Hi All,
I'm having a terrible time finding the discharge curves for the 200NC battery. The one that shows voltage vs state of charge.
I'm trying to figure out what voltage corresponds to 60% SOC so I know when I need to start the generator.
Thanks.
-Jacob
200NC Discharge Curve?
-
raysun
- Forum Overlord
- Posts: 13666
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: (Former system. Now retired.)
Flexpower Two: (2) FXR3048A-01 - Series Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid
Re: 200NC Discharge Curve?
I use 200NC and find the discharge curve fairly typical of AGM lead acid batteries. However, voltage v.s. SOC is a tricky proposition as it varies with load. In order to measure it with any accuracy, the battery must be in an open-circuit state (no load) for at least several hours, with 24 hours needed to assure a high degree of stability for the reading.
For example, under load, my 48V @ 350AH battery is at 65% SOC. With ~ 8A draw = 48.5V. With ~ 25A draw = 48.0V.
Most systems in continuous use (like my off-grid system) are best monitored using a "coulomb counter" that measures charge into and out of the battery to derive SOC. Outback's meter for this is the FlexNET DC. There are other quality counters as well.
For example, under load, my 48V @ 350AH battery is at 65% SOC. With ~ 8A draw = 48.5V. With ~ 25A draw = 48.0V.
Most systems in continuous use (like my off-grid system) are best monitored using a "coulomb counter" that measures charge into and out of the battery to derive SOC. Outback's meter for this is the FlexNET DC. There are other quality counters as well.