Lithium batteries are a challenge to integrate with FX class inverters due to the mismatch between Low Battery Cut-Off (LBCO) voltage required by many batteries and the LBCO voltage range settable in the Battery Protection parameters of the FX class inverters.
The FLEXnet DC battery monitor can be used in this case to track the LBCO voltage, and shut down the inverter output in the event the battery voltage is at or below LBCO.
A system with FX/FXR inverter, FLEXnet DC monitor, Mate, and Hub is required. Also a length of light gauge two conductor wire to connect the FNDC Aux relay to the Inverter / On-Off terminals on the FX.
Wire pair will connect to the Inverter On/Off terminals. The other ends will attach to the Aux terminals on the FNDC. There is no polarity to the wiring.
The FNDC Aux will be programmed for LBCO by setting the (Voltage) Low parameter, (Voltage) High parameter, and Low Enable Delay.
Programming for a 48V nominal battery that requires a 50V Low Battery Cut-Out voltage, 52V Low Battery Cut-In voltage, and LBCO Delay of 10 minutes. Relay Mode = Auto
No other parameters are set.
NOTE: The FNDC Aux is a latching relay. In order for it to be enabled (contacts closed), the battery voltage must first be greater than or equal to (Voltage) High.
Low Battery Cut-Off with FNDC
Moderators: OutBack, OutBack Moderator Team
-
- Forum Emperor
- Posts: 8024
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
- SandyP
- Forum Czar
- Posts: 513
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Low Battery Cut-Off with FNDC
Thanks for the write up on LBCO.raysun wrote: ↑Fri Jun 03, 2022 8:44 pm Lithium batteries are a challenge to integrate with FX class inverters due to the mismatch between Low Battery Cut-Off (LBCO) voltage required by many batteries and the LBCO voltage range settable in the Battery Protection parameters of the FX class inverters.
The FLEXnet DC battery monitor can be used in this case to track the LBCO voltage, and shut down the inverter output in the event the battery voltage is at or below LBCO.
A system with FX/FXR inverter, FLEXnet DC monitor, Mate, and Hub is required. Also a length of light gauge two conductor wire to connect the FNDC Aux relay to the Inverter / On-Off terminals on the FX.
Do you feel that the Victron BMV's relay function (Low Battery Voltage and/or SoC) would also be an option for those with FX inverters but no Hub or FNDC?
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Emperor
- Posts: 8024
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Low Battery Cut-Off with FNDC
Sure, the BMV series can provide LBCO Aux switching from a "stand alone" battery monitor.
- SandyP
- Forum Czar
- Posts: 513
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Low Battery Cut-Off with FNDC
Hmmm, looks like I will need to upgrade to the BMV-7## series as the earlier models have the relay normally open whilst the 7## series allow you to change that to normally closed.
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Emperor
- Posts: 8024
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Low Battery Cut-Off with FNDC
The 600 series have both Low Voltage and High Voltage sensing logic, do they not? If the relay is NO, then perhaps the Relay High Voltage parameter can be set to LBCI voltage, and the Clear Relay High Voltage parameter set to the LBCO voltage.
FWIW, the FNDC relay is operating like that. It's NO, so the LBCI voltage must be reached first to energize the relay.
- SandyP
- Forum Czar
- Posts: 513
- Joined: Tue Jun 21, 2011 4:44 am
- My RE system: 8 x 190W 24V Suntech panels (4 strings of 2) July 2011
4 x 325W 24V Suntech panels (2 strings of 2) added Sept2018
Mate2
Outback FM60 MPPT (max output lowered to 55amps)
12 x 2V Hoppecke GEL 612 Ah C24 - 24V System (June 2011)
Outback VFX3024 Inverter/Charger
Victron BMV-602s
Honda 5.5kW Genset - Location: Victoria, Australia
Re: Low Battery Cut-Off with FNDC
Yep, it has both high and low settings and you are correct that, based on the manual, you could "trick" it by setting high as low and visa versa assuming they do not have any "hidden" logic that checks the relative values of each.raysun wrote: ↑Sun Jun 05, 2022 5:53 amThe 600 series have both Low Voltage and High Voltage sensing logic, do they not? If the relay is NO, then perhaps the Relay High Voltage parameter can be set to LBCI voltage, and the Clear Relay High Voltage parameter set to the LBCO voltage.
FWIW, the FNDC relay is operating like that. It's NO, so the LBCI voltage must be reached first to energize the relay.
Rl: Relay low voltage. When the battery voltage falls below this value for more than
10 seconds the alarm relay will be activated.
Rlc: Clear relay low voltage. When the battery voltage rises above this value, the
relay will be de-activated. This value needs to be greater than or equal to Rl.
Rh: Relay high voltage. When the battery voltage rises above this value for more
than 10 seconds the relay will be activated.
Rhc: Clear relay high voltage. When the battery voltage falls below this value, the
relay will be de-activated. This value needs to be less than or equal to Rh.
-------------------------
http://spwebcam.myddns.me/
http://spwebcam.myddns.me/
-
- Forum Emperor
- Posts: 8024
- Joined: Tue Jul 26, 2016 5:57 am
- My RE system: Flexpower Two: (2) FXR3048A-01, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
Honda EU7000is gas fuel generator
Re: Low Battery Cut-Off with FNDC
It should be fairly easy to test on the next charge cycle.
Set Rh = Absorb Voltage - 0.2V
Set Rhc = Float Voltage + 0.2V
For testing, Ah and Ahc parameters could be set to the values above to have a really annoying audible (and visual) indication the programming is working.
Better for real life, set Al and Alc so the alarm is enabled during the LBCO event.
Set Rh = Absorb Voltage - 0.2V
Set Rhc = Float Voltage + 0.2V
For testing, Ah and Ahc parameters could be set to the values above to have a really annoying audible (and visual) indication the programming is working.
Better for real life, set Al and Alc so the alarm is enabled during the LBCO event.