voltage should be lower than the GS8048A Absorb Voltage. Both those settings are 57.6VDC (default for both). Could that be my issue with Parms Met (now 67 days)?
S/D
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC coupled - batteries not charging from solar array during outage
Absolutely! Here's the relevant info from the app note:I read that the FNDC Charge Voltage should be lower than the GS8048A Absorb Voltage. Both those settings are 57.6VDC (default for both). Could that be my issue with Parms Met (now 67 days)?
"Since the charging source (inverters and charge controllers) will drive the battery voltage up to its Absorb set point, the Charged Voltage should be programed below (0.4V for 48V, 0.2V for 24V and 0.2V for 12V systems) the Absorb Voltage set point of the charging source. For example, if the inverter’s Absorb Voltage is set to 58.4V, then the Charged Voltage in the FN-DC should be set to 58.0V. This will guarantee that the Charged Voltage value in the FN-DC will always be met as the charging source will drive the battery voltage up to its Absorb set point."
So your charged voltage should be set for 57.6 - 0.4 = 57.2. If you want to attain a higher absorb point, adjust both settings up but make sure the charged voltage in the FNDC is set 0.4 volts lower than your inverter absorb setpoint.
I think if you do this you'll see charge parameters met.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
Mike, et al;
Done.
So wondering what changed, I looked back in my record to 67 days ago, the last time the Charge Parms were met.
I had experienced a serious battery power consumption problem during an outage, hence this thread (and some others). I eventualy figured out our well pump was constantly short-cycling due to a major leak under our driveway slab. Once repaired, all perceived solar issues resolved. However, I wallowed in solar tech support for several weeks, not realizing the cause. Some other settings issues did come to light, however.
I was directed to change the following, which I did, exactly 67 days ago:
Radian GS8048A: Changed Absorb charge settings from 1 hr. to 4 hrs.
FNDC: Battery AH from 400 to 660 & Charged Voltage from 28.7 to 57.6.
Charge Parms not met ever since.
We will see tomorrow, when the sun comes up methinks!
S/D
Done.
So wondering what changed, I looked back in my record to 67 days ago, the last time the Charge Parms were met.
I had experienced a serious battery power consumption problem during an outage, hence this thread (and some others). I eventualy figured out our well pump was constantly short-cycling due to a major leak under our driveway slab. Once repaired, all perceived solar issues resolved. However, I wallowed in solar tech support for several weeks, not realizing the cause. Some other settings issues did come to light, however.
I was directed to change the following, which I did, exactly 67 days ago:
Radian GS8048A: Changed Absorb charge settings from 1 hr. to 4 hrs.
FNDC: Battery AH from 400 to 660 & Charged Voltage from 28.7 to 57.6.
Charge Parms not met ever since.
We will see tomorrow, when the sun comes up methinks!
S/D
-
IanMcCluskey
Re: AC coupled - batteries not charging from solar array during outage
Hi S/D, I looked at the last few days of history, and though the system seems to perform as expected, I see the FN-DC still reports 70 days since parms met. I will try to find out why. I would not worry about it affecting performance at this point.
-
Greg T Fordan
Re: AC coupled - batteries not charging from solar array during outage
SD, remember that your FNDC "Charged Voltage " setting used to be 28.8VDC and a wrong setting. That was the reason you were frequently getting a "Charged Parms Met" because it was easily getting its target of 28.8 VDC which did not apply/meaningless in your 48V system in the first place.
If you really want to get some of that "Charged Parms Met" reports again, try this: Lower your "Charged Voltage" setting to 51VDC.
If you really want to get some of that "Charged Parms Met" reports again, try this: Lower your "Charged Voltage" setting to 51VDC.
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
Group;
OK, so I think I am getting the idea about the role of the FNDC. I adjusted the Charged voltage a couple times and was able to get the Days Since ChargeParms Met to reset. Currently watching array output versus Charged Voltage settings to decide what to leave it at. Interestingly, when attempting to change the Charged voltage through the FNDC device via OpticsRE, it will not accept the setting of 51v you recommended (Greg). Does allow 52v.
New issue: I have the following settings in place.
Settings > MATE3s > FLEXnet DC Advanced Control:
o Enable Charge Termination Control: Y
o Enable Auto Grid-Tie Control: Y
o Offset Enable: Y
Although the MATE3s Programming Guide claims setting Enable Grid-Tie Control to "Y" causes Offset Enable to automatically revert to "Y". 1) That did not occur, so I set it manually. 2) After re-checking numerous times, Offset Enable always reverts to "N". I have manually reset to "Y" numerous times, to no avail.
What could be causing this and how might I remedy it?
My goal is to fully charge the batteries from the array before selling... which does not seem to be occurring as it should.
Thanks for any input!
S/D
OK, so I think I am getting the idea about the role of the FNDC. I adjusted the Charged voltage a couple times and was able to get the Days Since ChargeParms Met to reset. Currently watching array output versus Charged Voltage settings to decide what to leave it at. Interestingly, when attempting to change the Charged voltage through the FNDC device via OpticsRE, it will not accept the setting of 51v you recommended (Greg). Does allow 52v.
New issue: I have the following settings in place.
Settings > MATE3s > FLEXnet DC Advanced Control:
o Enable Charge Termination Control: Y
o Enable Auto Grid-Tie Control: Y
o Offset Enable: Y
Although the MATE3s Programming Guide claims setting Enable Grid-Tie Control to "Y" causes Offset Enable to automatically revert to "Y". 1) That did not occur, so I set it manually. 2) After re-checking numerous times, Offset Enable always reverts to "N". I have manually reset to "Y" numerous times, to no avail.
What could be causing this and how might I remedy it?
My goal is to fully charge the batteries from the array before selling... which does not seem to be occurring as it should.
Thanks for any input!
S/D
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC coupled - batteries not charging from solar array during outage
I would try disabling auto charge termination control. That's how my system is set up and it works properly.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
Thx... but I have no FLEXmax charge controllers, which I believe the Global Charge menu is intended for. Global Charger Control id "Disabled".
S/D
S/D
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC coupled - batteries not charging from solar array during outage
Based on the Mate3s manual, I think the global charge menu applies whether you have an fm80 or not:I would still try disabling auto charge termination, just to see if it makes a difference.
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
OK... done. I see the MATE3s Programming Guide states that an FNDC is required (only). We will see. Wondering then, as Global Charger Control is set to the default "Disabled". Should this be enabled?
S/D
S/D
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC coupled - batteries not charging from solar array during outage
Based on the manual, sounds like global charge control is just to limit total battery charging amps from FM's plus inverters, but it doesn't limit charging from inverters so I'd say with your system it doesn't matter. Disabled should still allow the other settings to work. Here's what the manual says about it:
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
OK... tried that, but Offset Enable still reverted to "N". No idea when exactly that occurs. The Programming Guide states that if Auto Grid-Tie Control is enabled (Y), Offset Enable will automatically switch to enable (Y). That has never occurred. Have reset many times to "Y"... to no avail.
Here are some relevant settings:
• Settings>MATE3s>Global Charge:
o Auto Charge Terrmination Control: Disabled (as recommended by Mike Curran)
• Settings>MATE3s>FLEXnet DC Advanced Control:
o Enable Charge Termination Control: N
o Enable Auto Grid-Tie Control: Y
• Settings>Inverter>Grid-Tie Sell: Offset Enable: Y (eventually reverts to N, consistently)
• Settings>Inverter>AC Coupling:
o Inverter-AC Coupling-AC Coupling Enabled: Y
So my questions are... why does this occur and does it matter? If it matters... how can I correct it?
Thx!
S/D
Here are some relevant settings:
• Settings>MATE3s>Global Charge:
o Auto Charge Terrmination Control: Disabled (as recommended by Mike Curran)
• Settings>MATE3s>FLEXnet DC Advanced Control:
o Enable Charge Termination Control: N
o Enable Auto Grid-Tie Control: Y
• Settings>Inverter>Grid-Tie Sell: Offset Enable: Y (eventually reverts to N, consistently)
• Settings>Inverter>AC Coupling:
o Inverter-AC Coupling-AC Coupling Enabled: Y
So my questions are... why does this occur and does it matter? If it matters... how can I correct it?
Thx!
S/D
- Mike Curran
- Forum Emperor
- Posts: 3602
- Joined: Sat Aug 28, 2004 6:28 pm
- My RE system: Outback - Garage roof (2017):
- 6 (2×3) ALEO S79-300's into one FM80 (2017-25, restored 9-7-2026)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 6 Simpliphi 3.8kwh, 24V, 900Ah (replaced 2007-25 vintage Rolls)
- Hub10.3, Mate3s, FNDC. Tigo ES maximizers on each PV module.
Westinghouse Solar - Barn roof: (2012)
- 24 (2x12) 235W Lightways panels with Enphase M215 microinverters plus 6 - 275W Talesun panels, also with M215s, grid-tied
Outback Skybox - Barn roof: (2019)
- 14 Trina Solar 270W in series (DC array input to SB inverter/charger), installed 3/5/24 (replaced original 2019 Talesun DC array)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters
Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed - Location: Chagrin Falls, Ohio
Re: AC coupled - batteries not charging from solar array during outage
Mine also reverts to N, until charge parameters are met, and then it changes to Y. Until midnight when it resets to N again, waiting for charge parameters to be met again. During cloudy periods, this won't happen until the sun comes out - possibly for days.Settings>Inverter>Grid-Tie Sell: Offset Enable: Y (eventually reverts to N, consistently)
I'm just a beginner when it comes to AC coupled arrays, so I don't know if you can expect your AC coupled array to charge the battery unless the grid goes down... if that's your only PV charging source, you may never meet charge parameters. However, I'm re-reading your post and I see your system isn't charging when the grid is down - is that still the case?
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
No. The real source of my issues was a water leak causing a well pump to cycle every few minutes. During an outage, batteries low voltage shutdown, triggering other issues. Leak is fixed and I understand what occurred.
What you describe with Offset Enable and your system may well whst happens... I have read nothing on this in the literature.
Batteries can charge from array, grid, or both depending on load.
If your description of on and off Offset Enable is correct, then all is working as it should as well as selling a lot of power.
Thx for your help.
S/D
What you describe with Offset Enable and your system may well whst happens... I have read nothing on this in the literature.
Batteries can charge from array, grid, or both depending on load.
If your description of on and off Offset Enable is correct, then all is working as it should as well as selling a lot of power.
Thx for your help.
S/D
-
IanMcCluskey
Re: AC coupled - batteries not charging from solar array during outage
Thread moved to the newly created AC Coupling forum
-
atomicsolar
- Forum Junior Member
- Posts: 1
- Joined: Sat Feb 08, 2020 12:03 pm
Re: AC coupled - batteries not charging from solar array during outage
ROCB is tripping main breakers? Would AFCI trip it as well? Could be a load in the back up panel, like a pump pressure switch arcing, setting off the AFCI?
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
I thought all was resolved, but we are now in the midst of the first outage (high winds bringing down lines) since my previous issues. Today we suffered a power outage and I noticed the batteries seemed not to be charging from the array, although we have a cloudless, sunny day. Upon checking my SolarEdge 6000 inverter, I saw the original fault returned. This time, there is no low voltage issue.
In 4.5 hours batteries have dropped to 90% and <50vdc. I am thinking I need to connect the generator and charge up before I run into the low-voltage shutdown again.
No idea where to go with this, this time around, since I thought all settings were appropriate and my power drain resolved (cycling well pump). Any assistance appreciated!
S/D
In 4.5 hours batteries have dropped to 90% and <50vdc. I am thinking I need to connect the generator and charge up before I run into the low-voltage shutdown again.
No idea where to go with this, this time around, since I thought all settings were appropriate and my power drain resolved (cycling well pump). Any assistance appreciated!
S/D
-
Swampdog
- Forum Guru
- Posts: 126
- Joined: Tue Feb 19, 2019 4:23 pm
- My RE system: 7.0 kw system
AC-coupled
25 x Solarworld SW280 w/SolarEdge Power Optimizers
12 x 220 GH Energycell
Outback GS load center GSLC175-PV-120/240
Outback Radian 8048a
Outback MATE3s
Outback HUB
Outback FlexNet DC
SOLAREDGE SE6000A-US
Briggs & Stratton Elite 5500w generator (8,500 surge; manual connect)
Re: AC coupled - batteries not charging from solar array during outage
Update:
Before connecting the generator, I was able to clear the SolarEdge fault and it appears, at the moment anyway, array is charging batteries and voltage rising. Not enough daylight left to fully charge, I am sure, sop may supplement with the generator a bit later.
This leaves me to believe there was a problem switching immediately as the grid power failed, so likaly a setting.
Assistance still needed to analyze this, however.
S/D
Before connecting the generator, I was able to clear the SolarEdge fault and it appears, at the moment anyway, array is charging batteries and voltage rising. Not enough daylight left to fully charge, I am sure, sop may supplement with the generator a bit later.
This leaves me to believe there was a problem switching immediately as the grid power failed, so likaly a setting.
Assistance still needed to analyze this, however.
S/D