Battery causing the GFDI to trip

A place where users can meetup with other FlexPower One users and can find support for one another. A great place for people who have not purchased the FlexPower One yet to look up information.
Post Reply
Shiante
Forum Member
Posts: 20
Joined: Sun Jan 24, 2021 6:13 am
My RE system: FLEXpower, Pre-wired,GVFX3048E

Battery causing the GFDI to trip

Post by Shiante »

Problem:
The GFDI does not trip when only the PV Array is connected. But it trips as soon as I connect the battery.

Questions:
How do I fix this problem?

System description:
This is a new installation of Flex Power One, with the following key components:
1. MATE3 Serial Number MA1614F0100289
2. Inverter Model VFXR3048E and Serial number VFXR1545F1623283
3. FlexMax 80
4. FlexNet DC
5. Lithium Ion Battery
5.1 Nominal voltage: 48v
5.2 Rated capacity: 100Ah
5.3 Rated reserved energy: 4800Wh
5.4 Standard charging current: 20A
5.5 Standard discharging current: 50A
5.6 Maximum continuous discharging current: 100A
raysun
Forum Emperor
Posts: 9024
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A-01 - Parallel Stacked, (2) FM80, MATE3s, FlexNetDC
6 SimpliPhi 3.8-48 (48v @ 75AH. 450AH total)
Outback IBR3 battery enclosure
REC Alpha 440W panels - 2 arrays: each of 4 strings of 2 in series
2 Midnite Solar MNPV6 combiners w/20A DC disconnects.
Honda EU7000is gas fuel generator
Off-Grid

Re: Battery causing the GFDI to trip

Post by raysun »

Just as a general precaution, the charge controller should never be attached to PV without first being attached to the battery, or damage to the unit can result.

Does GFDI trip when the the battery is connected but the PV disconnected?

If no, does it trip when the PV is subsequently connected?

The GFDI is wired to disconnect the charge controller from the battery in the event of a ground fault in the PV array. If it continues to trip when the controller is properly connected: battery first, then PV, look for the ground fault in the array wiring.