Flexware 500-DC Ground Question

OutBack's newest innovation in balance-of-system components

Moderators: OutBack, OutBack Moderator Team

Post Reply
bdimambro
Forum Member
Posts: 5
Joined: Thu Mar 17, 2022 8:28 am
My RE system: Outback Power 24VDC Power Panel 2x VXFR3524A / 2x FM100 - Currently Building

Flexware 500-DC Ground Question

Post by bdimambro »

All,

Yea I know ... another ground question. The Flexware DC-500 enclosure I purchased for use in my power panel build has the ground terminal bonded to the line (device) DC terminal block for SHUNTA. I do not see this bond on the schematics or being present on my brother-in-laws's 48VDC factory wired Flexware power panel (in the 500-DC power box). I do have the AC neutral bonded to ground in the 500-AC power box. Is this bond necessary?

Thanks for the help,

Brian
raysun
Forum Emperor
Posts: 9024
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Parallel Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Flexware 500-DC Ground Question

Post by raysun »

Battery Negative is frequently grounded, along with other DC components, and this may be an implementation for that purpose. I don't know of a reason it would be connected on the load side of a shunt, however.
The AC ground to neutral bond generally terminates on the same ground, but serves a different purpose.
bdimambro
Forum Member
Posts: 5
Joined: Thu Mar 17, 2022 8:28 am
My RE system: Outback Power 24VDC Power Panel 2x VXFR3524A / 2x FM100 - Currently Building

Re: Flexware 500-DC Ground Question

Post by bdimambro »

Yea, my verbiage was sloppy. What I meant was if the bond between the ground and SHUNTA was necessary in the DC-500 box. Bonding the AC neutral to ground is needed.

Brian
raysun
Forum Emperor
Posts: 9024
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Parallel Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Flexware 500-DC Ground Question

Post by raysun »

If you are wanting to ground the battery negative (generally considered a best practice), that connection would allow for it.