Charge controller is not registering correct

General Talk

Moderators: OutBack, OutBack Moderator Team

Post Reply
jainsw
Forum Guru
Posts: 457
Joined: Mon Dec 28, 2009 10:54 am
My RE system: My setup is a 48v system and is comprised of the following components:
12-ES190 Evergreen solar panels-pole mount non-auto tracking, 4 220 Volt GE panels fixed mount
12-Hanwha Q Peak 300watt panels
1-Outback FM60 PV Charge controller 60a MPPT, 12-60 vdc. 60a output
1-Outback FM80 PV CC, 80a MPPT
1-Outback VFX3648 3.6kw, 120vac output
1-Mate3s with OpticsRE
1-Outback Hub
1-Outback FNDC
7-SimpliPhi 3.8-48v-75Ah Lithium batteries

Charge controller is not registering correct

Post by jainsw »

I have two charge controllers and my battery bank is showing only 78%, but the FM60 controller is showing float and the FM80 is showing charging. Any ideas of what is the issue?
raysun
Forum Emperor
Posts: 9024
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Parallel Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Charge controller is not registering correct

Post by raysun »

Assuming the two arrays are functioning normally, and the charge parameters set the same, the most likely issue is calibration (or lack thereof).
viewtopic.php?t=15400
User avatar
Mike Curran
Forum Emperor
Posts: 2912
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Charge controller is not registering correct

Post by Mike Curran »

Whenever I see this issue on the forum I always remember the Mate3s has a float coordination function, which should be almost as important in resolving it as calibration is.
Screenshot_20221119_100507_Adobe Acrobat.jpg
Screenshot_20221119_100333_Samsung Internet.jpg
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
jainsw
Forum Guru
Posts: 457
Joined: Mon Dec 28, 2009 10:54 am
My RE system: My setup is a 48v system and is comprised of the following components:
12-ES190 Evergreen solar panels-pole mount non-auto tracking, 4 220 Volt GE panels fixed mount
12-Hanwha Q Peak 300watt panels
1-Outback FM60 PV Charge controller 60a MPPT, 12-60 vdc. 60a output
1-Outback FM80 PV CC, 80a MPPT
1-Outback VFX3648 3.6kw, 120vac output
1-Mate3s with OpticsRE
1-Outback Hub
1-Outback FNDC
7-SimpliPhi 3.8-48v-75Ah Lithium batteries

Re: Charge controller is not registering correct

Post by jainsw »

Trying to remember how to reset the SoC on my system as I shut it down this am when it was at 54% and upon turning everything back on the SoC is at 100%. How to reset the SoC?
raysun
Forum Emperor
Posts: 9024
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Parallel Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Charge controller is not registering correct

Post by raysun »

jainsw wrote: Sat Nov 19, 2022 8:56 am Trying to remember how to reset the SoC on my system as I shut it down this am when it was at 54% and upon turning everything back on the SoC is at 100%. How to reset the SoC?
Answered in the other post. In a word, the FNDC SoC can't be adjusted. The battery must now be fully charged to sync with the meter reading.
jainsw
Forum Guru
Posts: 457
Joined: Mon Dec 28, 2009 10:54 am
My RE system: My setup is a 48v system and is comprised of the following components:
12-ES190 Evergreen solar panels-pole mount non-auto tracking, 4 220 Volt GE panels fixed mount
12-Hanwha Q Peak 300watt panels
1-Outback FM60 PV Charge controller 60a MPPT, 12-60 vdc. 60a output
1-Outback FM80 PV CC, 80a MPPT
1-Outback VFX3648 3.6kw, 120vac output
1-Mate3s with OpticsRE
1-Outback Hub
1-Outback FNDC
7-SimpliPhi 3.8-48v-75Ah Lithium batteries

Re: Charge controller is not registering correct

Post by jainsw »

raysun wrote: Sat Nov 19, 2022 8:58 am
jainsw wrote: Sat Nov 19, 2022 8:56 am Trying to remember how to reset the SoC on my system as I shut it down this am when it was at 54% and upon turning everything back on the SoC is at 100%. How to reset the SoC?
Answered in the other post. In a word, the FNDC SoC can't be adjusted. The battery must now be fully charged to sync with the meter reading.
Ok so if I leave everything plugged in will it reset without me here for two weeks?
raysun
Forum Emperor
Posts: 9024
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Parallel Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Charge controller is not registering correct

Post by raysun »

jainsw wrote: Sat Nov 19, 2022 9:00 am
raysun wrote: Sat Nov 19, 2022 8:58 am
jainsw wrote: Sat Nov 19, 2022 8:56 am Trying to remember how to reset the SoC on my system as I shut it down this am when it was at 54% and upon turning everything back on the SoC is at 100%. How to reset the SoC?
Answered in the other post. In a word, the FNDC SoC can't be adjusted. The battery must now be fully charged to sync with the meter reading.
Ok so if I leave everything plugged in will it reset without me here for two weeks?
It doesn't reset, so much as sync with the true battery status once it's fully charged.
jainsw
Forum Guru
Posts: 457
Joined: Mon Dec 28, 2009 10:54 am
My RE system: My setup is a 48v system and is comprised of the following components:
12-ES190 Evergreen solar panels-pole mount non-auto tracking, 4 220 Volt GE panels fixed mount
12-Hanwha Q Peak 300watt panels
1-Outback FM60 PV Charge controller 60a MPPT, 12-60 vdc. 60a output
1-Outback FM80 PV CC, 80a MPPT
1-Outback VFX3648 3.6kw, 120vac output
1-Mate3s with OpticsRE
1-Outback Hub
1-Outback FNDC
7-SimpliPhi 3.8-48v-75Ah Lithium batteries

Re: Charge controller is not registering correct

Post by jainsw »

raysun wrote: Sat Nov 19, 2022 9:02 am
jainsw wrote: Sat Nov 19, 2022 9:00 am
raysun wrote: Sat Nov 19, 2022 8:58 am

Answered in the other post. In a word, the FNDC SoC can't be adjusted. The battery must now be fully charged to sync with the meter reading.
Ok so if I leave everything plugged in will it reset without me here for two weeks?
It doesn't reset, so much as sync with the true battery status once it's fully charged.
Thanks much again!