How to charge the AGM batteries?

Post by mrch22 »

how to charge AGM batteries using the power grid, I have tried to configure my skybox to do it but I can't find a way to charge them without using solar energy
Ampster
Forum Guru
Posts: 319
Joined: Sat Apr 11, 2015 5:14 pm
My RE system: 7.9 kW self installed Enphase system NEM 2.0 PTO 9*2021. Skybox, and heat pump/AC system. The Skybox is powered by a 42 kWh pack of LFP batteries and 2kW panels. It is used in self consumption mode for load shifting and backup.
Location: Kenwood, Northern California

Re: How to charge the AGM batteries?

Post by Ampster »

If you just want a one time charge you can do a reset that will start Bulk. Do you have a rate structure that is economical to charge from grid? What mode are you using?
Use my Skybox in Self Consumption mode to reduce my energy costs, including charging two EV from solar when possible.
User avatar
Mike Curran
Forum Emperor
Posts: 2863
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof (2007/2017):
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied VFXR3524A-01's series stacked, replaced GVFX's (2020)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS. Tigo ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 microinverters

Battery systems operate in grid-tied, net metering w/backup mode
All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: How to charge the AGM batteries?

Post by Mike Curran »

Your Skybox will only charge from grid when battery voltage drops to the rebulk setpoint, or if you manually start a bulk charge by doing a reset, as Ampster says. So set rebulk where you want charging from grid to begin:
Screenshot_20220917_212051_Samsung Internet.jpg
As you can see I have mine set for 51.0V. My battery never reaches that point because I have solar charging. On OpticsRE:
Screenshot_20220917_212458_Samsung Internet.jpg
https://ei.tigoenergy.com/p/pZXn7SZQyO45
https://enlighten.enphaseenergy.com/public/systems/Hctc107221
Ampster
Forum Guru
Posts: 319
Joined: Sat Apr 11, 2015 5:14 pm
My RE system: 7.9 kW self installed Enphase system NEM 2.0 PTO 9*2021. Skybox, and heat pump/AC system. The Skybox is powered by a 42 kWh pack of LFP batteries and 2kW panels. It is used in self consumption mode for load shifting and backup.
Location: Kenwood, Northern California

Re: How to charge the AGM batteries?

Post by Ampster »

Its raining here today and my battery is at 82% and there is not much prospect of much solar production I just triggered a reset while rates are low so I will have capacity.
Use my Skybox in Self Consumption mode to reduce my energy costs, including charging two EV from solar when possible.