2 FM80
i have to install 12 panels 545 Watts each(isc 14A, Voc 50V)
i have 2 FM80
what do you suggest to configure them ?? and what cables thickness i would use ?
thx
i have 2 FM80
what do you suggest to configure them ?? and what cables thickness i would use ?
thx
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
This for a 48V nominal battery?
6 panels per FM80
The individual arrays:
2 panels in series (100Voc)
3 series strings in parallel
Each array needs a combiner box to connect the parallel strings (2 combiner boxes in total, each with at least 3 series connections via fuse or circuit breaker). Each string should be connected to the combiner using 10AWG wire rated for solar panel use. The connection from the combiner output to the FM80 PV input should be via an 80A disconnect (circuit breaker) and 6AWG wire.
Programming the FM80s will depend on the specific battery connected. Has that been identified?
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
yes sure it's clear ... thx
another thing could i install 8 panels (2 in series and 4 in parallel) for the first FM80
and 4 panels(2 in series and 2 in parallel ) for the second FM80 ????
cause i have a problem with the wiring for the second one .
any problem with that ??
thx
another thing could i install 8 panels (2 in series and 4 in parallel) for the first FM80
and 4 panels(2 in series and 2 in parallel ) for the second FM80 ????
cause i have a problem with the wiring for the second one .
any problem with that ??
thx
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
8 panels @ 545 Watts = 4360 Watts for the array. It exceeds the FM80's recommended limit of 4000 Watts sufficiently to put the controller at risk of overload, and possibly failure. I'd advise against the 8 panel array.
What sort of wiring issue is there?
What sort of wiring issue is there?
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
I have 16 mm2 cables for the first one(Fm80) and 6 mm2 for the second one and it's difficult to change them
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
Yes from PVs to Controller.
Pvs : philadelphia 545w bifacial
Pvs : philadelphia 545w bifacial
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
A 6 panel array (2 x 3) would have a maximum power current of just under 40A. 6mm² wire is rated at 47A (free air), 30A in conduit. Since full output current is rare, the 6mm cable might be able to handle the array, but is a bare minimum to be sure. To protect the wiring, use a DC circuit breaker of a size commensurate with the wire's rated capacity.
The 16mm² cable, of course, can handle the 40A current.
Are there two combiner boxes, one for each array, at the location of the arrays? The 6mm² and 16mm² cables are the output from the combiner going to the PV input of the two FM80s?
Keeping the arrays under the 4kW power limit will help assure a long life for the FM80s.
The 16mm² cable, of course, can handle the 40A current.
Are there two combiner boxes, one for each array, at the location of the arrays? The 6mm² and 16mm² cables are the output from the combiner going to the PV input of the two FM80s?
Keeping the arrays under the 4kW power limit will help assure a long life for the FM80s.
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
Yes it's clear ... Thx a lot
And sure i have 2 combiner boxes for each array at the location of the arrays.
And the 6mm2 and 16mm2 are the Pvs input to the FM80s.
I will put a breaker of 50A at the end of 6 mm2 cable ... Good?
And sure i have 2 combiner boxes for each array at the location of the arrays.
And the 6mm2 and 16mm2 are the Pvs input to the FM80s.
I will put a breaker of 50A at the end of 6 mm2 cable ... Good?
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
The breaker is there to protect the cable. I'd suggest 40A DC breaker for the 6mm.I will put a breaker of 50A at the end of 6 mm2 cable ...
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
Ok i'll do it
Thx
Thx
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
another question ...
can i use mc4 parallel connectors ? or combiner boxes is better ???
thx
can i use mc4 parallel connectors ? or combiner boxes is better ???
thx
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
ok
thx a lot
thx a lot
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
I already installed the new panels and new FM80 ... Any settings must be done ??
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
Is this the battery in the system?
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
No ... It's cousin's one ...
Exide Enersol T 2V (450A) 24 batteries 5 years old.
FXR3048E - 2FM80 - Mate3
Exide Enersol T 2V (450A) 24 batteries 5 years old.
FXR3048E - 2FM80 - Mate3
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
Do you have the factory charging specifications for the battery?
-
- Forum Whiz
- Posts: 48
- Joined: Tue Apr 21, 2015 4:33 am
- My RE system: Grid interactive system,(Backup),GVFX3048E , Flexmax 80 , Xtralast 200A 12V (4), 2600W Solar, Sell:NO, RTS, Hub4, Mate3, OpticsRE
- Location: Batroun, Lebanon
Re: 2 FM80
yes , and i don't have problem setting the 2 FM with batteries settings, so the point is that could i make some settings to let the 2 FM to work together in all cases(Absorption and floating) ... or they do that automatically when they are connecting to the same HUB ???
-
- Forum Emperor
- Posts: 8023
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: 2 FM80
Both FM80 need to be manually programmed with the same charging parameters. Absorb Voltage, Absorb Time, Float Voltage, Re-Bulk Voltage, EQ Voltage, EQ Time, and Auto EQ Interval should be set to equal values on both FM80. End Amps = 0 on both FM80.
Further, the combined maximum charging current output from the two FM80 must be adjusted to match the battery's maximum allowed charging current. The theoretical maximum output of the combined FM80 is 160A. If the battery's maximum charge current specification is, for example, 60A, then the Maximum Current setting on the two controllers must be set such that their values add to no more than 60A. The two Maximum Current values need not be the same, and it may take some experimentation to get optimum settings, dependent on array permance. As a practical measure, the FM80 that draws from array that uses the 16mm² cable to feed current could be set to a higher Maximum Current value than the FM80 drawing current from the array wired with the 6mm² cable.
Finally, in order to work in tandem, both FM80 must be calibrated to the battery voltage.
viewtopic.php?t=15400
Further, the combined maximum charging current output from the two FM80 must be adjusted to match the battery's maximum allowed charging current. The theoretical maximum output of the combined FM80 is 160A. If the battery's maximum charge current specification is, for example, 60A, then the Maximum Current setting on the two controllers must be set such that their values add to no more than 60A. The two Maximum Current values need not be the same, and it may take some experimentation to get optimum settings, dependent on array permance. As a practical measure, the FM80 that draws from array that uses the 16mm² cable to feed current could be set to a higher Maximum Current value than the FM80 drawing current from the array wired with the 6mm² cable.
Finally, in order to work in tandem, both FM80 must be calibrated to the battery voltage.
viewtopic.php?t=15400